Chassis heat problems
|
03-16-2008, 10:29
Post: #21
|
|||
|
|||
Chassis heat problems
The front valve on mine should keep the front radiator cool when the slide is in
the cool position, but I can see where manual override might be needed. Both of my gate valves are at similar heights. For reference for anyone following this thread I've put up a picture with components labeled, here: http://www.arcatapet.net/image/heaterplumbing.jpg When I took the top off the Graco pump I lost nearly 5 gallons of coolant! I'm guessing that is because the top of the radiator is higher still. Couldn't stop the flow, because the gasket got ripped/destroyed in the removal. I wouldn't want to try to remove either valve without draining a lot, first! On 3/16/2008 at 1:15 PM Leroy Eckert wrote: >Shane may have a different theory. >Straight through-I guess the theory for the valves in the first place may >be two fold. One to cut off the hot water to the heater core in summer. I >never close mine and have not noticed any difference. The fans are off as >are the slide switch. The hot air blows out of different vents than the >chassis air. Two, if a leak developed forward of the engine the gate >valves would stop the leak until repaired. "???????" > >My valves bottom and top out. > >I do not know where the best place to drain is located. I can see how I >could change the valve that screws into the right thermostat housing >without draining and not have much fluid loss. The other one on my coach >is down low in front of the rear bumper and may be another issue. > >Leroy Eckert >1990 WB-40 Smoke N Mirrors >Dahlonega, GA >Royale Conversion > >Don Bradner >Three questions: > > Why replace the valve at all, rather than a straight-through? > > Did the handle still come to a stop at each end of travel (mine do)? > > Where do you drain the coolant in order to get it low enough to remove >the valves? > > On 3/16/2008 at 4:41 PM sfedeli3 wrote: > > >Good luck! I sure hope it fixes your problem. I was so darn confounded > >with mine that I eventually gave up and just listened to Kelly > >complain about cold feet. Finding the dropped gate was purely > >accidental. The R&R on the water pump was just some "preventative" > >maintenance that I had elected to do. > > > >-- In WanderlodgeForum@yahoogroups.com, "Don Bradner" > > > >> > >> Shane, that's a new one, thanks! > >> > >> Don Bradner > >> 90 PT40 "Blue Thunder" > >> Eureka, CA > >> > >> On 3/16/2008 at 11:13 AM sfedeli3 wrote: > >> > >> >Hi Don, > >> > > >> > My guess is that one of your gate valves "dropped". Even though the > >> > valve handle is turning, the inner gate is not lifting. My front heat > >> >circuit did not work for 3 years. Tried flushing the entire loop, > >> >replacing sporlans, relays, dash switches, circulating pump and still > >> >no heat. Finally, removed the gate valve when I pulled the water pump > >> >to replace it and saw that the gate was in the down position. The > >> >inner threads had eroded and when you rotated the handle, nothing > >> >would happen to the gate. I've replaced 2 of the 4 valves with ball > >> >valves. > >> > > >> >Shane Fedeli > >> >85PT40 > >> >Hershey, PA > >> > > > > > > > > >------------------------------------ > > > >Yahoo! Groups Links > > > > > > > > > > > > >--------------------------------- >Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try it >now. |
|||
03-16-2008, 11:28
Post: #22
|
|||
|
|||
Chassis heat problems
I know you will post the result when you find out. I took your photo and looked at mine. If I have a sporlan valve in my system it is in parts unknown. Strange. I don't have any other ideas except something is interrupting the flow in the loop assuming the Graco is actually pumping properly. Did you check the Graco for flow on the bench?
