01-15-2007, 09:44
For all those interested though, ensure that the correct size of wire is used at
all times, too small a wire can lead to electrical fires, which can be stubborn to put out. There are all different types of wire with different class/heat ratings, check the electrical code book to make sure that the wire is adequate. Bill 84 FC 35 SB "$quanderlodge" Terrace, B.C. Canada ----- Original Message ---- From: John To: WanderlodgeForum@yahoogroups.com Sent: Monday, January 15, 2007 11:06:51 AM Subject: [WanderlodgeForum] Re: Using Generator As Backup For House Power Eric, Check out these two pages on my web site; http://www.pbase. com/iamflagman/ image/41069743 http://www.pbase. com/iamflagman/ image/50203372 Before anybody jumps the gun on the orange wire that I used, from the breaker box, to the 50 amp plug, the wire is ROMEX SIMpull 10/3 with ground which according to my electrician, is good for short runs like this in dry locations, it does not get hot when used to power my shop and sections of the rental property electrical system. the breaker box is just there for added security, as the power going to it is tapped off of the breaker box in the generator compartment. "REMEMBER SEPTEMBER 11, 2001" John Finn '82 35FCRB BLUEBIRD WANDERLODGE TO VISIT THE "FINN'S INN EXPRESS" REMODELING ADVENTURE GO TO; http://www.pbase. com/image/ 24977457 HOPKINS, SOUTH CAROLINA //////////// ///////// ///////// ///////// ///////// //////// --- In WanderlodgeForum@ yahoogroups. com, "Eric Johnson" wrote: > > Ice storms may bring loss of power to our home as in other areas of the country so I brought > the coach to the house with the idea of moving into it if we have a problem. Then I got to > thinking about using the generator to provide power to the home so we could have heat and > lights. Has anyone else done this? What would be the best way to make the connection so > you get maximum use of the generator capacity? > > Regards, Eric in San Antonio > 84FC35SBWL2 > <!-- #ygrp-mlmsg {font-size:13px;font-family:arial,helvetica,clean,sans-serif;} #ygrp-mlmsg table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115% monospace;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{ font-family:Georgia; } #ygrp-text p{ margin:0 0 1em 0; } #ygrp-tpmsgs{ font-family:Arial; clear:both; } #ygrp-vitnav{ padding-top:10px; font-family:Verdana; font-size:77%; margin:0; } #ygrp-vitnav a{ padding:0 1px; } #ygrp-actbar{ clear:both; margin:25px 0; white-space:nowrap; color:#666; text-align:right; } #ygrp-actbar .left{ float:left; white-space:nowrap; } .bld{font-weight:bold;} #ygrp-grft{ font-family:Verdana; font-size:77%; padding:15px 0; } #ygrp-ft{ font-family:verdana; font-size:77%; border-top:1px solid #666; padding:5px 0; } #ygrp-mlmsg #logo{ padding-bottom:10px; } #ygrp-vital{ background-color:#e0ecee; margin-bottom:20px; padding:2px 0 8px 8px; } #ygrp-vital #vithd{ font-size:77%; font-family:Verdana; font-weight:bold; color:#333; text-transform:uppercase; } #ygrp-vital ul{ padding:0; margin:2px 0; } #ygrp-vital ul li{ list-style-type:none; clear:both; border:1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight:bold; color:#ff7900; float:right; width:2em; text-align:right; padding-right:.5em; } #ygrp-vital ul li .cat{ font-weight:bold; } #ygrp-vital a { text-decoration:none; } #ygrp-vital a:hover{ text-decoration:underline; } #ygrp-sponsor #hd{ color:#999; font-size:77%; } #ygrp-sponsor #ov{ padding:6px 13px; background-color:#e0ecee; margin-bottom:20px; } #ygrp-sponsor #ov ul{ padding:0 0 0 8px; margin:0; } #ygrp-sponsor #ov li{ list-style-type:square; padding:6px 0; font-size:77%; } #ygrp-sponsor #ov li a{ text-decoration:none; font-size:130%; } #ygrp-sponsor #nc { background-color:#eee; margin-bottom:20px; padding:0 8px; } #ygrp-sponsor .ad{ padding:8px 0; } #ygrp-sponsor .ad #hd1{ font-family:Arial; font-weight:bold; color:#628c2a; font-size:100%; line-height:122%; } #ygrp-sponsor .ad a{ text-decoration:none; } #ygrp-sponsor .ad a:hover{ text-decoration:underline; } #ygrp-sponsor .ad p{ margin:0; } o {font-size:0;} .MsoNormal { margin:0 0 0 0; } #ygrp-text tt{ font-size:120%; } blockquote{margin:0 0 0 4px;} .replbq {margin:4;} --> __________________________________________________ Do You Yahoo!? Tired of spam? Yahoo! Mail has the best spam protection around http://mail.yahoo.com [Non-text portions of this message have been removed] |
01-15-2007, 09:49
AND don't get caught, could be a big fine.
