| Powertech 15kw cooling fan - Printable Version +- Wanderlodge Gurus - The Member Funded Wanderlodge Forum (http://www.wanderlodgegurus.com) +-- Forum: Yahoo Groups Archive (/forumdisplay.php?fid=61) +--- Forum: WanderlodgeForum (/forumdisplay.php?fid=63) +--- Thread: Powertech 15kw cooling fan (/showthread.php?tid=5671) |
| Powertech 15kw cooling fan - Pete Masterson - 09-16-2007 07:46 Just got back from a trip to Oregon. The cooling fan on my Powertech generator seems to have quit working. In the few days before the failure, I was noticing a very serious (but transient) amperage draw on leg one accompanied by dimmed lights in the coach. These lasted from one-two seconds up to about 10 seconds (infrequently). At first, I suspected one of the AC units -- but the problem didn't occur on shore power. Finally, the generator would run for 20 minutes or so -- then just quit-- with the water temp gauge showing a high temperature. After allowing an hour of so for cool down, the generator would start up -- and run for awhile until the temperature got too high again. The water is full up (as it has been). Oil is OK -- and so on. However, the fan simply doesn't cycle on. I searched the archives -- but there don't seem to be specific discussions of what to do when the fan simply doesn't work. (I'm guessing I have to replace the fan motor.) Any comments and suggestions where to get a replacement fan motor? Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 El Sobrante CA aeonix1@... [Non-text portions of this message have been removed] Powertech 15kw cooling fan - bloomas - 09-16-2007 08:38 ----- Original Message ----- From: Pete Masterson To: wanderlodge@yahoogroups.com ; WanderlodgeForum@yahoogroups.com Sent: Sunday, September 16, 2007 2:46 PM Subject: [WanderlodgeForum] Powertech 15kw cooling fan The first thing that I would is check that there is power to both legs to the fan motor.If both legs are hot then I would guess that the motor is bad.When I replace my motor I got it from Granger. Bob Loomas PT 36 1985 Just got back from a trip to Oregon. The cooling fan on my Powertech generator seems to have quit working. In the few days before the failure, I was noticing a very serious (but transient) amperage draw on leg one accompanied by dimmed lights in the coach. These lasted from one-two seconds up to about 10 seconds (infrequently). At first, I suspected one of the AC units -- but the problem didn't occur on shore power. Finally, the generator would run for 20 minutes or so -- then just quit-- with the water temp gauge showing a high temperature. After allowing an hour of so for cool down, the generator would start up -- and run for awhile until the temperature got too high again. The water is full up (as it has been). Oil is OK -- and so on. However, the fan simply doesn't cycle on. I searched the archives -- but there don't seem to be specific discussions of what to do when the fan simply doesn't work. (I'm guessing I have to replace the fan motor.) Any comments and suggestions where to get a replacement fan motor? Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 El Sobrante CA aeonix1@... [Non-text portions of this message have been removed] [Non-text portions of this message have been removed] Powertech 15kw cooling fan - ronmarabito2002 - 09-16-2007 10:31 I replaced my fan motor a year ago. You can purchase a replacement at any good appliance repair company. It is a 220v motor. You might have to modify the rubber mountings in the brackets. It is difficult to remove the fan from the shaft. Soak it well and place the fan on wood blocks so you can knock the motor shaft out of the fan. When you replace it, make sure to balance the motor & fan. There are small metal clips on the fan blades used to balance it. R.E. (Ron) Marabito, Dallas, TX 92WB40 --- In WanderlodgeForum@yahoogroups.com, Pete Masterson wrote: > > Just got back from a trip to Oregon. The cooling fan on my Powertech > generator seems to have quit working. > > In the few days before the failure, I was noticing a very serious > (but transient) amperage draw on leg one accompanied by dimmed lights > in the coach. These lasted from one-two seconds up to