Kohler generator overheating
|
08-14-2008, 15:05
Post: #21
|
|||
|
|||
Kohler generator overheating
|
|||
08-14-2008, 16:16
Post: #22
|
|||
|
|||
Kohler generator overheating
Yep, mine is definitely the traditional blade fan, back of a square radiator. It's pretty hard to get to the motor though, and having been through the process of taking out the radiator and putting it back in, I'm not anxious to try. Some of the hex bolts securing the fan shroud to the radiator were exceedingly difficult to put back in. But I will attempt to get to the fan motor tomorrow - if I can do so without jacking the bus up. After hearing all the recent tales, that's also something I'm loathe to do. Greg 86 PT40 Escondido, CA ----- Original Message ---- From: Leroy Eckert To: WanderlodgeForum@yahoogroups.com Sent: Thursday, August 14, 2008 8:05:35 PM Subject: Re: [WanderlodgeForum] Re: Kohler generator overheating
|
|||
08-15-2008, 07:53
Post: #23
|
|||
|
|||
Kohler generator overheating
-Greg,
I'd be looking real hard for that excess oil. That may be what's causing the overheating. It could damage the engine. I'd take a small piece of stiff wire and poke it into the drain plug hole in the oil pan. There must be something blocking the oil from coming out. You don't need to have the filter off, nor the filler cap off to have oil running out of the plug when it's out. If there is something blocking the drain hole, than you can assume that the entire motor is coated with whatever you find. It's possible that a "onetime" something is plugging the drain, but that's pretty rare. If it's sludge, or something similar; you probably need to clean the motor our some. The easiest way to do this will be in several steps. First, get the old oil out. Second, remove the cable to the starter or wire the fuel solenoid in the off position- you must ensure the engine won't start for the next little bit. Then fill the engine with diesel, kerosene or some other oil based solvent. You want to try and break up the sludge that's accumulated. You can take the coach for a drive with the solvent in the generator engine. This will slosh it around and help to clean it. 15 miles or so should be good. If the engine is already hot prior to doing this, that helps soften the sludge as well, making it easier for the solvent to break it up. Back to the shop and drain out the solvent. Depending on how bad it looks, I might consider repeating this process again. Then refill the engine with clean oil, ensuring it's not overfull. Run it for about a half hour or so. Shut it down and drain it. Refill it with clean oil again (replace the filter both times). Then use as usual, but figure on changing it early, at maybe 50 hours or so. Then you should have a failry clean system and be able to go back to normal service intervals. This would be a good time to replace the drain plug with a quarter turn valve and enough piping to get the oil to drain to an easy spot to catch it. Often it's draining onto an pan which then drains out a hole in the pan. With a little "engineering" you can get the oil drain to line up over the pan drain hole, eliminating most of the mess that goes with servicing the generator. You should be able to take you drain plug with you to Home Depot or Lowe's and get everything you need to do this. I hope this is clear enough to understand. If not, let me know and we'll get in touch to square it away. John -- In WanderlodgeForum@yahoogroups.com, Leroy Eckert wrote: > > Ok. Disregard. > Leroy Eckert > 1990 WB-40 Smoke N Mirrors > Dahlonega, GA > Royale Conversion > > --- On Thu, 8/14/08, Scott Forman <scottforman75@...> wrote: > From: Scott Forman <scottforman75@...