Leroy Eckert 1990 WB-40 Smoke N Mirrors Dahlonega, GA Don Bradner
Looking for last minute shopping deals? Find them fast with Yahoo! Search. |
|||
03-16-2008, 11:51
Post: #23
|
|||
|
|||
Chassis heat problems
I did not pull and bench test the pump. It is pump design I'm very familiar with
(sold a lot of that design over the years), and is mighty simple. So long as it turns easily (it does) and has no broken blades (it doesn't) there isn't much to go wrong. This design has no problems with blockages - it will turn freely without pumping anything. On 3/16/2008 at 3:28 PM Leroy Eckert wrote: >I know you will post the result when you find out. I took your photo and >looked at mine. If I have a sporlan valve in my system it is in parts >unknown. Strange. I don't have any other ideas except something is >interrupting the flow in the loop assuming the Graco is actually pumping >properly. Did you check the Graco for flow on the bench? > >Leroy Eckert >1990 WB-40 Smoke N Mirrors >Dahlonega, GA > >Don Bradner >The front valve on mine should keep the front radiator cool when the slide >is in the cool position, but I can see where manual override might be >needed. > > Both of my gate valves are at similar heights. For reference for anyone >following this thread I've put up a picture with components labeled, here: > http://www.arcatapet.net/image/heaterplumbing.jpg > > When I took the top off the Graco pump I lost nearly 5 gallons of >coolant! I'm guessing that is because the top of the radiator is higher >still. Couldn't stop the flow, because the gasket got ripped/destroyed in >the removal. I wouldn't want to try to remove either valve without >draining a lot, first! > > On 3/16/2008 at 1:15 PM Leroy Eckert wrote: > > >Shane may have a different theory. > >Straight through-I guess the theory for the valves in the first place may > >be two fold. One to cut off the hot water to the heater core in summer. I > >never close mine and have not noticed any difference. The fans are off as > >are the slide switch. The hot air blows out of different vents than the > >chassis air. Two, if a leak developed forward of the engine the gate > >valves would stop the leak until repaired. "???????" > > > >My valves bottom and top out. > > > >I do not know where the best place to drain is located. I can see how I > >could change the valve that screws into the right thermostat housing > >without draining and not have much fluid loss. The other one on my coach > >is down low in front of the rear bumper and may be another issue. > > > >Leroy Eckert > >1990 WB-40 Smoke N Mirrors > >Dahlonega, GA > >Royale Conversion > > > >Don Bradner > > >Three questions: > > > > Why replace the valve at all, rather than a straight-through? > > > > Did the handle still come to a stop at each end of travel (mine do)? > > > > Where do you drain the coolant in order to get it low enough to remove > >the valves? > > > > On 3/16/2008 at 4:41 PM sfedeli3 wrote: > > > > >Good luck! I sure hope it fixes your problem. I was so darn confounded > > >with mine that I eventually gave up and just listened to Kelly > > >complain about cold feet. Finding the dropped gate was purely > > >accidental. The R&R on the water pump was just some "preventative" > > >maintenance that I had elected to do. > > > > > >-- In WanderlodgeForum@yahoogroups.com, "Don Bradner" > > > > > >> > > >> Shane, that's a new one, thanks! > > >> > > >> Don Bradner > > >> 90 PT40 "Blue Thunder" > > >> Eureka, CA > > >> > > >> On 3/16/2008 at 11:13 AM sfedeli3 wrote: > > >> > > >> >Hi Don, > > >> > > > >> > My guess is that one of your gate valves "dropped". Even though >the > > >> > valve handle is turning, the inner gate is not lifting. My front >heat > > >> >circuit did not work for 3 years. Tried flushing the entire loop, > > >> >replacing sporlans, relays, dash switches, circulating pump and >still > > >> >no heat. Finally, removed the gate valve when I pulled the water >pump > > >> >to replace it and saw that the gate was in the down position. The > > >> >inner threads had eroded and when you rotated the handle, nothing > > >> >would happen to the gate. I've replaced 2 of the 4 valves with ball > > >> >valves. > > >> > > > >> >Shane Fedeli > > >> >85PT40 > > >> >Hershey, PA > > >> > > > > > > > > > > > > >------------------------------------ > > > > > >Yahoo! Groups Links > > > > > > > > > > > > > > > > > > > > > > >--------------------------------- > >Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try >it > >now. > > > > > > >--------------------------------- >Looking for last minute shopping deals? Find them fast with Yahoo! Search. |
|||
03-16-2008, 12:23
Post: #24
|
|||
|
|||
Chassis heat problems
Don,