Bill 84 FC 35 SB "$quanderlodge" Terrace, B.C. Canada ----- Original Message ---- From: Chuck Wheeler To: WanderlodgeForum@yahoogroups.com Sent: Monday, January 15, 2007 8:20:09 AM Subject: RE: [WanderlodgeForum] Using Generator As Backup For House Power Eric, I added a 50 and 30 amp plugs to the Bird that are used to power friend's trailers when we are camping. I added a Generator Transfer Switch to the house and can plug it into the coach to power the house. It will run the heat pump if nothing else except lights are on, we can cook and have hot water if the heat is off. (Our genset has a new 15KW back end on it.) Takes a little planning but it works. We have rental houses, I made a cable to back feed through the electric dryer plug when the power is off so I could work on them. Main breaker HAS to be off!!! Don't do this unless you are very comfortable with electricity. I brought the Bird home for the current Fort Worth storm but it wasn't needed. - Chuck Wheeler - 82 FC 31 SB Fort Worth, TX _____ From: WanderlodgeForum@ yahoogroups. com [mailto:WanderlodgeForum@ yahoogroups. com] On Behalf Of Eric Johnson Sent: Monday, January 15, 2007 9:06 AM To: WanderlodgeForum@ yahoogroups. com Subject: [WanderlodgeForum] Using Generator As Backup For House Power Ice storms may bring loss of power to our home as in other areas of the country so I brought the coach to the house with the idea of moving into it if we have a problem. Then I got to thinking about using the generator to provide power to the home so we could have heat and lights. Has anyone else done this? What would be the best way to make the connection so you get maximum use of the generator capacity? Regards, Eric in San Antonio 84FC35SBWL2 [Non-text portions of this message have been removed] <!-- #ygrp-mlmsg {font-size:13px;font-family:arial,helvetica,clean,sans-serif;} #ygrp-mlmsg table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115% monospace;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{ font-family:Georgia; } #ygrp-text p{ margin:0 0 1em 0; } #ygrp-tpmsgs{ font-family:Arial; clear:both; } #ygrp-vitnav{ padding-top:10px; font-family:Verdana; font-size:77%; margin:0; } #ygrp-vitnav a{ padding:0 1px; } #ygrp-actbar{ clear:both; margin:25px 0; white-space:nowrap; color:#666; text-align:right; } #ygrp-actbar .left{ float:left; white-space:nowrap; } .bld{font-weight:bold;} #ygrp-grft{ font-family:Verdana; font-size:77%; padding:15px 0; } #ygrp-ft{ font-family:verdana; font-size:77%; border-top:1px solid #666; padding:5px 0; } #ygrp-mlmsg #logo{ padding-bottom:10px; } #ygrp-vital{ background-color:#e0ecee; margin-bottom:20px; padding:2px 0 8px 8px; } #ygrp-vital #vithd{ font-size:77%; font-family:Verdana; font-weight:bold; color:#333; text-transform:uppercase; } #ygrp-vital ul{ padding:0; margin:2px 0; } #ygrp-vital ul li{ list-style-type:none; clear:both; border:1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight:bold; color:#ff7900; float:right; width:2em; text-align:right; padding-right:.5em; } #ygrp-vital ul li .cat{ font-weight:bold; } #ygrp-vital a { text-decoration:none; } #ygrp-vital a:hover{ text-decoration:underline; } #ygrp-sponsor #hd{ color:#999; font-size:77%; } #ygrp-sponsor #ov{ padding:6px 13px; background-color:#e0ecee; margin-bottom:20px; } #ygrp-sponsor #ov ul{ padding:0 0 0 8px; margin:0; } #ygrp-sponsor #ov li{ list-style-type:square; padding:6px 0; font-size:77%; } #ygrp-sponsor #ov li a{ text-decoration:none; font-size:130%; } #ygrp-sponsor #nc { background-color:#eee; margin-bottom:20px; padding:0 8px; } #ygrp-sponsor .ad{ padding:8px 0; } #ygrp-sponsor .ad #hd1{ font-family:Arial; font-weight:bold; color:#628c2a; font-size:100%; line-height:122%; } #ygrp-sponsor .ad a{ text-decoration:none; } #ygrp-sponsor .ad a:hover{ text-decoration:underline; } #ygrp-sponsor .ad p{ margin:0; } o {font-size:0;} .MsoNormal { margin:0 0 0 0; } #ygrp-text tt{ font-size:120%; } blockquote{margin:0 0 0 4px;} .replbq {margin:4;} --> __________________________________________________ Do You Yahoo!? Tired of spam? Yahoo! Mail has the best spam protection around http://mail.yahoo.com [Non-text portions of this message have been removed] |
01-15-2007, 11:27
Chet,
You could throw the main breaker and seperate your house from the power company. But the correct way is with the automatic shut off. Folks forget proper procedures and others get killed. Lawyers love these kinds of cases. Protect yourself and protect others do it correctly.. Howard Truitt Camilla, Ga. 86 PT40 ----- Original Message ----- From: chet geist To: WanderlodgeForum@yahoogroups.com Sent: Monday, January 15, 2007 11:49 AM Subject: RE: [WanderlodgeForum] Using Generator As Backup For House Power Ralph, I'm not an electrician, but in an emergency situation couldn't Eric just turn off the main disconnect on the outside of his house and then run extension cords? This should prevent sending power down the grid. Chet Geist 1981 FC33, Austin, Texas -----Original Message----- From: WanderlodgeForum@yahoogroups.com [mailto:WanderlodgeForum@yahoogroups.com]On Behalf Of Ralph L. Fullenwider Sent: Monday, January 15, 2007 9:55 AM To: WanderlodgeForum@yahoogroups.com Subject: Re: [WanderlodgeForum] Using Generator As Backup For House Power Eric: Yes it is doable. You will need an auto transfer switch to switch out the power grid in coming from your utility company. Then install a buddy plug on your coach wired 220vac 50 amp and have a cable long enough to run from the coach to the house to another plug wired to the auto transfer switch. The transfer switch control would need to be wired so the default power is from the power grid. Reason for the transfer switch is to keep from feeding power into the electrical grid from your utility and fry someone working on the down power lines. And of course, to keep the power grid from feeding back into your genset. Safe travels, Ralph and Charolette Fullenwider ( iced in, in Oklahoma) 84FC35 Ralph's RV Solutions, Duncan, Oklahoma This is done with back up gen sets at hospitals and so forth. Check with your power company, they should have the info you need. At 03:05 PM 1/15/2007 +0000, you wrote: >Ice storms may bring loss of power to our home as in other areas of the >country so I brought >the coach to the house with the idea of moving into it if we have a >problem. Then I got to >thinking about using the generator to provide power to the home so we >could have heat and >lights. Has anyone else done this? What would be the best way to make >the connection so >you get maximum use of the generator capacity? > >Regards, Eric in San Antonio >84FC35SBWL2 > > [Non-text portions of this message have been removed] ------------------------------------------------------------------------------ No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.1.410 / Virus Database: 268.16.8/621 - Release Date: 1/9/2007 [Non-text portions of this message have been removed] |