> > Subject: [WanderlodgeForum] Re: Kohler generator overheating > To: WanderlodgeForum@yahoogroups.com > Date: Thursday, August 14, 2008, 10:39 PM > > > > > > > > > > > > This is not a squirrel cage. The pre-87 units are old- fashioned fan > > units. > > > > Scott > > > > --- In WanderlodgeForum@ yahoogroups. com, Leroy Eckert > > > > > > > > If you look closely, there is an arrow on the squirrel cage housing > > showing direction. At least there is on mine. The motor on mine is > > 208v. I have a typical wiring diagram from the box to the fan motor > > if anyone needs it. > > > Leroy Eckert > > > 1990 WB-40 Smoke N Mirrors > > > Dahlonega, GA > > > Royale Conversion > > > > > > --- On Thu, 8/14/08, Bryan Altier > > > From: Bryan Altier > > > Subject: Re: [WanderlodgeForum] Re: Kohler generator overheating > > > To: WanderlodgeForum@ yahoogroups. com > > > Date: Thursday, August 14, 2008, 9:05 PM > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Greg, > > > Looking at the motor at the end of the fan, mine > > > had two wires coming out of the winding and wrapped up before going > > back into > > > the winding. I removed the wrapping and found that there were two > > > connectors that I swapped causing the motor to run in the proper > > > direction. Look and see if there is a sticker on the end of the > > fan > > > housing with an arrow "direction". Since I got mine blowing out > > the bottom > > > of the fan my overheating problems are apparently gone. > > > > > > Bryan Altier > > > 88 WLWB 40 > > > Greenville, SC > > > > > > ----- Original Message ----- > > > From: > > > Greg Young > > > To: WanderlodgeForum@ yahoogroups. com > > > > > > Sent: Thursday, August 14, 2008 7:36 > > > PM > > > Subject: Re: [WanderlodgeForum] Re: > > > Kohler generator overheating > > > > > > > > > > > > > > > > > > Hi Bryan & Scott and everybody > > > > > > Follow up to our generator > > > issues. I had the radiator serviced and it was only 20% blocked, > > so the > > > guess is that was not the problem. However, I was wrong about > > the > > > fan. Ours appeared to be sucking air in rather than blowing > > out. > > > There is a junction box leading to the fan motor, which was wired > > normally - > > > Hot (black) to black, neutral (white) to white. I reversed these > > and the > > > motor continues to suck in. So how does one reverse the wiring > > and > > > actually make it change direction? > > > > > > I'm also a little baffled about oil > > > levels and think we may have a plug somewhere - the dipstick > > showed oil level > > > above max, yet when I opened the plug, with the filter off and > > the oil filler > > > cap off, no oil came out. Putting in more resulted in oil > > spilling out > > > the breather hose. > > > > > > Sorry, I'm not a gearhead like so many of you, but I > > > can follow instructions if they're detailed enough... > > > > > > Thanks! > > > Greg > > > Young > > > 1986 PT40 > > > Escondido, CA > > > (760) 807-1727 > > > > > > > > > > > > ----- > > > Original Message ---- > > > From: Greg Young > > > To: > > > WanderlodgeForum@ yahoogroups. com > > > Sent: Thursday, August 7, 2008 > > > 7:17:51 PM > > > Subject: Re: [WanderlodgeForum] Re: Kohler generator > > > overheating > > > > > > > > > > > > Hi Scott - Thanks for the info. We have the standard vertical, > > so I > > > think the fan's OK. Time to flush, and if that doesn't improve > > it, I'll > > > probably take it in for "professional" (i.e. expensive) > > > assessment. > > > > > > Greg Young > > > 1986 PT40 > > > Escondido CA > > > > > > > > > > > > ----- > > > Original Message ---- > > > From: Scott Forman > > > <scottforman75@ gmail.com> > > > To: > > > WanderlodgeForum@ yahoogroups. com > > > Sent: Thursday, August 7, 2008 > > > 5:54:06 PM > > > Subject: [WanderlodgeForum] Re: Kohler generator > > > overheating > > > > > > > > > > > > Greg, > > > > > > If you bus has the stock vertical radiator with traditional > > > fan, it > > > should blow out...or at least that is what mine does. > > > > > > > > > Later models...and some retro-fitted earlier ones...have a > > horizontal > > > > > > radiator with squirrel's cage fan blowing down and out. > > > > > > I ran my > > > Yanmar this past weekend at heavy load in 104 degree heat > > > and it never > > > went above 180. > > > > > > Scott Forman > > > 86 PT38 > > > Memphis > > > > > > --- In WanderlodgeForum@ > > > yahoogroups. com, Greg Young > > > wrote: > > > > > > > > > > > Hi Bryan - Thanks for the idea. Which way is it supposed to turn - > > > > > > > > exhausting air through the radiator, or pulling it in? I would > > think > > > > > > out, which is what ours is doing. > > > > -Greg > > > > 86 PT40 > > > > > > > > > > > > > > > > > > > ----- Original Message ---- > > > > From: Bryan > > > Altier > > > > To: WanderlodgeForum@ > > > yahoogroups. com > > > > Sent: Thursday, August 7, 2008 3:45:08 PM > > > > > > > Subject: Re: [WanderlodgeForum] Kohler generator overheating > > > > > > > > > > > > > > > Greg, We had some problems with ours overheating > > > > just at > > > times, (hot weather) and I discovered that the cooling fan > > > on the > > > > > > > radiator was turning backwards. Reversed two wires and problem > > > > > > > solved. > > > > > > > > Bryan Altier > > > > 88WLWB 40 > > > > Greenville, > > > SC > > > > ----- Original Message ----- > > > > From: Greg Young > > > > To: > > > Wanderlodge Forum > > > > Sent: Thursday, August 07, 2008 4:09 PM > > > > > > > Subject: [WanderlodgeForum] Kohler generator overheating > > > > > > > > Hi > > > - > > > > > > > > Our Kohler generator is overheating under load. So far I've > > > > > > replaced the thermostat, and so I guess that flushing the system is > > > > > > the next step. > > > > > > > > Details: > > > > 86 PT-40 > > > > Kohler > > > 12.5CCO67-RV > > > > Yanmar 4-cyl engine > > > > with no load ran cool. > > > Started adding load at around 180 degrees > > > > Added load up to 20A leg > > > one, 30A leg two - all three cruise-air > > > AC's running plus some other > > > appliances. Maintained about 115V all > > > the time. > > > > Temp slowly > > > climbed up to about 215 before I took the load off. In > > > the past it > > > actually tripped the high temp switch, but I didn't see > > > any point in doing > > > that again. > > > > After I took the load off it slowly dropped to around 200. > > > Stopped > > > it then. > > > > > > > > We've got two weeks before we head to > > > the desert and 100+ heat. > > > Any thoughts would be appreciated. > > > > > > > > > > > Thanks! > > > > Greg Young > > > > 1986 PT40 > > > > Escondido, > > > CA > > > > (760) > > > 807-1727 > > > > > > > > |
|||
08-15-2008, 09:44
Post: #24
|
|||
|
|||
Kohler generator overheating
Hey John - Thanks for the advice on this. I believe the oil stoppage is the core of our problem, so I'll do the best I can to follow all this... Our oil drain empties through a hole in the tray so no problem collecting whatever comes out. However taking the coach out for a spin is a very big project for us given where it's parked and the state of disarray it's in. Anyway, I'll see what falls out - if anything at all! Greg ----- Original Message ---- From: jcmace59 To: WanderlodgeForum@yahoogroups.com Sent: Friday, August 15, 2008 12:53:23 PM Subject: [WanderlodgeForum] Re: Kohler generator overheating -Greg, I'd be looking real hard for that excess oil. That may be what's causing the overheating. It could damage the engine. I'd take a small piece of stiff wire and poke it into the drain plug hole in the oil pan. There must be something blocking the oil from coming out. You don't need to have the filter off, nor the filler cap off to have oil running out of the plug when it's out. If there is something blocking the drain hole, than you can assume that the entire motor is coated with whatever you find. It's possible that a "onetime" something is plugging the drain, but that's pretty rare. If it's sludge, or something similar; you probably need to clean the motor our some. The easiest way to do this will be in several steps. First, get the old oil out. Second, remove the cable to the starter or wire the fuel solenoid in the off position- you must ensure the engine won't start for the next little bit. Then fill the engine with diesel, kerosene or some other oil based solvent. You want to try and break up the sludge that's accumulated. You can take the coach for a drive with the solvent in the generator engine. This will slosh it around and help to clean it. 15 miles or so should be good. If the engine is already hot prior to doing this, that helps soften the sludge as