This is a far out possibility, but, searching for an explanation. I have found some strange wireing errors on my Bird. These Birds were hand wired , and easy to make a mistake, with color-coding and thousands of connections. So, My suggestion is to check the polarity of the 12 volts, the pump may be turning in reverse. Bill 88 FC Michigan --- In WanderlodgeForum@yahoogroups.com, "Don Bradner" > > I did not pull and bench test the pump. It is pump design I'm very familiar with (sold a lot of that design over the years), and is mighty simple. So long as it turns easily (it does) and has no broken blades (it doesn't) there isn't much to go wrong. This design has no problems with blockages - it will turn freely without pumping anything. > > On 3/16/2008 at 3:28 PM Leroy Eckert wrote: > > >I know you will post the result when you find out. I took your photo and > >looked at mine. If I have a sporlan valve in my system it is in parts > >unknown. Strange. I don't have any other ideas except something is > >interrupting the flow in the loop assuming the Graco is actually pumping > >properly. Did you check the Graco for flow on the bench? > > > >Leroy Eckert > >1990 WB-40 Smoke N Mirrors > >Dahlonega, GA > > > >Don Bradner > >The front valve on mine should keep the front radiator cool when the slide > >is in the cool position, but I can see where manual override might be > >needed. > > > > Both of my gate valves are at similar heights. For reference for anyone > >following this thread I've put up a picture with components labeled, here: > > http://www.arcatapet.net/image/heaterplumbing.jpg > > > > When I took the top off the Graco pump I lost nearly 5 gallons of > >coolant! I'm guessing that is because the top of the radiator is higher > >still. Couldn't stop the flow, because the gasket got ripped/destroyed in > >the removal. I wouldn't want to try to remove either valve without > >draining a lot, first! > > > > On 3/16/2008 at 1:15 PM Leroy Eckert wrote: > > > > >Shane may have a different theory. > > >Straight through-I guess the theory for the valves in the first place may > > >be two fold. One to cut off the hot water to the heater core in summer. I > > >never close mine and have not noticed any difference. The fans are off as > > >are the slide switch. The hot air blows out of different vents than the > > >chassis air. Two, if a leak developed forward of the engine the gate > > >valves would stop the leak until repaired. "???????" > > > > > >My valves bottom and top out. > > > > > >I do not know where the best place to drain is located. I can see how I > > >could change the valve that screws into the right thermostat housing > > >without draining and not have much fluid loss. The other one on my coach > > >is down low in front of the rear bumper and may be another issue. > > > > > >Leroy Eckert > > >1990 WB-40 Smoke N Mirrors > > >Dahlonega, GA > > >Royale Conversion > > > > > >Don Bradner > > > > >Three questions: > > > > > > Why replace the valve at all, rather than a straight-through? > > > > > > Did the handle still come to a stop at each end of travel (mine do)? > > > > > > Where do you drain the coolant in order to get it low enough to remove > > >the valves? > > > > > > On 3/16/2008 at 4:41 PM sfedeli3 wrote: > > > > > > >Good luck! I sure hope it fixes your problem. I was so darn confounded > > > >with mine that I eventually gave up and just listened to Kelly > > > >complain about cold feet. Finding the dropped gate was purely > > > >accidental. The R&R on the water pump was just some "preventative" > > > >maintenance that I had elected to do. > > > > > > > >-- In WanderlodgeForum@yahoogroups.com, "Don Bradner" > > > > > > > >> > > > >> Shane, that's a new one, thanks! > > > >> > > > >> Don Bradner > > > >> 90 PT40 "Blue Thunder" > > > >> Eureka, CA > > > >> > > > >> On 3/16/2008 at 11:13 AM sfedeli3 wrote: > > > >> > > > >> >Hi Don, > > > >> > > > > >> > My guess is that one of your gate valves "dropped". Even though > >the > > > >> > valve handle is turning, the inner gate is not lifting. My front > >heat > > > >> >circuit did not work for 3 years. Tried flushing the entire loop, > > > >> >replacing sporlans, relays, dash switches, circulating pump and > >still > > > >> >no heat. Finally, removed the gate valve when I pulled the water > >pump > > > >> >to replace it and saw that the gate was in the down position. The > > > >> >inner threads had eroded and when you rotated the handle, nothing > > > >> >would happen to the gate. I've replaced 2 of the 4 valves with ball > > > >> >valves. > > > >> > > > > >> >Shane Fedeli > > > >> >85PT40 > > > >> >Hershey, PA > > > >> > > > > > > > > > > > > > > > > >------------------------------------ > > > > > > > >Yahoo! Groups Links > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > >--------------------------------- > > >Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try > >it > > >now. > > > > > > > > > > > > > >--------------------------------- > >Looking for last minute shopping deals? Find them fast with Yahoo! Search. > |
|||
03-16-2008, 12:29
Post: #25
|
|||
|
|||
Chassis heat problems
For info.