about 10 > seconds (infrequently). At first, I suspected one of the AC units -- > but the problem didn't occur on shore power. > > Finally, the generator would run for 20 minutes or so -- then just > quit-- with the water temp gauge showing a high temperature. After > allowing an hour of so for cool down, the generator would start up -- > and run for awhile until the temperature got too high again. > > The water is full up (as it has been). Oil is OK -- and so on. > > However, the fan simply doesn't cycle on. > > I searched the archives -- but there don't seem to be specific > discussions of what to do when the fan simply doesn't work. (I'm > guessing I have to replace the fan motor.) > > Any comments and suggestions where to get a replacement fan motor? > > > Pete Masterson > '95 Blue Bird Wanderlodge WBDA 42 > El Sobrante CA > aeonix1@... > > > > > > [Non-text portions of this message have been removed] > Powertech 15kw cooling fan - Curt Sprenger - 09-16-2007 10:57 Pete, If your gen. fan set up is the same as on the 87 PT, which looks like the fan unit for the house furnace, take the whole unit out and take it to a motor shop (AAA Electric Motors in Anaheim is where I took ours). I paid $158.58 for a new motor, clean/paint the housing, new fan/balancing, new capacitor. On 9/16/07, ronmarabito2002 > > I replaced my fan motor a year ago. You can purchase a replacement at > any good appliance repair company. It is a 220v motor. You might > have to modify the rubber mountings in the brackets. It is difficult > to remove the fan from the shaft. Soak it well and place the fan on > wood blocks so you can knock the motor shaft out of the fan. > > When you replace it, make sure to balance the motor & fan. There are > small metal clips on the fan blades used to balance it. > > R.E. (Ron) Marabito, Dallas, TX 92WB40 > > --- In WanderlodgeForum@yahoogroups.com > Pete Masterson > wrote: > > > > Just got back from a trip to Oregon. The cooling fan on my Powertech > > generator seems to have quit working. > > > > In the few days before the failure, I was noticing a very serious > > (but transient) amperage draw on leg one accompanied by dimmed lights > > in the coach. These lasted from one-two seconds up to about 10 > > seconds (infrequently). At first, I suspected one of the AC units -- > > but the problem didn't occur on shore power. > > > > Finally, the generator would run for 20 minutes or so -- then just > > quit-- with the water temp gauge showing a high temperature. After > > allowing an hour of so for cool down, the generator would start up -- > > and run for awhile until the temperature got too high again. > > > > The water is full up (as it has been). Oil is OK -- and so on. > > > > However, the fan simply doesn't cycle on. > > > > I searched the archives -- but there don't seem to be specific > > discussions of what to do when the fan simply doesn't work. (I'm > > guessing I have to replace the fan motor.) > > > > Any comments and suggestions where to get a replacement fan motor? > > > > > > Pete Masterson > > '95 Blue Bird Wanderlodge WBDA 42 > > El Sobrante CA > > aeonix1@... > > > > > > > > > > > > [Non-text portions of this message have been removed] > > > > > -- Curt Sprenger 1987 PT38 8V92 "MacAttack Racing" Anaheim Hills, CA [Non-text portions of this message have been removed] Powertech 15kw cooling fan - Pete Masterson - 09-16-2007 13:15 Indeed, it sounds much the same. I like this idea. I'll check around for a similar shop in this area. =============================================== Pete Masterson, Author of Book Design and Production: A Guide for Authors and Publishers Aeonix1@... Aeonix Publishing Group http://www.aeonix.com =============================================== On Sep 16, 2007, at 3:57 PM, Curt Sprenger wrote: > Pete, > > If your gen. fan set up is the same as on the 87 PT, which looks > like the > fan unit for the house furnace, take the whole unit out and take it > to a > motor shop (AAA Electric Motors in Anaheim is where I took ours). I > paid > $158.58 for a new motor, clean/paint the housing, new fan/ > balancing, new > capacitor. > > > On 9/16/07, ronmarabito2002 >> >> I replaced my