well, making it easier for the solvent to break it up. Back to the shop and drain out the solvent. Depending on how bad it looks, I might consider repeating this process again. Then refill the engine with clean oil, ensuring it's not overfull. Run it for about a half hour or so. Shut it down and drain it. Refill it with clean oil again (replace the filter both times). Then use as usual, but figure on changing it early, at maybe 50 hours or so. Then you should have a failry clean system and be able to go back to normal service intervals. This would be a good time to replace the drain plug with a quarter turn valve and enough piping to get the oil to drain to an easy spot to catch it. Often it's draining onto an pan which then drains out a hole in the pan. With a little "engineering" you can get the oil drain to line up over the pan drain hole, eliminating most of the mess that goes with servicing the generator. You should be able to take you drain plug with you to Home Depot or Lowe's and get everything you need to do this. I hope this is clear enough to understand. If not, let me know and we'll get in touch to square it away. John -- In "WanderlodgeForum%40yahoogroups.com", Leroy Eckert wrote: > > Ok. Disregard. > Leroy Eckert > 1990 WB-40 Smoke N Mirrors > Dahlonega, GA > Royale Conversion > > --- On Thu, 8/14/08, Scott Forman <scottforman75@ ...> wrote: > From: Scott Forman <scottforman75@ ...> > Subject: [WanderlodgeForum] Re: Kohler generator overheating > To: "WanderlodgeForum%40yahoogroups.com" > Date: Thursday, August 14, 2008, 10:39 PM > > > > > > > > > > > > This is not a squirrel cage. The pre-87 units are old- fashioned fan > > units. > > > > Scott > > > > --- In WanderlodgeForum@ yahoogroups. com, Leroy Eckert > > > > > > > > If you look closely, there is an arrow on the squirrel cage housing > > showing direction. At least there is on mine. The motor on mine is > > 208v. I have a typical wiring diagram from the box to the fan motor > > if anyone needs it. > > > Leroy Eckert > > > 1990 WB-40 Smoke N Mirrors > > > Dahlonega, GA > > > Royale Conversion > > > > > > --- On Thu, 8/14/08, Bryan Altier > > > From: Bryan Altier > > > Subject: Re: [WanderlodgeForum] Re: Kohler generator overheating > > > To: WanderlodgeForum@ yahoogroups. com > > > Date: Thursday, August 14, 2008, 9:05 PM > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Greg, > > > Looking at the motor at the end of the fan, mine > > > had two wires coming out of the winding and wrapped up before going > > back into > > > the winding. I removed the wrapping and found that there were two > > > connectors that I swapped causing the motor to run in the proper > > > direction. Look and see if there is a sticker on the end of the > > fan > > > housing with an arrow "direction". Since I got mine blowing out > > the bottom > > > of the fan my overheating problems are apparently gone. > > > > > > Bryan Altier > > > 88 WLWB 40 > > > Greenville, SC > > > > > > ----- Original Message ----- > > > From: > > > Greg Young > > > To: WanderlodgeForum@ yahoogroups. com > > > > > > Sent: Thursday, August 14, 2008 7:36 > > > PM > > > Subject: Re: [WanderlodgeForum] Re: > > > Kohler generator overheating > > > > > > > > > > > > > > > > > > Hi Bryan & Scott and everybody > > > > > > Follow up to our generator > > > issues. I had the radiator serviced and it was only 20% blocked, > > so the > > > guess is that was not the problem. However, I was wrong about > > the > > > fan. Ours appeared to be sucking air in rather than blowing > > out. > > > There is a junction box leading to the fan motor, which was wired > > normally - > > > Hot (black) to black, neutral (white) to white. I reversed these > > and the > > > motor continues to suck in. So how does one reverse the wiring > > and > > > actually make it change direction? > > > > > > I'm also a little baffled about oil > > > levels and think we may have a plug somewhere - the dipstick > > showed oil level > > > above max, yet when I opened the plug, with the filter off and > > the oil filler > > > cap off, no oil came out. Putting in