One thing that I learned working on the climate control of my old MBZ is I never drain the radiator because the system is a pain to purge. It also has a aux water pump. I simply pull the hose off and plug it with a rubber plug or cork. I did the same when I had to change the pump on my Webasto. Minimal fluid loss. Leroy Eckert 1990 WB-40 Smoke N Mirrors Dahlonega, GA Don Bradner
Never miss a thing. Make Yahoo your homepage. |
|||
03-16-2008, 12:38
Post: #26
|
|||
|
|||
Chassis heat problems
I've seen a lot of strange wiring as well, but that's not the issue here. Even
if the system hadn't worked fine until a few weeks ago, I did observe the rotational direction with the head off, and it is correct. This type of pump will probably move fluid in the right direction when turning the wrong way, although output will be reduced. It works by "throwing" the water outward from the center intake to the exterior output. Since the output line is off-center it is certainly designed to work in one direction, but centrifugal force will still move it outwards if turning the wrong way. On 3/16/2008 at 11:23 PM pattypape wrote: >Don, > >This is a far out possibility, but, searching for an explanation. >I have found some strange wireing errors on my Bird. These Birds >were hand wired , and easy to make a mistake, with color-coding and >thousands of connections. >So, My suggestion is to check the polarity of the 12 volts, the pump >may be turning in reverse. > >Bill 88 FC Michigan > >--- In WanderlodgeForum@yahoogroups.com, "Don Bradner" > >> >> I did not pull and bench test the pump. It is pump design I'm very >familiar with (sold a lot of that design over the years), and is >mighty simple. So long as it turns easily (it does) and has no broken >blades (it doesn't) there isn't much to go wrong. This design has no >problems with blockages - it will turn freely without pumping >anything. >> >> On 3/16/2008 at 3:28 PM Leroy Eckert wrote: >> >> >I know you will post the result when you find out. I took your >photo and >> >looked at mine. If I have a sporlan valve in my system it is in >parts >> >unknown. Strange. I don't have any other ideas except something is >> >interrupting the flow in the loop assuming the Graco is actually >pumping >> >properly. Did you check the Graco for flow on the bench? >> > >> >Leroy Eckert >> >1990 WB-40 Smoke N Mirrors >> >Dahlonega, GA >> > >> >Don Bradner >> >The front valve on mine should keep the front radiator cool when >the slide >> >is in the cool position, but I can see where manual override might >be >> >needed. >> > >> > Both of my gate valves are at similar heights. For reference for >anyone >> >following this thread I've put up a picture with components >labeled, here: >> > http://www.arcatapet.net/image/heaterplumbing.jpg >> > >> > When I took the top off the Graco pump I lost nearly 5 gallons of >> >coolant! I'm guessing that is because the top of the radiator is >higher >> >still. Couldn't stop the flow, because the gasket got >ripped/destroyed in >> >the removal. I wouldn't want to try to remove either valve without >> >draining a lot, first! >> > >> > On 3/16/2008 at 1:15 PM Leroy Eckert wrote: >> > >> > >Shane may have a different theory. >> > >Straight through-I guess the theory for the valves in the first >place may >> > >be two fold. One to cut off the hot water to the heater core in >summer. I >> > >never close mine and have not noticed any difference. The fans >are off as >> > >are the slide switch. The hot air blows out of different vents >than the >> > >chassis air. Two, if a leak developed forward of the engine the >gate >> > >valves would stop the leak until repaired. "???????" >> > > >> > >My valves bottom and top out. >> > > >> > >I do not know where the best place to drain is located. I can >see how I >> > >could change the valve that screws into the right thermostat >housing >> > >without draining and not have much fluid loss. The other one on >my coach >> > >is down low in front of the rear bumper and may be another issue. >> > > >> > >Leroy Eckert >> > >1990 WB-40 Smoke N Mirrors >> > >Dahlonega, GA >> > >Royale Conversion >> > > >> > >Don Bradner >> > >> > >Three questions: >> > > >> > > Why replace the valve at all, rather than a straight-through? >> > > >> > > Did the handle still come to a stop at each end of travel (mine >do)? >> > > >> > > Where do you drain the coolant in order to get it low enough to >remove >> > >the valves? >> > > >> > > On 3/16/2008 at 4:41 PM sfedeli3 wrote: >> > > >> > > >Good luck! I sure hope it fixes your problem. I was so darn >confounded >> > > >with mine that I eventually gave up and just listened to Kelly >> > > >complain