fan motor a year ago. You can purchase a >> replacement at >> any good appliance repair company. It is a 220v motor. You might >> have to modify the rubber mountings in the brackets. It is difficult >> to remove the fan from the shaft. Soak it well and place the fan on >> wood blocks so you can knock the motor shaft out of the fan. >> >> When you replace it, make sure to balance the motor & fan. There are >> small metal clips on the fan blades used to balance it. >> >> R.E. (Ron) Marabito, Dallas, TX 92WB40 >> >> --- In WanderlodgeForum@yahoogroups.com >> Pete Masterson >> wrote: >>> >>> Just got back from a trip to Oregon. The cooling fan on my Powertech >>> generator seems to have quit working. >>> >>> In the few days before the failure, I was noticing a very serious >>> (but transient) amperage draw on leg one accompanied by dimmed >>> lights >>> in the coach. These lasted from one-two seconds up to about 10 >>> seconds (infrequently). At first, I suspected one of the AC units -- >>> but the problem didn't occur on shore power. >>> >>> Finally, the generator would run for 20 minutes or so -- then just >>> quit-- with the water temp gauge showing a high temperature. After >>> allowing an hour of so for cool down, the generator would start >>> up -- >>> and run for awhile until the temperature got too high again. >>> >>> The water is full up (as it has been). Oil is OK -- and so on. >>> >>> However, the fan simply doesn't cycle on. >>> >>> I searched the archives -- but there don't seem to be specific >>> discussions of what to do when the fan simply doesn't work. (I'm >>> guessing I have to replace the fan motor.) >>> >>> Any comments and suggestions where to get a replacement fan motor? >>> >>> >>> Pete Masterson >>> '95 Blue Bird Wanderlodge WBDA 42 >>> El Sobrante CA >>> aeonix1@... >>> >>> >>> >>> >>> >>> [Non-text portions of this message have been removed] >>> >> >> >> > > > > -- > Curt Sprenger > 1987 PT38 8V92 "MacAttack Racing" > Anaheim Hills, CA > > > [Non-text portions of this message have been removed] > > > > > Yahoo! Groups Links > > > [Non-text portions of this message have been removed] Powertech 15kw cooling fan - putneyflash@...> - 09-16-2007 14:07 Is the fan motor getting voltage? If so you are sure its the motor can you have it rebuilt? > From: Pete Masterson > Date: 2007/09/16 Sun PM 03:46:50 EDT > To: wanderlodge@yahoogroups.com, WanderlodgeForum@yahoogroups.com > Subject: [WanderlodgeForum] Powertech 15kw cooling fan > > Just got back from a trip to Oregon. The cooling fan on my Powertech > generator seems to have quit working. > > In the few days before the failure, I was noticing a very serious > (but transient) amperage draw on leg one accompanied by dimmed lights > in the coach. These lasted from one-two seconds up to about 10 > seconds (infrequently). At first, I suspected one of the AC units -- > but the problem didn't occur on shore power. > > Finally, the generator would run for 20 minutes or so -- then just > quit-- with the water temp gauge showing a high temperature. After > allowing an hour of so for cool down, the generator would start up -- > and run for awhile until the temperature got too high again. > > The water is full up (as it has been). Oil is OK -- and so on. > > However, the fan simply doesn't cycle on. > > I searched the archives -- but there don't seem to be specific > discussions of what to do when the fan simply doesn't work. (I'm > guessing I have to replace the fan motor.) > > Any comments and suggestions where to get a replacement fan motor? > > > Pete Masterson > '95 Blue Bird Wanderlodge WBDA 42 > El Sobrante CA > aeonix1@... > > > > > > [Non-text portions of this message have been removed] > > > Powertech 15kw cooling fan - roncan1842@... - 09-16-2007 19:05 most likely your fan motor is gone, I just recently replaced mine, 95pt 40 not bad for 12 yrs, a replacement motor cost me $55.00, it is the same motor used on residential ac units, grainger was almost twice as much, check out your local ac supply house ron roberts 95pt40 ************************************** See what's new at http://www.aol.com [Non-text portions of this message have been removed] |