more resulted in oil > > spilling out > > > the breather hose. > > > > > > Sorry, I'm not a gearhead like so many of you, but I > > > can follow instructions if they're detailed enough... > > > > > > Thanks! > > > Greg > > > Young > > > 1986 PT40 > > > Escondido, CA > > > (760) 807-1727 > > > > > > > > > > > > ----- > > > Original Message ---- > > > From: Greg Young > > > To: > > > WanderlodgeForum@ yahoogroups. com > > > Sent: Thursday, August 7, 2008 > > > 7:17:51 PM > > > Subject: Re: [WanderlodgeForum] Re: Kohler generator > > > overheating > > > > > > > > > > > > Hi Scott - Thanks for the info. We have the standard vertical, > > so I > > > think the fan's OK. Time to flush, and if that doesn't improve > > it, I'll > > > probably take it in for "professional" (i.e. expensive) > > > assessment. > > > > > > Greg Young > > > 1986 PT40 > > > Escondido CA > > > > > > > > > > > > ----- > > > Original Message ---- > > > From: Scott Forman > > > <scottforman75@ <a href="http://gmail.com" target="_blank">gmail.com> > > > To: > > > WanderlodgeForum@ yahoogroups. com > > > Sent: Thursday, August 7, 2008 > > > 5:54:06 PM > > > Subject: [WanderlodgeForum] Re: Kohler generator > > > overheating > > > > > > > > > > > > Greg, > > > > > > If you bus has the stock vertical radiator with traditional > > > fan, it > > > should blow out...or at least that is what mine does. > > > > > > > > > Later models...and some retro-fitted earlier ones...have a > > horizontal > > > > > > radiator with squirrel's cage fan blowing down and out. > > > > > > I ran my > > > Yanmar this past weekend at heavy load in 104 degree heat > > > and it never > > > went above 180. > > > > > > Scott Forman > > > 86 PT38 > > > Memphis > > > > > > --- In WanderlodgeForum@ > > > yahoogroups. com, Greg Young > > > wrote: > > > > > > > > > > > Hi Bryan - Thanks for the idea. Which way is it supposed to turn - > > > > > > > > exhausting air through the radiator, or pulling it in? I would > > think > > > > > > out, which is what ours is doing. > > > > -Greg > > > > 86 PT40 > > > > > > > > > > > > > > > > > > > ----- Original Message ---- > > > > From: Bryan > > > Altier > > > > To: WanderlodgeForum@ > > > yahoogroups. com > > > > Sent: Thursday, August 7, 2008 3:45:08 PM > > > > > > > Subject: Re: [WanderlodgeForum] Kohler generator overheating > > > > > > > > > > > > > > > Greg, We had some problems with ours overheating > > > > just at > > > times, (hot weather) and I discovered that the cooling fan > > > on the > > > > > > > radiator was turning backwards. Reversed two wires and problem > > > > > > > solved. > > > > > > > > Bryan Altier > > > > 88WLWB 40 > > > > Greenville, > > > SC > > > > ----- Original Message ----- > > > > From: Greg Young > > > > To: > > > Wanderlodge Forum > > > > Sent: Thursday, August 07, 2008 4:09 PM > > > > > > > Subject: [WanderlodgeForum] Kohler generator overheating > > > > > > > > Hi > > > - > > > > > > > > Our Kohler generator is overheating under load. So far I've > > > > > > replaced the thermostat, and so I guess that flushing the system is > > > > > > the next step. > > > > > > > > Details: > > > > 86 PT-40 > > > > Kohler > > > 12.5CCO67-RV > > > > Yanmar 4-cyl engine > > > > with no load ran cool. > > > Started adding load at around 180 degrees > > > > Added load up to 20A leg > > > one, 30A leg two - all three cruise-air > > > AC's running plus some other > > > appliances. Maintained about 115V all > > > the time. > > > > Temp slowly > > > climbed up to about 215 before I took the load off. In > > > the past it > > > actually tripped the high temp switch, but I didn't see > > > any point in doing > > > that again. > > > > After I took the load off it slowly dropped to around 200. > > > Stopped > > > it then. > > > > > > > > We've got two weeks before we head to > > > the desert and 100+ heat. > > > Any thoughts would be appreciated. > > > > > > > > > > > Thanks! > > > > Greg Young > > > > 1986 PT40 > > > > Escondido, > > > CA > > > > (760) > > > 807-1727 > > > > > > > > |
|||
« Next Oldest | Next Newest »
|
User(s) browsing this thread: 3 Guest(s)