about cold feet. Finding the dropped gate was purely >> > > >accidental. The R&R on the water pump was just >some "preventative" >> > > >maintenance that I had elected to do. >> > > > >> > > >-- In WanderlodgeForum@yahoogroups.com, "Don Bradner" >> > > > >> > > >> >> > > >> Shane, that's a new one, thanks! >> > > >> >> > > >> Don Bradner >> > > >> 90 PT40 "Blue Thunder" >> > > >> Eureka, CA >> > > >> >> > > >> On 3/16/2008 at 11:13 AM sfedeli3 wrote: >> > > >> >> > > >> >Hi Don, >> > > >> > >> > > >> > My guess is that one of your gate valves "dropped". Even >though >> >the >> > > >> > valve handle is turning, the inner gate is not lifting. My >front >> >heat >> > > >> >circuit did not work for 3 years. Tried flushing the entire >loop, >> > > >> >replacing sporlans, relays, dash switches, circulating pump >and >> >still >> > > >> >no heat. Finally, removed the gate valve when I pulled the >water >> >pump >> > > >> >to replace it and saw that the gate was in the down >position. The >> > > >> >inner threads had eroded and when you rotated the handle, >nothing >> > > >> >would happen to the gate. I've replaced 2 of the 4 valves >with ball >> > > >> >valves. >> > > >> > >> > > >> >Shane Fedeli >> > > >> >85PT40 >> > > >> >Hershey, PA >> > > >> > >> > > > >> > > > >> > > > >> > > >------------------------------------ >> > > > >> > > >Yahoo! Groups Links >> > > > >> > > > >> > > > >> > > >> > > >> > > >> > > >> > > >> > > >> > >--------------------------------- >> > >Be a better friend, newshound, and know-it-all with Yahoo! >Mobile. Try >> >it >> > >now. >> > >> > >> > >> > >> > >> > >> >--------------------------------- >> >Looking for last minute shopping deals? Find them fast with >Yahoo! Search. >> > > > >------------------------------------ > >Yahoo! Groups Links > > > |
|||
03-16-2008, 13:18
Post: #27
|
|||
|
|||
Chassis heat problems
Sent from my Verizon Wireless BlackBerry
-----Original Message----- From: "Don Bradner" Date: Sun, 16 Mar 2008 16:38:13 To:WanderlodgeForum@yahoogroups.com Subject: Re: [WanderlodgeForum] Re: Chassis heat problems I've seen a lot of strange wiring as well, but that's not the issue here. Even if the system hadn't worked fine until a few weeks ago, I did observe the rotational direction with the head off, and it is correct. This type of pump will probably move fluid in the right direction when turning the wrong way, although output will be reduced. It works by "throwing" the water outward from the center intake to the exterior output. Since the output line is off-center it is certainly designed to work in one direction, but centrifugal force will still move it outwards if turning the wrong way. On 3/16/2008 at 11:23 PM pattypape wrote: >Don, > >This is a far out possibility, but, searching for an explanation. >I have found some strange wireing errors on my Bird. These Birds >were hand wired , and easy to make a mistake, with color-coding and >thousands of connections. >So, My suggestion is to check the polarity of the 12 volts, the pump >may be turning in reverse. > >Bill 88 FC Michigan > >--- In WanderlodgeForum@ yahoogroups.com, "Don Bradner" > >> >> I did not pull and bench test the pump. It is pump design I'm very >familiar with (sold a lot of that design over the years), and is >mighty simple. So long as it turns easily (it does) and has no broken >blades (it doesn't) there isn't much to go wrong. This design has no >problems with blockages - it will turn freely without pumping >anything. >> >> On 3/16/2008 at 3:28 PM Leroy Eckert wrote: >> >> >I know you will post the result when you find out. I took your >photo and >> >looked at mine. If I have a sporlan valve in my system it is in >parts >> >unknown. Strange. I don't have any other ideas except something is >> >interrupting the flow in the loop assuming the Graco is actually >pumping >> >properly. Did you check the Graco for flow on the bench? >> > >> >Leroy Eckert >> >1990 WB-40 Smoke N Mirrors >> >Dahlonega, GA >> > >> >Don Bradner >> >The front valve on mine should keep the front radiator cool when >the slide >> >is in the cool position, but I can see where manual override might >be >> >needed. >> > >> > Both of my gate valves are at similar heights. For reference for >anyone >> >following this thread I've put up a picture with components >labeled, here: >> > http://www.arcatape <http://www.arcatapet.net/image/heaterplumbing.jpg> t.net/image/heaterplumbing.jpg >> > >> > When I took the top off the Graco pump I lost nearly 5 gallons of >> >coolant! I'm guessing that is because the top of the radiator is >higher >> >still. Couldn't stop the flow, because the gasket got >ripped/destroyed in >> >the