Xantrex and cable sizes
|
06-10-2008, 00:00
Post: #1
|
|||
|
|||
Xantrex and cable sizes
115ft to the Xantrex from the batteries sounds like a crazy installation to
me. I spent my life in the welding supply business and worked on big welders (low voltage, high amp, DC) and I think you will find MCM cable hard to find but 4/0 welding cable should be readily available and off the shelf connectors to attach two cables to one lug are available if wanted. You can "stack" them to get the capacity you need. If available always pay more for 34awg stranded cable (instead of standard 30awg), the extra flexibility can really help. Steve Wannabee |
|||
06-10-2008, 02:03
Post: #2
|
|||
|
|||
Xantrex and cable sizes
Steve,
That was 115' total wire. It's only 22' feet from inverters to the Batts. Via inside of rail mounting. It's really a Guestimation, could be a little more or less. Or four wires of 22' each. 2 Pos. 2Neg. 2 wires per inverter/charger Not really so far fetched. with the exception that it will not work:{ Like so many things Looked good on paper. At this point in the installation I've decided to put the new units in the origonal inverter box inside the engine compartment. Kurt Horvath 95 Pt-42 10AC --- In WanderlodgeForum@yahoogroups.com, "Steve Pfiffner" > > 115ft to the Xantrex from the batteries sounds like a crazy installation to > me. I spent my life in the > welding supply business and worked on big welders (low voltage, high amp, > DC) and I think you will find > MCM cable hard to find but 4/0 welding cable should be readily available and > off the shelf connectors to attach two cables to one lug are available if > wanted. You can "stack" them to get the capacity you need. > If available always pay more for 34awg stranded cable (instead of standard > 30awg), the extra flexibility > can really help. > > Steve > Wannabee > |
|||
06-10-2008, 02:40
Post: #3
|
|||
|
|||
Xantrex and cable sizes
It's not true that you can't make the wires thick enough or parallel enough of them to work. I don't know how many it would take, but you can find various tools for computing voltage drop in a given wire at a given current in amps. Ask Xantrex how much voltage drop is acceptable and parallel wires until each carries an amount of current that doesn't result in too much voltage drop. Then decide if the bundle of wire is too thick too deal with
On Tue, Jun 10, 2008 at 10:03 AM, bumpersbird <"bumpersbird@yahoo.com"> wrote:
|
|||