I am desperate for any info I can get on repairing/replacing the
blower motor in the Intertherm a/c unit on my '90WL. The fan runs for about 10-15 minutes then slows down and stalls. If I let it sit for 5 - 6 minutes it will run again for 10-15 min's. When it first runs it runs at top speed and the drop off to 0 rpm takes about 30 sec's. Same result with a/c on or fan only. Has anyone out there had this same experience? If so can someone tell me how big a job it is to replace/repair the motor and how much disassembly is required to access it? |
|||
06-15-2005, 05:55
Post: #2
|
|||
|
|||
Help! Intertherm blower motor
I'm not familiar with that particular unit, but I can say it sounds
like lack of lubrication to the bearings. You might check to see if they have a lube port. If not, you will probably have to replace the motor, or have it rebuilt. R.E. (Ron) Marabito, Dallas, TX 92WB40 Moderator --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > I am desperate for any info I can get on repairing/replacing the > blower motor in the Intertherm a/c unit on my '90WL. > The fan runs for about 10-15 minutes then slows down and stalls. > If I let it sit for 5 - 6 minutes it will run again for 10-15 min's. > When it first runs it runs at top speed and the drop off to 0 rpm > takes about 30 sec's. Same result with a/c on or fan only. > Has anyone out there had this same experience? If so can someone > tell me how big a job it is to replace/repair the motor and how much > disassembly is required to access it? |
|||
06-15-2005, 07:45
Post: #3
|
|||
|
|||
Help! Intertherm blower motor
Thanks Ron, I guess I was hoping for an easy way out.
--- In WanderlodgeForum@yahoogroups.com, "ronmarabito2002" > I'm not familiar with that particular unit, but I can say it sounds > like lack of lubrication to the bearings. You might check to see if > they have a lube port. If not, you will probably have to replace > the motor, or have it rebuilt. > > R.E. (Ron) Marabito, Dallas, TX 92WB40 > Moderator > > > --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > > > I am desperate for any info I can get on repairing/replacing the > > blower motor in the Intertherm a/c unit on my '90WL. > > The fan runs for about 10-15 minutes then slows down and stalls. > > If I let it sit for 5 - 6 minutes it will run again for 10-15 > min's. > > When it first runs it runs at top speed and the drop off to 0 rpm > > takes about 30 sec's. Same result with a/c on or fan only. > > Has anyone out there had this same experience? If so can someone > > tell me how big a job it is to replace/repair the motor and how > much > > disassembly is required to access it? |
|||
06-15-2005, 12:26
Post: #4
|
|||
|
|||
Help! Intertherm blower motor
My knowledge in minimal but I have one Intertherm left on my 89SP but
the outside cover is starting to come apart. If you remove the cover you will find an access cover that will allow you to lubricate the unit and, as I recall, the blower. Do you have a copy of the literature that came with the unit? If not, let me know and I will see what I have. --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > I am desperate for any info I can get on repairing/replacing the > blower motor in the Intertherm a/c unit on my '90WL. > The fan runs for about 10-15 minutes then slows down and stalls. > If I let it sit for 5 - 6 minutes it will run again for 10-15 min's. > When it first runs it runs at top speed and the drop off to 0 rpm > takes about 30 sec's. Same result with a/c on or fan only. > Has anyone out there had this same experience? If so can someone > tell me how big a job it is to replace/repair the motor and how much > disassembly is required to access it? |
|||
06-16-2005, 00:46
Post: #5
|
|||
|
|||
Help! Intertherm blower motor
Thanks Fred,
When you say remove the cover do you mean the rooftop cover? --- In WanderlodgeForum@yahoogroups.com, "fred89sp" wrote: > My knowledge in minimal but I have one Intertherm left on my 89SP but > the outside cover is starting to come apart. > > If you remove the cover you will find an access cover that will allow > you to lubricate the unit and, as I recall, the blower. Do you have a > copy of the literature that came with the unit? If not, let me know > and I will see what I have. > > > --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > > > I am desperate for any info I can get on repairing/replacing the > > blower motor in the Intertherm a/c unit on my '90WL. > > The fan runs for about 10-15 minutes then slows down and stalls. > > If I let it sit for 5 - 6 minutes it will run again for 10-15 min's. > > When it first runs it runs at top speed and the drop off to 0 rpm > > takes about 30 sec's. Same result with a/c on or fan only. > > Has anyone out there had this same experience? If so can someone > > tell me how big a job it is to replace/repair the motor and how much > > disassembly is required to access it? |
