Perkins 12KW generator starting hard
When starting the generator it fires instantly but dies. If I hold the
starter on for a couple seconds after the generator has started it will stay running. Is there a shutdown delay on these so the oil pressare can build up? If so where would it be and what does it look like? Troy 1986 Newell |
|||
05-26-2006, 07:40
Post: #2
|
|||
|
|||
Perkins 12KW generator starting hard
Yes. There are two sensors on the forward side of the block. One is
the oil pressure sender switch and one is the low oil pressure cut off switch. The low pressure switch is wired in tandem with the high temperature shut off sensor at the top inboard side of the head. Kerry 82 FC 35 Denver --- In WanderlodgeForum@yahoogroups.com, "ttikalsky" wrote: > > When starting the generator it fires instantly but dies. If I hold the > starter on for a couple seconds after the generator has started it > will stay running. Is there a shutdown delay on these so the oil > pressare can build up? If so where would it be and what does it look > like? > > > Troy > 1986 Newell > |
|||
05-26-2006, 22:42
Post: #3
|
|||
|
|||
Perkins 12KW generator starting hard
--- In WanderlodgeForum@yahoogroups.com, "ttikalsky"
wrote: > Troy, There's a heater on the engine that needs to warm up before starting the engine. Hold the generator switch in the "off" position for 30 seconds or so before starting. That provides power to the heater and may be the reason the engine doesn't stay running. Mine does the same thing if I don't pre-heat it. In very cold weather, I hold it on for a minute. George Witt 81 FC 35 Lincoln, Nebraska > When starting the generator it fires instantly but dies. If I hold the > starter on for a couple seconds after the generator has started it > will stay running. Is there a shutdown delay on these so the oil > pressare can build up? If so where would it be and what does it look > like? > > > Troy > 1986 Newell > |
|||
05-27-2006, 01:07
Post: #4
|
|||
|
|||
Perkins 12KW generator starting hard
The heater is a set of glow plugs. On mine, the glow plugs are series
plugs and not parallel plugs. This means that if one glow plug fails, they all do. It's something to keep in mind if it starts hard or won't run right away. I don't know if there is a retrofit kit to change the glow plugs to parallel plugs. I changed to parallel from series on my 77 Mercedes diesel and it made all the difference in the world when it came to starting in cold weather. Kerry 82 FC 35 > Troy, > There's a heater on the engine that needs to warm up before > starting the engine. Hold the generator switch in the "off" position > for 30 seconds or so before starting. That provides power to the > heater and may be the reason the engine doesn't stay running. > Mine does the same thing if I don't pre-heat it. > In very cold weather, I hold it on for a minute. > > George Witt > 81 FC 35 > Lincoln, Nebraska |
|||
05-27-2006, 01:39
Post: #5
|
|||
|
|||
Perkins 12KW generator starting hard
Troy, If it runs while you are holding the start button down and then dies when
you let go, that usually means the generator is not generating electricity. Dan ----- Original Message ----- From: ttikalsky To: WanderlodgeForum@yahoogroups.com Sent: Friday, May 26, 2006 2:12 PM Subject: [WanderlodgeForum] Perkins 12KW generator starting hard When starting the generator it fires instantly but dies. If I hold the starter on for a couple seconds after the generator has started it will stay running. Is there a shutdown delay on these so the oil pressare can build up? If so where would it be and what does it look like? Troy 1986 Newell SPONSORED LINKS Recreational vehicles Recreational vehicle financing Recreational vehicle repair Recreational vehicle rental Recreational vehicle camper Recreational vehicle rate ------------------------------------------------------------------------------ YAHOO! GROUPS LINKS a.. Visit your group "WanderlodgeForum" on the web. b.. To unsubscribe from this group, send an email to: WanderlodgeForum-unsubscribe@yahoogroups.com c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. ------------------------------------------------------------------------------ [Non-text portions of this message have been removed] |
|||