01-15-2007, 12:01
As Bill suspects, the 400 Amp transfer switch size requirement is/was because
the code requires the transfer switch to equal or exceed the larger of either the main panel size or the generator size. In my case, the main panel was 400 amp and the generator was 25KW (100amp at 240volts). Additionally, in the event of fire, the fire department typically wants to easily disconnect power so their folks aren't pouring water on electrically "hot" wires. Therefore, before considering any generator and/or electrical modifications to your property, check for the latest codes; especially new maximum distances from the meter to the main disconnect(s) (if not co-located at the meter); how remote disconnects/transfer switches must be "labeled" for the fire department; and possible reflective tape marking for location "in the dark." Last, don't forget to advise your homeowner's insurance company if you add a generator. John Wilhelmus Schreurs I do not know how the figure of a 400 amp transfer switch was determined, but here you would require at least the size of the mains coming into the house, or the size of the generator, whichever is greater. (As John said, it must have both legs AND the neutral, this is so that no unbalance from the two legs is fed back either) Also an automatic transfer switch is not required, but a transfer switch whether it be auto or manual is. The transfer switch is two fold as well, first and foremost it is to stop electrocuting the lineman who is trying to repair the circuit, but second to pick up a long length of line, transformers as well as other loads, you could do great harm to your generator/engine. Bill 84 FC 35 SB "$quanderlodge" Terrace, B.C. Canada ----- Original Message ---- From: John Suter To: WanderlodgeForum@yahoogroups.com Sent: Monday, January 15, 2007 12:28:00 PM Subject: Re: [WanderlodgeForum] Re: Using Generator As Backup For House Power Lest anyone needs to hear it one more time, a manual or automatic transfer switch WHICH LIFTS BOTH LEGS AND THE NEUTRAL, must be used to comply with many codes passed since the recent hurricanes. Generally, backfeeding the house through a "dryer" plug with just the "panel disconnected, " does not comply, as that method normally does not also disconnect the panel neutral from the utility neutral. The penalty for being caught feeding any house circuit (versus feeding just an extension cord) other than through an "approved transfer switch" in Florida jurisdictions where the latest code has been adopted, is, the utility company will "pull" the meter. The re-application takes up to 6 months and is for INITIAL electrical service, which means; accompanied by plans signed-off by an engineer/licensed electrician certifying the house/business wiring meets all current electrical codes. Learned these goodies from the inspectors in 2005 when I added a house generator to replace the past "tried and true" Bird methods. I also stopped complaining about the outrageous cost of a 400 Amp transfer switch when I got the estimate to bring the 6-year-old house up to current electrical codes. John Suter Currently Birdless > > Eric: > > Yes it is doable. You will need an auto transfer switch to switch out the > power grid in coming from your utility company. Then install a buddy plug > on your coach wired 220vac 50 amp and have a cable long enough to run from > the coach to the house to another plug wired to the auto transfer switch. > The transfer switch control would need to be wired so the default power is > from the power grid. Reason for the transfer switch is to keep from > feeding > power into the electrical grid from your utility and fry someone working > on > the down power lines. And of course, to keep the power grid from feeding > back into your genset. > > Safe travels, > > Ralph and Charolette Fullenwider ( iced in, in Oklahoma) > 84FC35 > Ralph's RV Solutions, Duncan, Oklahoma > > This is done with back up gen sets at hospitals and so forth. Check with > your power company, they should have the info you need. > _._,_.___ Messages in this topic (9) Reply (via web post) | Start a new topic Messages | Files | Photos | Links | Database | Polls | Calendar Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch format to Traditional Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe Recent Activity 12 New Members 6 New Photos Visit Your Group SPONSORED LINKS Automotive advertising Automotive lifts Recreational vehicle dealer Blue bird house Recreational vehicle rental Sitebuilder Over 380 Templates Build and custo- mize your web site Y! Toolbar Get it Free! easy 1-click access to your groups. Yahoo! Groups Start a group in 3 easy steps. Connect with others. . <!