|||
06-16-2005, 02:01
Post: #6
|
|||
|
|||
Help! Intertherm blower motor
That is correct, 2 Phillips on back and side, 3 on the front. The
inside cover has 2 but they may not be Phillips so take a straight one on your first trip up. Be gentle with the cover, they get brittle over the years. --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > Thanks Fred, > When you say remove the cover do you mean the rooftop cover? > > --- In WanderlodgeForum@yahoogroups.com, "fred89sp" > wrote: > > My knowledge in minimal but I have one Intertherm left on my 89SP > but > > the outside cover is starting to come apart. > > > > If you remove the cover you will find an access cover that will > allow > > you to lubricate the unit and, as I recall, the blower. Do you > have a > > copy of the literature that came with the unit? If not, let me > know > > and I will see what I have. > > > > > > --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > > > > > I am desperate for any info I can get on repairing/replacing the > > > blower motor in the Intertherm a/c unit on my '90WL. > > > The fan runs for about 10-15 minutes then slows down and stalls. > > > If I let it sit for 5 - 6 minutes it will run again for 10-15 > min's. > > > When it first runs it runs at top speed and the drop off to 0 rpm > > > takes about 30 sec's. Same result with a/c on or fan only. > > > Has anyone out there had this same experience? If so can someone > > > tell me how big a job it is to replace/repair the motor and how > much > > > disassembly is required to access it? |
|||
06-16-2005, 03:59
Post: #7
|
|||
|
|||
Help! Intertherm blower motor
-FRED: you are in luck...I just removed, had rewound and replaced
my blower motor on my 90SO. removal is a piece of cake and I am just your average spark plug /oil changing guy. I looked all over for the blower motor in vegas but it was special and too old..had it rewound for $100. a bit high but what the heck..better than a new ac unit built in China!!! I did not have any trouble replacing the motor...it is on top after you take off some covers and remove left and righ blower fans with a long alen wrench. the motor wires are color coded but I taped numbers and colors in case I forgot. from what I heard from rv ac guy, the intertherm is a great unit compared to the new ones that do not last as long. let me know if you have any specific questions. best, Hank Hannigan 90SP36 -- In WanderlodgeForum@yahoogroups.com, "fred89sp" wrote: > My knowledge in minimal but I have one Intertherm left on my 89SP but > the outside cover is starting to come apart. > > If you remove the cover you will find an access cover that will allow > you to lubricate the unit and, as I recall, the blower. Do you have a > copy of the literature that came with the unit? If not, let me know > and I will see what I have. > > > --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > > > I am desperate for any info I can get on repairing/replacing the > > blower motor in the Intertherm a/c unit on my '90WL. > > The fan runs for about 10-15 minutes then slows down and stalls. > > If I let it sit for 5 - 6 minutes it will run again for 10-15 min's. > > When it first runs it runs at top speed and the drop off to 0 rpm > > takes about 30 sec's. Same result with a/c on or fan only. > > Has anyone out there had this same experience? If so can someone > > tell me how big a job it is to replace/repair the motor and how much > > disassembly is required to access it? |
|||
06-16-2005, 04:10
Post: #8
|
|||
|
|||
Help! Intertherm blower motor
Fred: one more thing..RON was right..had I oiled my blower motor
