generator won't stay running?
03-03-2007, 13:03
Post: #1
generator won't stay running?
I have a 12.5 Kolher with a Yanmar motor. From any of the switches
the generator will start but as soon as the start switch is released
it stops. I ran a temporary 12vdc jumper to the fuel solenoid to rule
out the safety shutdowns, same thing, it stops. I watched the voltage
gages while I held the switch in the start position to keep the motor
going. No AC registered on the gages and the radiator fan doesn't
come on either. I've had this problem recently twice before, but it
was intermittent and worked again after that, but now its
consistantly not working.
I checked the archives and have seen that other people have had this
problem, but I couldn't find any solutions.
Does anyone have any suggestions? I'd like to get it working before
Maxton!
Does house battery voltage have anything to do with the generator?

p.s. A Kohler dealer e-mailed (pdf file) me the parts manual and
service manuel, which Kinkos put into booklet form for me. If anybody
needs them I can e-mail them to you.

Tom Sorrentino
1987 PT38
Bedford Hills, NY
Quote this message in a reply
03-03-2007, 13:54
Post: #2
generator won't stay running?
Tom, check the latching ciruit created by an
oil pressure switch. This is a safely device
to prevent running of the engine with no oil.
bob janes, greenville, sc


--- In WanderlodgeForum@yahoogroups.com, "thomas_sorrentino"
wrote:
>
> I have a 12.5 Kolher with a Yanmar motor. From any of the switches
> the generator will start but as soon as the start switch is
released
> it stops. I ran a temporary 12vdc jumper to the fuel solenoid to
rule
> out the safety shutdowns, same thing, it stops. I watched the
voltage
> gages while I held the switch in the start position to keep the
motor
> going. No AC registered on the gages and the radiator fan doesn't
> come on either. I've had this problem recently twice before, but it
> was intermittent and worked again after that, but now its
> consistantly not working.
> I checked the archives and have seen that other people have had
this
> problem, but I couldn't find any solutions.
> Does anyone have any suggestions? I'd like to get it working before
> Maxton!
> Does house battery voltage have anything to do with the generator?
>
> p.s. A Kohler dealer e-mailed (pdf file) me the parts manual and
> service manuel, which Kinkos put into booklet form for me. If
anybody
> needs them I can e-mail them to you.
>
> Tom Sorrentino
> 1987 PT38
> Bedford Hills, NY
>
Quote this message in a reply
03-03-2007, 14:02
Post: #3
generator won't stay running?
Bob,
Correct me if I'm wrong but I thought running the temp. 12vdc jumper
to the fuel solenoid bypassed that?

Tom Sorrentino
1987 PT38
Bedford HIlls, NY

--- In WanderlodgeForum@yahoogroups.com, "one_dusty_hoot"
wrote:
>
> Tom, check the latching ciruit created by an
> oil pressure switch. This is a safely device
> to prevent running of the engine with no oil.
> bob janes, greenville, sc
>
>
> --- In WanderlodgeForum@yahoogroups.com, "thomas_sorrentino"
> wrote:
> >
> > I have a 12.5 Kolher with a Yanmar motor. From any of the
switches
> > the generator will start but as soon as the start switch is
> released
> > it stops. I ran a temporary 12vdc jumper to the fuel solenoid to
> rule
> > out the safety shutdowns, same thing, it stops. I watched the
> voltage
> > gages while I held the switch in the start position to keep the
> motor
> > going. No AC registered on the gages and the radiator fan doesn't
> > come on either. I've had this problem recently twice before, but
it
> > was intermittent and worked again after that, but now its
> > consistantly not working.
> > I checked the archives and have seen that other people have had
> this
> > problem, but I couldn't find any solutions.
> > Does anyone have any suggestions? I'd like to get it working
before
> > Maxton!
> > Does house battery voltage have anything to do with the generator?
> >
> > p.s. A Kohler dealer e-mailed (pdf file) me the parts manual and
> > service manuel, which Kinkos put into booklet form for me. If
> anybody
> > needs them I can e-mail them to you.
> >
> > Tom Sorrentino
> > 1987 PT38
> > Bedford Hills, NY
> >
>
Quote this message in a reply
03-03-2007, 16:36
Post: #4
generator won't stay running?
Tom: I had a similar, not exactly as you explained, problem. It turned out to
be a failing fuel pump. It was pumping just enough fuel to get it going but not
enough to run. I put a new one on and have been fine since. The overtemp sensor
can shut you down if it is bad. Pull the wire off and see if it runs.

Leroy Eckert
1990 WB-40"Smoke N Mirrors"
Niceville, FL



----- Original Message -----
From: thomas_sorrentino
To: WanderlodgeForum@yahoogroups.com
Sent: Saturday, March 03, 2007 7:03 PM
Subject: [WanderlodgeForum] generator won't stay running?