-- #ygrp-mlmsg {font-size:13px;font-family:arial,helvetica,clean,sans-serif;} #ygrp-mlmsg table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115% monospace;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{ font-family:Georgia; } #ygrp-text p{ margin:0 0 1em 0; } #ygrp-tpmsgs{ font-family:Arial; clear:both; } #ygrp-vitnav{ padding-top:10px; font-family:Verdana; font-size:77%; margin:0; } #ygrp-vitnav a{ padding:0 1px; } #ygrp-actbar{ clear:both; margin:25px 0; white-space:nowrap; color:#666; text-align:right; } #ygrp-actbar .left{ float:left; white-space:nowrap; } .bld{font-weight:bold;} #ygrp-grft{ font-family:Verdana; font-size:77%; padding:15px 0; } #ygrp-ft{ font-family:verdana; font-size:77%; border-top:1px solid #666; padding:5px 0; } #ygrp-mlmsg #logo{ padding-bottom:10px; } #ygrp-vital{ background-color:#e0ecee; margin-bottom:20px; padding:2px 0 8px 8px; } #ygrp-vital #vithd{ font-size:77%; font-family:Verdana; font-weight:bold; color:#333; text-transform:uppercase; } #ygrp-vital ul{ padding:0; margin:2px 0; } #ygrp-vital ul li{ list-style-type:none; clear:both; border:1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight:bold; color:#ff7900; float:right; width:2em; text-align:right; padding-right:.5em; } #ygrp-vital ul li .cat{ font-weight:bold; } #ygrp-vital a { text-decoration:none; } #ygrp-vital a:hover{ text-decoration:underline; } #ygrp-sponsor #hd{ color:#999; font-size:77%; } #ygrp-sponsor #ov{ padding:6px 13px; background-color:#e0ecee; margin-bottom:20px; } #ygrp-sponsor #ov ul{ padding:0 0 0 8px; margin:0; } #ygrp-sponsor #ov li{ list-style-type:square; padding:6px 0; font-size:77%; } #ygrp-sponsor #ov li a{ text-decoration:none; font-size:130%; } #ygrp-sponsor #nc { background-color:#eee; margin-bottom:20px; padding:0 8px; } #ygrp-sponsor .ad{ padding:8px 0; } #ygrp-sponsor .ad #hd1{ font-family:Arial; font-weight:bold; color:#628c2a; font-size:100%; line-height:122%; } #ygrp-sponsor .ad a{ text-decoration:none; } #ygrp-sponsor .ad a:hover{ text-decoration:underline; } #ygrp-sponsor .ad p{ margin:0; } o {font-size:0;} .MsoNormal { margin:0 0 0 0; } #ygrp-text tt{ font-size:120%; } blockquote{margin:0 0 0 4px;} .replbq {margin:4;} --> __________________________________________________ Do You Yahoo!? Tired of spam? Yahoo! Mail has the best spam protection around http://mail.yahoo.com [Non-text portions of this message have been removed] --------------------------------- Bored stiff? Loosen up... Download and play hundreds of games for free on Yahoo! Games. [Non-text portions of this message have been removed] |
01-15-2007, 12:35
Bob, I wonder how the grid deals with the residential solar gen
stations homeowners set up?? Could your troybuilt scenario appear here also? In fear of a $500. transfer switch , I stay out in the motorhome for the short period of time lights and services are off. GregoryO'Connor 94ptRomoland --- In WanderlodgeForum@yahoogroups.com, "one_dusty_hoot" > > Absolutely, I did this for several years with a > small 3KW generator on a Troy Built Tractor, two > male plugs on an extension cord. Electricity > entered the outlet, through the circuit breaker, > though another circuit breaker to the furnace motor > an TV. THEN I said what if someone accidentally > throw the main? Voltage would go through the box > through the street transformer building up to a > high voltage. A repairman could be electrocuted. > NOT ME, NOT ANYMORE, SOMEONE COULD DIE!! I did > this 20 years ago and principals of electricity > don't change in time. The only safe way is the > right way, use a line transfer switch/relay. > > bob janes, greenville, sc > > > --- In WanderlodgeForum@yahoogroups.com, "chet geist" > wrote: > > > > Ralph, > > > > I'm not an electrician, but in an emergency situation couldn't Eric > just > > turn off the main disconnect on the outside of his house and then > run > > extension cords? This should prevent sending power down the grid. > > > > Chet Geist > > 1981 FC33, Austin, Texas > > > > > > -----Original Message----- > > From: WanderlodgeForum@yahoogroups.com > > [mailto:WanderlodgeForum@yahoogroups.com]On Behalf Of Ralph L. > Fullenwider > > Sent: Monday, January 15, 2007 9:55 AM > > To: WanderlodgeForum@yahoogroups.com > > Subject: Re: [WanderlodgeForum] Using Generator As Backup For > House Power > > > > > > Eric: > > > > Yes it is doable. You will need an auto transfer switch to switch > out the > > power grid in coming from your utility company. Then install a > buddy plug > > on your coach wired 220vac 50 amp and have a cable long enough to > run from > > the coach to the house to another plug wired to the auto transfer > switch. > > The transfer switch control would need to be wired so the default > power is > > from the power grid. Reason for the transfer switch is to keep > from > > feeding > > power into the electrical grid from your utility and fry someone > working > > on > > the down power lines. And of course, to keep the power grid from > feeding > > back into your genset. > > > > Safe travels, > > > > Ralph and Charolette Fullenwider ( iced in, in Oklahoma) > > 84FC35 > > Ralph's RV Solutions, Duncan, Oklahoma > > > > This is done with back up gen sets at hospitals and so forth. > Check with > > your power company, they should have the info you need. > > > > At 03:05 PM 1/15/2007 +0000, you wrote: > > >Ice storms may bring loss of power to our home as in other areas > of the > > >country so I brought > > >the coach to the house with the idea of moving into it if we > have a > > >problem. Then I got to > > >thinking about using the generator to provide power to the home > so we > > >could have heat and > > >lights. Has anyone else done this? What would be the best way to > make > > >the connection so > > >you get maximum use of the generator capacity? > > > > > >Regards, Eric in San Antonio > > >84FC35SBWL2 > > > > > > > > > > > > > > > > > > > > [Non-text portions of this message have been removed] > > > |
01-15-2007, 12:56
Hey to all:
A point to always remember is that the local power company's GENERATOR IS BIGGER THAN YOUR GENERATOR. If at any time your generator tries to butt heads with theirs, you will pay dearly. Over the years I have seen the results of situations similiar to this. The power companys go to great lengths to protect their linemen from unwanted voltage during disasters. They have cut out locations or cut the wires to isolate areas that they are working on. Also they ground the phase wires close to the area they are working. The theory is that electricity will take the path of the least restistance. The lead people also drive or walk the area looking for dangers to the linemen. Cheapest and easiest way to use your bus genny is to run an extension cord to whatever you want to power. John Slone Pikeville, Ky 84 PT35 |
01-15-2007, 13:25
Totally solar don't worry about the grid.