each year, I would have avoided the problemm..you may not be too late..try oiling each unit's motor..very easy..have to use oild from walmart in pain accessories section..only $2 and has long spout making oiling easier..forgot name of it but it is in cooling/accessories section at wally'smart next to copper tubing etc.. the long thin spout pulls out at least a foot so you oil the motors without taking off all the covers...i just flew to chicago otherwise I could tell you the name of the stuff!!! make sure you oil the other unit also!!!!! put a ton of oil in them!!! later, Hank Hannigan 90SP36 and lovin it~~~~--- In WanderlodgeForum@yahoogroups.com, "Henry Jay Hannigan" > -FRED: you are in luck...I just removed, had rewound and replaced > my blower motor on my 90SO. removal is a piece of cake and I am > just your average spark plug /oil changing guy. I looked all over > for the blower motor in vegas but it was special and too old..had it > rewound for $100. a bit high but what the heck..better than a new > ac unit built in China!!! I did not have any trouble replacing > the motor...it is on top after you take off some covers and remove > left and righ blower fans with a long alen wrench. the motor wires > are color coded but I taped numbers and colors in case I forgot. > from what I heard from rv ac guy, the intertherm is a great unit > compared to the new ones that do not last as long. let me know if > you have any specific questions. > best, > Hank Hannigan > 90SP36 > -- In WanderlodgeForum@yahoogroups.com, "fred89sp" > wrote: > > My knowledge in minimal but I have one Intertherm left on my 89SP > but > > the outside cover is starting to come apart. > > > > If you remove the cover you will find an access cover that will > allow > > you to lubricate the unit and, as I recall, the blower. Do you > have a > > copy of the literature that came with the unit? If not, let me > know > > and I will see what I have. > > > > > > --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > > > > > I am desperate for any info I can get on repairing/replacing the > > > blower motor in the Intertherm a/c unit on my '90WL. > > > The fan runs for about 10-15 minutes then slows down and stalls. > > > If I let it sit for 5 - 6 minutes it will run again for 10-15 > min's. > > > When it first runs it runs at top speed and the drop off to 0 rpm > > > takes about 30 sec's. Same result with a/c on or fan only. > > > Has anyone out there had this same experience? If so can someone > > > tell me how big a job it is to replace/repair the motor and how > much > > > disassembly is required to access it? |
|||
06-16-2005, 04:14
Post: #9
|
|||
|
|||
Help! Intertherm blower motor
Check http://www.surpluscenter.com/ I've had good luck getting fan
motors from them. Curt Sprenger â87PT38, Anaheim, Calif. Henry Jay Hannigan wrote: > -FRED: you are in luck...I just removed, had rewound and replaced > my blower motor on my 90SO. removal is a piece of cake and I am > just your average spark plug /oil changing guy. I looked all over > for the blower motor in vegas but it was special and too old..had it > rewound for $100. a bit high but what the heck..better than a new > ac unit built in China!!! I did not have any trouble replacing > the motor...it is on top after you take off some covers and remove > left and righ blower fans with a long alen wrench. the motor wires > are color coded but I taped numbers and colors in case I forgot. > from what I heard from rv ac guy, the intertherm is a great unit > compared to the new ones that do not last as long. let me know if > you have any specific questions. > best, > Hank Hannigan > 90SP36 > -- In WanderlodgeForum@yahoogroups.com, "fred89sp" > wrote: > > My knowledge in minimal but I have one Intertherm left on my 89SP > but > > the outside cover is starting to come apart. > > > > If you remove the cover you will find an access cover that will > allow > > you to lubricate the unit and, as I recall, the blower. Do you > have a > > copy of the literature that came with the unit? If not, let me > know > > and I will see what I have. > > > > > > --- In WanderlodgeForum@yahoogroups.com, "williamcharrison" > > > > > I am desperate for any info I can get on repairing/replacing the > > > blower motor in the Intertherm a/c unit on my '90WL. > > > The fan runs for about 10-15 minutes then slows down and stalls. > > > If I let it sit for 5 - 6 minutes it will run again for 10-15 > min's. > > > When it first runs it runs at top speed and the drop off to 0 rpm > > > takes about 30 sec's. Same result with a/c on or fan only. > > > Has anyone out there had this same experience? If so can someone > > > tell me how big a job it is to replace/repair the motor and how > much > > > disassembly is required to access it? > > |
|||