I have a 12.5 Kolher with a Yanmar motor. From any of the switches
the generator will start but as soon as the start switch is released
it stops. I ran a temporary 12vdc jumper to the fuel solenoid to rule
out the safety shutdowns, same thing, it stops. I watched the voltage
gages while I held the switch in the start position to keep the motor
going. No AC registered on the gages and the radiator fan doesn't
come on either. I've had this problem recently twice before, but it
was intermittent and worked again after that, but now its
consistantly not working.
I checked the archives and have seen that other people have had this
problem, but I couldn't find any solutions.
Does anyone have any suggestions? I'd like to get it working before
Maxton!
Does house battery voltage have anything to do with the generator?

p.s. A Kohler dealer e-mailed (pdf file) me the parts manual and
service manuel, which Kinkos put into booklet form for me. If anybody
needs them I can e-mail them to you.

Tom Sorrentino
1987 PT38
Bedford Hills, NY





[Non-text portions of this message have been removed]
Quote this message in a reply
03-03-2007, 17:20
Post: #5
generator won't stay running?
Tom:

The fuel sol is held in by the S/R contacts on the start solenoid. If the
low oil pressure or high water temp shorts to ground ( defective) it is the
same as hitting the stop switch.

Also go under with the gen slid out, remove the rear cover on the Kohler,
there is a fuse and diode on the quadrature windings, check those, Inspect
the brushes and slip rings they ride on and check the L1/L2 and Neutral
wires on the isolated lugs to be sure they are tight. After that you want
to measure at the isolated studs L1 to neutral for A/C while someone holds
the start button. There is an A/C relay in the control box that pulls in
when there is voltage on L1 and Neutral, the A/c relay is the one that sets
up the holding contacts for run. If no voltage, check for 12 vdc on the
brushes. If you have 12 vdc on the brushes then it is a good bet that the
regulator is out.

Safe travels,

Ralph and Charolette Fullenwider
84FC35
Ralph's RV Solutions, Duncan, Oklahoma

At 01:03 AM 3/4/2007 +0000, you wrote:
>I have a 12.5 Kolher with a Yanmar motor. From any of the switches
>the generator will start but as soon as the start switch is released
>it stops. I ran a temporary 12vdc jumper to the fuel solenoid to rule
>out the safety shutdowns, same thing, it stops. I watched the voltage
>gages while I held the switch in the start position to keep the motor
>going. No AC registered on the gages and the radiator fan doesn't
>come on either. I've had this problem recently twice before, but it
>was intermittent and worked again after that, but now its
>consistantly not working.
>I checked the archives and have seen that other people have had this
>problem, but I couldn't find any solutions.
>Does anyone have any suggestions? I'd like to get it working before
>Maxton!
>Does house battery voltage have anything to do with the generator?
>
>p.s. A Kohler dealer e-mailed (pdf file) me the parts manual and
>service manuel, which Kinkos put into booklet form for me. If anybody
>needs them I can e-mail them to you.
>
>Tom Sorrentino
>1987 PT38
>Bedford Hills, NY
>
>
>
>
>
>Yahoo! Groups Links
>
>
>

Safe travels,

Ralph and Charolette Fullenwider
84FC35
Ralph's RV Solutions, Duncan, Oklahoma
Quote this message in a reply
03-04-2007, 00:23
Post: #6
generator won't stay running?
Had the same problem with the same setup as yours. It was the
brushes. The holder broke and destroyed the stator. Replaced both.

I'd appreciate a copy of your manual if you don't mind.... Thanks
rlfaubion at yahoo dot com

Ron, No. California
85PT36

>No AC registered on the gages and the radiator fan doesn't
>come on either. Does house battery voltage have anything to do with
the >generator?
>
> p.s. A Kohler dealer e-mailed (pdf file) me the parts manual and
> service manuel, which Kinkos put into booklet form for me. If anybody
> needs them I can e-mail them to you.
>
> Tom Sorrentino
> 1987 PT38
> Bedford Hills, NY
>
Quote this message in a reply
03-04-2007, 05:07
Post: #7
generator won't stay running?
Check and see if you have a fuel bleed valve on the passenger side
of the engine going into the injector pump. If you do, it should only
be open about 1/2 to 3/4 turn. On my unit, the lock nut had vibrated
loose and the valve was fully open and returning all the fuel to the
tank rather than the pump.

R.E. (Ron) Marabito, Dallas, TX 92WB40


--- In WanderlodgeForum@yahoogroups.com, "thomas_sorrentino"
wrote:
>
> I have a 12.5 Kolher with a Yanmar motor. From any of the switches
> the generator will start but as soon as the start switch is released
> it stops. I ran a temporary 12vdc jumper to the fuel solenoid to rule
> out the safety shutdowns, same thing, it stops. I watched the voltage
> gages while I held the switch in the start position to keep the motor
> going. No AC registered on the gages and the radiator fan doesn't
> come on either. I've had this problem recently twice before, but it
> was intermittent and worked again after that, but now its
> consistantly not working.
> I checked the archives and have seen that other people have had this
> problem, but I couldn't find any solutions.
> Does anyone have any suggestions? I'd like to get it working before
> Maxton!
> Does house battery voltage have anything to do with the generator?
>
> p.s. A Kohler dealer e-mailed (pdf file) me the parts manual and
> service manuel, which Kinkos put into booklet form for me. If anybody
> needs them I can e-mail them to you.
>
> Tom Sorrentino
> 1987 PT38
> Bedford Hills, NY
>