Partially solar,or solar emergency would use a transfer switch. Any small AC generator could do damage to the inverters in a solar system. Having natural gas, the sweetest arrangement would be a natural gas generator that auto fires when a no voltage situation occurs at the house. Compact and quiet, off the shelf buy. The longest we have been without AC because of ice breaking off tree limbs has been 6 days. Can't see the expense for such a short time. bob janes, greenville, sc --- In WanderlodgeForum@yahoogroups.com, "Gregory OConnor" > > Bob, I wonder how the grid deals with the residential solar gen > stations homeowners set up?? Could your troybuilt scenario appear > here also? In fear of a $500. transfer switch , I stay out in the > motorhome for the short period of time lights and services are off. > > GregoryO'Connor > 94ptRomoland > > --- In WanderlodgeForum@yahoogroups.com, "one_dusty_hoot" > > > > > Absolutely, I did this for several years with a > > small 3KW generator on a Troy Built Tractor, two > > male plugs on an extension cord. Electricity > > entered the outlet, through the circuit breaker, > > though another circuit breaker to the furnace motor > > an TV. THEN I said what if someone accidentally > > throw the main? Voltage would go through the box > > through the street transformer building up to a > > high voltage. A repairman could be electrocuted. > > NOT ME, NOT ANYMORE, SOMEONE COULD DIE!! I did > > this 20 years ago and principals of electricity > > don't change in time. The only safe way is the > > right way, use a line transfer switch/relay. > > > > bob janes, greenville, sc > > > > > > --- In WanderlodgeForum@yahoogroups.com, "chet geist" > > wrote: > > > > > > Ralph, > > > > > > I'm not an electrician, but in an emergency situation couldn't > Eric > > just > > > turn off the main disconnect on the outside of his house and then > > run > > > extension cords? This should prevent sending power down the grid. > > > > > > Chet Geist > > > 1981 FC33, Austin, Texas > > > > > > > > > -----Original Message----- > > > From: WanderlodgeForum@yahoogroups.com > > > [mailto:WanderlodgeForum@yahoogroups.com]On Behalf Of Ralph L. > > Fullenwider > > > Sent: Monday, January 15, 2007 9:55 AM > > > To: WanderlodgeForum@yahoogroups.com > > > Subject: Re: [WanderlodgeForum] Using Generator As Backup For > > House Power > > > > > > > > > Eric: > > > > > > Yes it is doable. You will need an auto transfer switch to > switch > > out the > > > power grid in coming from your utility company. Then install a > > buddy plug > > > on your coach wired 220vac 50 amp and have a cable long enough > to > > run from > > > the coach to the house to another plug wired to the auto > transfer > > switch. > > > The transfer switch control would need to be wired so the > default > > power is > > > from the power grid. Reason for the transfer switch is to keep > > from > > > feeding > > > power into the electrical grid from your utility and fry > someone > > working > > > on > > > the down power lines. And of course, to keep the power grid > from > > feeding > > > back into your genset. > > > > > > Safe travels, > > > > > > Ralph and Charolette Fullenwider ( iced in, in Oklahoma) > > > 84FC35 > > > Ralph's RV Solutions, Duncan, Oklahoma > > > > > > This is done with back up gen sets at hospitals and so forth. > > Check with > > > your power company, they should have the info you need. > > > > > > At 03:05 PM 1/15/2007 +0000, you wrote: > > > >Ice storms may bring loss of power to our home as in other > areas > > of the > > > >country so I brought > > > >the coach to the house with the idea of moving into it if we > > have a > > > >problem. Then I got to > > > >thinking about using the generator to provide power to the > home > > so we > > > >could have heat and > > > >lights. Has anyone else done this? What would be the best way > to > > make > > > >the connection so > > > >you get maximum use of the generator capacity? > > > > > > > >Regards, Eric in San Antonio > > > >84FC35SBWL2 > > > > > > > > > > > > > > > > > > > > > > > > > > > > > [Non-text portions of this message have been removed] > > > > > > |
01-15-2007, 13:33
Howard:
The key here is it must be a transfer switch, not necessarily "automatic". Automatic is nice, easy as well, but a manual is a lot cheaper, and you cannot go wrong, it is either main power or generator power - not both. Bill 84 FC 35 SB "$quanderlodge" Terrace, B.C. Canada ----- Original Message ---- From: Howard O. Truitt Sent: Monday, January 15, 2007 3:27:13 PM Subject: Re: [WanderlodgeForum] Using Generator As Backup For House Power Chet, You could throw the main breaker and seperate your house from the power company. But the correct way is with the automatic shut off. Folks forget proper procedures and others get killed. Lawyers love these kinds of cases. Protect yourself and protect others do it correctly.. Howard Truitt Camilla, Ga. 86 PT40 ----- Original