removal. I wouldn't want to try to remove either valve without >> >draining a lot, first! >> > >> > On 3/16/2008 at 1:15 PM Leroy Eckert wrote: >> > >> > >Shane may have a different theory. >> > >Straight through-I guess the theory for the valves in the first >place may >> > >be two fold. One to cut off the hot water to the heater core in >summer. I >> > >never close mine and have not noticed any difference. The fans >are off as >> > >are the slide switch. The hot air blows out of different vents >than the >> > >chassis air. Two, if a leak developed forward of the engine the >gate >> > >valves would stop the leak until repaired. "???????" >> > > >> > >My valves bottom and top out. >> > > >> > >I do not know where the best place to drain is located. I can >see how I >> > >could change the valve that screws into the right thermostat >housing >> > >without draining and not have much fluid loss. The other one on >my coach >> > >is down low in front of the rear bumper and may be another issue. >> > > >> > >Leroy Eckert >> > >1990 WB-40 Smoke N Mirrors >> > >Dahlonega, GA >> > >Royale Conversion >> > > >> > >Don Bradner >> > >> > >Three questions: >> > > >> > > Why replace the valve at all, rather than a straight-through? >> > > >> > > Did the handle still come to a stop at each end of travel (mine >do)? >> > > >> > > Where do you drain the coolant in order to get it low enough to >remove >> > >the valves? >> > > >> > > On 3/16/2008 at 4:41 PM sfedeli3 wrote: >> > > >> > > >Good luck! I sure hope it fixes your problem. I was so darn >confounded >> > > >with mine that I eventually gave up and just listened to Kelly >> > > >complain about cold feet. Finding the dropped gate was purely >> > > >accidental. The R&R on the water pump was just >some "preventative" >> > > >maintenance that I had elected to do. >> > > > >> > > >-- In WanderlodgeForum@ yahoogroups.com, "Don Bradner" >> > > > >> > > >> >> > > >> Shane, that's a new one, thanks! >> > > >> >> > > >> Don Bradner >> > > >> 90 PT40 "Blue Thunder" >> > > >> Eureka, CA >> > > >> >> > > >> On 3/16/2008 at 11:13 AM sfedeli3 wrote: >> > > >> >> > > >> >Hi Don, >> > > >> > >> > > >> > My guess is that one of your gate valves "dropped". Even >though >> >the >> > > >> > valve handle is turning, the inner gate is not lifting. My >front >> >heat >> > > >> >circuit did not work for 3 years. Tried flushing the entire >loop, >> > > >> >replacing sporlans, relays, dash switches, circulating pump >and >> >still >> > > >> >no heat. Finally, removed the gate valve when I pulled the >water >> >pump >> > > >> >to replace it and saw that the gate was in the down >position. The >> > > >> >inner threads had eroded and when you rotated the handle, >nothing >> > > >> >would happen to the gate. I've replaced 2 of the 4 valves >with ball >> > > >> >valves. >> > > >> > >> > > >> >Shane Fedeli >> > > >> >85PT40 >> > > >> >Hershey, PA >> > > >> > >> > > > >> > > > >> > > > >> > > >------------------------------------ >> > > > >> > > >Yahoo! Groups Links >> > > > >> > > > >> > > > >> > > >> > > >> > > >> > > >> > > >> > > >> > >--------------------------------- >> > >Be a better friend, newshound, and know-it-all with Yahoo! >Mobile. Try >> >it >> > >now. >> > >> > >> > >> > >> > >> > >> >--------------------------------- >> >Looking for last minute shopping deals? Find them fast with >Yahoo! Search. >> > > > >------------------------------------ > >Yahoo! Groups Links > > > |
|||
03-16-2008, 13:25
Post: #28
|
|||
|
|||
Chassis heat problems
Chris, did you have some input on this problem? Nothing came through except the
quoted message(s). On 3/17/2008 at 12:18 AM cfogleman@... wrote: >Sent from my Verizon Wireless BlackBerry > >-----Original Message----- >From: "Don Bradner" > >Date: Sun, 16 Mar 2008 16:38:13 >To:WanderlodgeForum@yahoogroups.com >Subject: Re: [WanderlodgeForum] Re: Chassis heat problems > > >I've seen a lot of strange wiring as well, but that's not the issue here. >Even if the system hadn't worked fine until a few weeks ago, I did observe >the rotational direction with the head off, and it is correct. This type >of pump will probably move fluid in the right direction when turning the >wrong way, although output will be reduced. It works by "throwing" the >water outward from the center intake to the exterior output. Since the >output line is off-center it is certainly designed to work in one >direction, but centrifugal force will still move it outwards if turning >the wrong way. |
|||
03-16-2008, 14:22
Post: #29
|
|||
|
|||
Chassis heat problems
Ernie, it is odd. I communicate with a person who uses Blackberry while driving the Autobahn at 100 mph and all is well.
