					Suburban Furnance Fixed
				 
			 | 
		
| 
				 
					02-23-2008, 12:54 
				 
				
Post: #1 
			 | 
		|||
				
  | 
		|||
| 
				Suburban Furnance Fixed 
				 
					Since purchasing last summer, the front LP furnace has not worked. 
				
				
				
			It would go through all the motions but would blow cold. So today I finally decided I would find the problem. I got out the air hose and started by blowing everything out. No change. However, the front LP sensor has been false sensing, and the air hose fixed that problem....progress. Next I pulled the front off the furnace and unscrewed the furnace from the floor. After closing the gas valve at the unit, I disconnected the gas line. Then I pulled the unit forward and rotated it up so I could take a close look at everything. Observing no problems, I then pulled the igniter. And there was the problem. A wasp built a mud nest across the electrode and shorted it out. I cleaned it up, and put everything back together. Now it works like it should....One less project. Regards, Glenn Allen 1986 PT40 Marietta, GA  | 
		|||
| 
				
	 