Message ----- From: chet geist To: WanderlodgeForum@ yahoogroups. com Sent: Monday, January 15, 2007 11:49 AM Subject: RE: [WanderlodgeForum] Using Generator As Backup For House Power Ralph, I'm not an electrician, but in an emergency situation couldn't Eric just turn off the main disconnect on the outside of his house and then run extension cords? This should prevent sending power down the grid. Chet Geist 1981 FC33, Austin, Texas -----Original Message----- From: WanderlodgeForum@ yahoogroups. com [mailto:WanderlodgeForum@ yahoogroups. com]On Behalf Of Ralph L. Fullenwider Sent: Monday, January 15, 2007 9:55 AM To: WanderlodgeForum@ yahoogroups. com Subject: Re: [WanderlodgeForum] Using Generator As Backup For House Power Eric: Yes it is doable. You will need an auto transfer switch to switch out the power grid in coming from your utility company. Then install a buddy plug on your coach wired 220vac 50 amp and have a cable long enough to run from the coach to the house to another plug wired to the auto transfer switch. The transfer switch control would need to be wired so the default power is from the power grid. Reason for the transfer switch is to keep from feeding power into the electrical grid from your utility and fry someone working on the down power lines. And of course, to keep the power grid from feeding back into your genset. Safe travels, Ralph and Charolette Fullenwider ( iced in, in Oklahoma) 84FC35 Ralph's RV Solutions, Duncan, Oklahoma This is done with back up gen sets at hospitals and so forth. Check with your power company, they should have the info you need. At 03:05 PM 1/15/2007 +0000, you wrote: >Ice storms may bring loss of power to our home as in other areas of the >country so I brought >the coach to the house with the idea of moving into it if we have a >problem. Then I got to >thinking about using the generator to provide power to the home so we >could have heat and >lights. Has anyone else done this? What would be the best way to make >the connection so >you get maximum use of the generator capacity? > >Regards, Eric in San Antonio >84FC35SBWL2 > > [Non-text portions of this message have been removed] ------------ --------- --------- --------- --------- --------- - No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.1.410 / Virus Database: 268.16.8/621 - Release Date: 1/9/2007 [Non-text portions of this message have been removed] <!-- #ygrp-mlmsg {font-size:13px;font-family:arial,helvetica,clean,sans-serif;} #ygrp-mlmsg table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115% monospace;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{ font-family:Georgia; } #ygrp-text p{ margin:0 0 1em 0; } #ygrp-tpmsgs{ font-family:Arial; clear:both; } #ygrp-vitnav{ padding-top:10px; font-family:Verdana; font-size:77%; margin:0; } #ygrp-vitnav a{ padding:0 1px; } #ygrp-actbar{ clear:both; margin:25px 0; white-space:nowrap; color:#666; text-align:right; } #ygrp-actbar .left{ float:left; white-space:nowrap; } .bld{font-weight:bold;} #ygrp-grft{ font-family:Verdana; font-size:77%; padding:15px 0; } #ygrp-ft{ font-family:verdana; font-size:77%; border-top:1px solid #666; padding:5px 0; } #ygrp-mlmsg #logo{ padding-bottom:10px; } #ygrp-vital{ background-color:#e0ecee; margin-bottom:20px; padding:2px 0 8px 8px; } #ygrp-vital #vithd{ font-size:77%; font-family:Verdana; font-weight:bold; color:#333; text-transform:uppercase; } #ygrp-vital ul{ padding:0; margin:2px 0; } #ygrp-vital ul li{ list-style-type:none; clear:both; border:1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight:bold; color:#ff7900; float:right; width:2em; text-align:right; padding-right:.5em; } #ygrp-vital ul li .cat{ font-weight:bold; } #ygrp-vital a { text-decoration:none; } #ygrp-vital a:hover{ text-decoration:underline; } #ygrp-sponsor #hd{ color:#999; font-size:77%; } #ygrp-sponsor #ov{ padding:6px 13px; background-color:#e0ecee; margin-bottom:20px; } #ygrp-sponsor #ov ul{ padding:0 0 0 8px; margin:0; } #ygrp-sponsor #ov li{ list-style-type:square; padding:6px 0; font-size:77%; } #ygrp-sponsor #ov li a{ text-decoration:none; font-size:130%; } #ygrp-sponsor #nc { background-color:#eee; margin-bottom:20px; padding:0 8px; } #ygrp-sponsor .ad{ padding:8px 0; } #ygrp-sponsor .ad #hd1{ font-family:Arial; font-weight:bold; color:#628c2a; font-size:100%; line-height:122%; } #ygrp-sponsor .ad a{ text-decoration:none; } #ygrp-sponsor .ad a:hover{ text-decoration:underline; } #ygrp-sponsor .ad p{ margin:0; } o {font-size:0;} .MsoNormal { margin:0 0 0 0; } #ygrp-text tt{ font-size:120%; } blockquote{margin:0 0 0 4px;} .replbq {margin:4;} --> __________________________________________________ Do You Yahoo!? Tired of spam? Yahoo! Mail has the best spam protection around http://mail.yahoo.com [Non-text portions of this message have been removed] |
01-15-2007, 13:47
Greg:
With a proper setup, which is very costly to boot, you can have an alternative energy system feeding back into the grid.(yes getting paid for it) If the grid were to lose power, you would be immediately disconnected from the system, thus having the power for yourself. There are many types of systems, solar, wind, hydro and a mixture of them all. The biggest thing though, is it financially viable to have a system. And does the electric company buy into those programs everywhere. In BC now, BC Hydro is not going to construct any new facilities, it will all come through the Independent Power Producers, which we are one of, producing 960,000,000watts, or 960 MW per hour. About 1/2 hour up the road from us, a group of fellows are putting a proposal together to build a 5MW plant, and what I understand it is a viable proposition. Bill 84 FC 35 SB "$quanderlodge" Terrace, B.C. Canada --- In WanderlodgeForum@ yahoogroups. com, "Gregory OConnor" > > Bob, I wonder how the grid deals with the residential solar gen > stations homeowners set up?? Could your troybuilt scenario appear > here also? In fear of a $500. transfer switch , I stay out in the > motorhome for the short period of time lights and services are off. > > GregoryO'Connor > 94ptRomoland > > > > > > > <!-- #ygrp-mlmsg {font-size:13px;font-family:arial,helvetica,clean,sans-serif;} #ygrp-mlmsg table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115% monospace;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{ font-family:Georgia; } #ygrp-text p{ margin:0 0 1em 0; } #ygrp-tpmsgs{ font-family:Arial; clear:both; } #ygrp-vitnav{ padding-top:10px; font-family:Verdana; font-size:77%; margin:0; } #ygrp-vitnav a{ padding:0 1px; } #ygrp-actbar{ clear:both; margin:25px 0; white-space:nowrap; color:#666; text-align:right; } #ygrp-actbar .left{ float:left; white-space:nowrap; } .bld{font-weight:bold;} #ygrp-grft{ font-family:Verdana; font-size:77%; padding:15px 0; } #ygrp-ft{ font-family:verdana; font-size:77%; border-top:1px solid #666; padding:5px 0; } #ygrp-mlmsg #logo{ padding-bottom:10px; } #ygrp-vital{ background-color:#e0ecee; margin-bottom:20px; padding:2px 0 8px 8px; } #ygrp-vital #vithd{ font-size:77%; font-family:Verdana; font-weight:bold; color:#333; text-transform:uppercase; } #ygrp-vital ul{ padding:0; margin:2px 0; } #ygrp-vital ul li{ list-style-type:none; clear:both; border:1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight:bold; color:#ff7900; float:right; width:2em; text-align:right; padding-right:.5em; } #ygrp-vital ul li .cat{ font-weight:bold; } #ygrp-vital a { text-decoration:none; } #ygrp-vital a:hover{ text-decoration:underline; } #ygrp-sponsor #hd{ color:#999; font-size:77%; } #ygrp-sponsor #ov{ padding:6px 13px; background-color:#e0ecee; margin-bottom:20px; } #ygrp-sponsor #ov ul{ padding:0 0 0 8px; margin:0; } #ygrp-sponsor #ov li{ list-style-type:square; padding:6px 0; font-size:77%; } #ygrp-sponsor #ov li a{ text-decoration:none; font-size:130%; } #ygrp-sponsor #nc { background-color:#eee; margin-bottom:20px; padding:0 8px; } #ygrp-sponsor .ad{ padding:8px 0; } #ygrp-sponsor .ad #hd1{ font-family:Arial; font-weight:bold; color:#628c2a; font-size:100%; line-height:122%; } #ygrp-sponsor .ad a{ text-decoration:none; } #ygrp-sponsor .ad a:hover{ text-decoration:underline; } #ygrp-sponsor .ad p{ margin:0; } o {font-size:0;} .MsoNormal { margin:0 0 0 0; } #ygrp-text tt{ font-size:120%; } blockquote{margin:0 0 0 4px;} .replbq {margin:4;} --> __________________________________________________ Do You Yahoo!? Tired of spam? Yahoo! Mail has the best spam protection around http://mail.yahoo.com [Non-text portions of this message have been removed] |
01-16-2007, 03:04
We pay dearly for a used or new bird $20,000 to $800,000. Then $450.00 for
tires, $750.00 for a tank of fuel and thousands for other upgrades and quibble over the cost of a transfer switch. Howard Truitt Camilla, Ga. 86 PT40 ----- Original Message ----- From: Wilhelmus Schreurs To: WanderlodgeForum@yahoogroups.com Sent: Monday, January 15, 2007 8:33 PM Subject: Re: [WanderlodgeForum] Using Generator As Backup For House Power Howard: The key here is it must be a transfer switch, not necessarily "automatic". Automatic is nice, easy as well, but a manual is a lot cheaper, and you cannot go wrong, it is either main power or generator power - not both. Bill 84 FC 35 SB "$quanderlodge" Terrace, B.C. Canada ----- Original Message ---- From: Howard O. Truitt Sent: Monday, January 15, 2007 3:27:13 PM Subject: Re: [WanderlodgeForum] Using Generator As Backup For House Power Chet, You could throw the main breaker and seperate your house from the power company. But the correct way is with the automatic shut off. Folks forget proper procedures and others get killed. Lawyers love these kinds of cases. Protect yourself and protect others do it correctly.. Howard Truitt Camilla, Ga. 86 PT40 ----- Original Message ----- From: chet geist To: WanderlodgeForum@ yahoogroups. com Sent: Monday, January 15, 2007 11:49 AM Subject: RE: [WanderlodgeForum] Using Generator As Backup For House