I have received the same message in the past. Leroy Eckert 1990 WB-40 Smoke N Mirrors Dahlonega, GA erniecarpet@... wrote:
Be a better friend, newshound, and know-it-all with Yahoo! Mobile. [url=http://us.rd.yahoo.com/evt=51733/*http://mobile.yahoo.com/;_ylt=Ahu06i62sR...o8Wcj9tAcJ ] Try it now.[/url] |
|||
03-16-2008, 23:49
Post: #30
|
|||
|
|||
Chassis heat problems
Hi Don,
Yes, the handle would rotate through to the open and closed stops, even though the gate was staying closed. It's important to have the valves for a couple of "foreseeable" issues- a tire blowout that damages the heater lines, which run pretty close to the tires, a failure in one of the heater cores and lastly, so that you can drain the engine without draining the heating system in the event of working on thermostats, water pump, etc... I put a couple of large aluminum pans under the coach and just removed the hoses on the valves. This allowed me to catch almost all of the coolant (which amounts to around 10 gallons for this job). I then re-filtered and re-used it. Most of the air will work its way out of the system over the course of a few weeks. I was able to re-fill the system with all but a few gallons initially and kept topping it off until everything that I had captured was gone. Shane Fedeli 85PT40 Hershey, PA --- In WanderlodgeForum@yahoogroups.com, "Don Bradner" > > Three questions: > > Why replace the valve at all, rather than a straight-through? > > Did the handle still come to a stop at each end of travel (mine do)? > > Where do you drain the coolant in order to get it low enough to remove the valves? > > On 3/16/2008 at 4:41 PM sfedeli3 wrote: > > >Good luck! I sure hope it fixes your problem. I was so darn confounded > >with mine that I eventually gave up and just listened to Kelly > >complain about cold feet. Finding the dropped gate was purely > >accidental. The R&R on the water pump was just some "preventative" > >maintenance that I had elected to do. > > > >-- In WanderlodgeForum@yahoogroups.com, "Don Bradner" > > > >> > >> Shane, that's a new one, thanks! > >> > >> Don Bradner > >> 90 PT40 "Blue Thunder" > >> Eureka, CA > >> > >> On 3/16/2008 at 11:13 AM sfedeli3 wrote: > >> > >> >Hi Don, > >> > > >> > My guess is that one of your gate valves "dropped". Even though the > >> > valve handle is turning, the inner gate is not lifting. My front heat > >> >circuit did not work for 3 years. Tried flushing the entire loop, > >> >replacing sporlans, relays, dash switches, circulating pump and still > >> >no heat. Finally, removed the gate valve when I pulled the water pump > >> >to replace it and saw that the gate was in the down position. The > >> >inner threads had eroded and when you rotated the handle, nothing > >> >would happen to the gate. I've replaced 2 of the 4 valves with ball > >> >valves. > >> > > >> >Shane Fedeli > >> >85PT40 > >> >Hershey, PA > >> > > > > > > > > >------------------------------------ > > > >Yahoo! Groups Links > > > > > > > |
|||