Power Ralph, I'm not an electrician, but in an emergency situation couldn't Eric just turn off the main disconnect on the outside of his house and then run extension cords? This should prevent sending power down the grid. Chet Geist 1981 FC33, Austin, Texas -----Original Message----- From: WanderlodgeForum@ yahoogroups. com [mailto:WanderlodgeForum@ yahoogroups. com]On Behalf Of Ralph L. Fullenwider Sent: Monday, January 15, 2007 9:55 AM To: WanderlodgeForum@ yahoogroups. com Subject: Re: [WanderlodgeForum] Using Generator As Backup For House Power Eric: Yes it is doable. You will need an auto transfer switch to switch out the power grid in coming from your utility company. Then install a buddy plug on your coach wired 220vac 50 amp and have a cable long enough to run from the coach to the house to another plug wired to the auto transfer switch. The transfer switch control would need to be wired so the default power is from the power grid. Reason for the transfer switch is to keep from feeding power into the electrical grid from your utility and fry someone working on the down power lines. And of course, to keep the power grid from feeding back into your genset. Safe travels, Ralph and Charolette Fullenwider ( iced in, in Oklahoma) 84FC35 Ralph's RV Solutions, Duncan, Oklahoma This is done with back up gen sets at hospitals and so forth. Check with your power company, they should have the info you need. At 03:05 PM 1/15/2007 +0000, you wrote: >Ice storms may bring loss of power to our home as in other areas of the >country so I brought >the coach to the house with the idea of moving into it if we have a >problem. Then I got to >thinking about using the generator to provide power to the home so we >could have heat and >lights. Has anyone else done this? What would be the best way to make >the connection so >you get maximum use of the generator capacity? > >Regards, Eric in San Antonio >84FC35SBWL2 > > [Non-text portions of this message have been removed] ------------ --------- --------- --------- --------- --------- - No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.1.410 / Virus Database: 268.16.8/621 - Release Date: 1/9/2007 [Non-text portions of this message have been removed] <!-- #ygrp-mlmsg {font-size:13px;font-family:arial,helvetica,clean,sans-serif;} #ygrp-mlmsg table {font-size:inherit;font:100%;} #ygrp-mlmsg select, input, textarea {font:99% arial,helvetica,clean,sans-serif;} #ygrp-mlmsg pre, code {font:115% monospace;} #ygrp-mlmsg * {line-height:1.22em;} #ygrp-text{ font-family:Georgia; } #ygrp-text p{ margin:0 0 1em 0; } #ygrp-tpmsgs{ font-family:Arial; clear:both; } #ygrp-vitnav{ padding-top:10px; font-family:Verdana; font-size:77%; margin:0; } #ygrp-vitnav a{ padding:0 1px; } #ygrp-actbar{ clear:both; margin:25px 0; white-space:nowrap; color:#666; text-align:right; } #ygrp-actbar .left{ float:left; white-space:nowrap; } .bld{font-weight:bold;} #ygrp-grft{ font-family:Verdana; font-size:77%; padding:15px 0; } #ygrp-ft{ font-family:verdana; font-size:77%; border-top:1px solid #666; padding:5px 0; } #ygrp-mlmsg #logo{ padding-bottom:10px; } #ygrp-vital{ background-color:#e0ecee; margin-bottom:20px; padding:2px 0 8px 8px; } #ygrp-vital #vithd{ font-size:77%; font-family:Verdana; font-weight:bold; color:#333; text-transform:uppercase; } #ygrp-vital ul{ padding:0; margin:2px 0; } #ygrp-vital ul li{ list-style-type:none; clear:both; border:1px solid #e0ecee; } #ygrp-vital ul li .ct{ font-weight:bold; color:#ff7900; float:right; width:2em; text-align:right; padding-right:.5em; } #ygrp-vital ul li .cat{ font-weight:bold; } #ygrp-vital a { text-decoration:none; } #ygrp-vital a:hover{ text-decoration:underline; } #ygrp-sponsor #hd{ color:#999; font-size:77%; } #ygrp-sponsor #ov{ padding:6px 13px; background-color:#e0ecee; margin-bottom:20px; } #ygrp-sponsor #ov ul{ padding:0 0 0 8px; margin:0; } #ygrp-sponsor #ov li{ list-style-type:square; padding:6px 0; font-size:77%; } #ygrp-sponsor #ov li a{ text-decoration:none; font-size:130%; } #ygrp-sponsor #nc { background-color:#eee; margin-bottom:20px; padding:0 8px; } #ygrp-sponsor .ad{ padding:8px 0; } #ygrp-sponsor .ad #hd1{ font-family:Arial; font-weight:bold; color:#628c2a; font-size:100%; line-height:122%; } #ygrp-sponsor .ad a{ text-decoration:none; } #ygrp-sponsor .ad a:hover{ text-decoration:underline; } #ygrp-sponsor .ad p{ margin:0; } o {font-size:0;} .MsoNormal { margin:0 0 0 0; } #ygrp-text tt{ font-size:120%; } blockquote{margin:0 0 0 4px;} .replbq {margin:4;} --> __________________________________________________ Do You Yahoo!? Tired of spam? Yahoo! Mail has the best spam protection around http://mail.yahoo.com [Non-text portions of this message have been removed] ------------------------------------------------------------------------------ No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.1.410 / Virus Database: 268.16.8/621 - Release Date: 1/9/2007 [Non-text portions of this message have been removed] |