Front Air Conditioner Drain problem
|
05-28-2005, 13:18
Post: #1
|
|||
|
|||
Front Air Conditioner Drain problem
Howdy, Y'all.
We live in our 1993 Wanderlodge. The condescent(sp?) from the front air conditioner is not going down the drainage tubes but is running across the roof and draining down the side of the coach. Jack has blown the tubes out with compressed air, he can pour water straight down the tubes and it flows into the bucket I have set on the ground. He has put those small chlorine tables in the drain tray to have a clorine solution going down the tubes to take care of any crud growing in them. Jack is out of solutions. Please help us solve this problem. Thanks, Jack and Liz Regards, Jack and Liz Pearce 1993 Wanderlodge WB40 Homesick Texans in Lantana, FL |
|||
05-29-2005, 04:13
Post: #2
|
|||
|
|||
Front Air Conditioner Drain problem
Jack & Liz:
First: Is the coach level? Have you checked the unit to see if it is level. If the drain is open but the water is not flowing through it, the units pan is not draining towards the tube or there is a leak in the pan causing the water to take the path of least resistance. Take a level up there to see what's happening. R.E. (Ron) Marabito, Dallas, TX 92WB40 Moderator --- In WanderlodgeForum@yahoogroups.com, "Jack and Liz Pearce" > Howdy, Y'all. > > We live in our 1993 Wanderlodge. The condescent(sp?) from the front > air conditioner is not going down the drainage tubes but is running > across the roof and draining down the side of the coach. Jack has > blown the tubes out with compressed air, he can pour water straight > down the tubes and it flows into the bucket I have set on the ground. > He has put those small chlorine tables in the drain tray to have a > clorine solution going down the tubes to take care of any crud > growing in them. Jack is out of solutions. Please help us solve this > problem. > > Thanks, > Jack and Liz > Regards, > Jack and Liz Pearce > 1993 Wanderlodge WB40 > Homesick Texans in Lantana, FL |
|||
05-29-2005, 13:58
Post: #3
|
|||
|
|||
Front Air Conditioner Drain problem
liz,the problem is this. the unit was designed so that the water would drain
onto the roof.but BB put a fitting in the roof just below the drain in the ac unit,there is a 1'' or so gap between the unit and the roof that had a spongie foam donut filling the gap.this foam donut shrinks with age and allows water to leak onto your roof,it will also make the water run onto your floor or bed when you drive it,something about the air blowing into the units drain so that it blows out the unit into your coach..what i did to fix this problem was to cut a piece of 1'' pvc pipe adout an inch long and force it under the unit,between the unit and the bus roof,then i glued it in with some silicone sealer..i got on the roof,measured the gap,had my helper cut the pvc and i put it in.on my coach there are 2 drains per unit,so 6 pieces of pipe was required..randydupree93wb ----- Original Message ----- From: Jack and Liz Pearce To: WanderlodgeForum@yahoogroups.com Sent: Saturday, May 28, 2005 9:18 PM Subject: [WanderlodgeForum] Front Air Conditioner Drain problem Howdy, Y'all. We live in our 1993 Wanderlodge. The condescent(sp?) from the front air conditioner is not going down the drainage tubes but is running across the roof and draining down the side of the coach. Jack has blown the tubes out with compressed air, he can pour water straight down the tubes and it flows into the bucket I have set on the ground. He has put those small chlorine tables in the drain tray to have a clorine solution going down the tubes to take care of any crud growing in them. Jack is out of solutions. Please help us solve this problem. Thanks, Jack and Liz Regards, Jack and Liz Pearce 1993 Wanderlodge WB40 Homesick Texans in Lantana, FL ------------------------------------------------------------------------------ Yahoo! Groups Links a.. To visit your group on the web, go to: http://groups.yahoo.com/group/WanderlodgeForum/ b.. To unsubscribe from this group, send an email to: WanderlodgeForum-unsubscribe@yahoogroups.com c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. [Non-text portions of this message have been removed] |
|||
05-29-2005, 15:28
Post: #4
|
|||
|
|||
Front Air Conditioner Drain problem
Randy,
Does the 1987 PT38 have the drains you describe? Curt Sprenger â87PT38, Anaheim, Calif. randydupree wrote: > liz,the problem is this. the unit was designed so that the water would > drain onto the roof.but BB put a fitting in the roof just below the > drain in the ac unit,there is a 1'' or so gap between the unit and the > roof that had a spongie foam donut filling the gap.this foam donut > shrinks with age and allows water to leak onto your roof,it will also > make the water run onto your floor or bed when you drive it,something > about the air blowing into the units drain so that it blows out the > unit into your coach..what i did to fix this problem was to cut a > piece of 1'' pvc pipe adout an inch long and force it under the > unit,between the unit and the bus roof,then i glued it in with some > silicone sealer..i got on the roof,measured the gap,had my helper cut > the pvc and i put it in.on my coach there are 2 drains per unit,so 6 > pieces of pipe was required..randydupree93wb |
|||
05-29-2005, 23:39
Post: #5
|
|||
|
|||
Front Air Conditioner Drain problem
these drains are on the roof airs,i'm not sure on the early pts.the ones
i've worked on had crusieairs. randy ----- Original Message ----- From: "Curt Sprenger" To: Sent: Sunday, May 29, 2005 11:28 PM Subject: Re: [WanderlodgeForum] Front Air Conditioner Drain problem > Randy, > Does the 1987 PT38 have the drains you describe? > > Curt Sprenger â87PT38, Anaheim, Calif. > > randydupree wrote: > >> liz,the problem is this. the unit was designed so that the water would >> drain onto the roof.but BB put a fitting in the roof just below the >> drain in the ac unit,there is a 1'' or so gap between the unit and the >> roof that had a spongie foam donut filling the gap.this foam donut >> shrinks with age and allows water to leak onto your roof,it will also >> make the water run onto your floor or bed when you drive it,something >> about the air blowing into the units drain so that it blows out the >> unit into your coach..what i did to fix this problem was to cut a >> piece of 1'' pvc pipe adout an inch long and force it under the >> unit,between the unit and the bus roof,then i glued it in with some >> silicone sealer..i got on the roof,measured the gap,had my helper cut >> the pvc and i put it in.on my coach there are 2 drains per unit,so 6 >> pieces of pipe was required..randydupree93wb > > > > > > > Yahoo! Groups Links > > > > > > > |
|||
05-30-2005, 02:16
Post: #6
|
|||
|
|||
Front Air Conditioner Drain problem
I don't believe that the '87 had drain tubes, not sure though.
The A/C units on the '87 have a foam drain tray, not easily replacable, but from my attempts no longer available. I have used Silicone sealer to re-build damaged walls on this foam tray so that the condensation is routed correctly with good success. - Jeff Miller --- In WanderlodgeForum@yahoogroups.com, Curt Sprenger > Randy, > Does the 1987 PT38 have the drains you describe? > > Curt Sprenger `87PT38, Anaheim, Calif. > > randydupree wrote: > > > liz,the problem is this. the unit was designed so that the water would > > drain onto the roof.but BB put a fitting in the roof just below the > > drain in the ac unit,there is a 1'' or so gap between the unit and the > > roof that had a spongie foam donut filling the gap.this foam donut > > shrinks with age and allows water to leak onto your roof,it will also > > make the water run onto your floor or bed when you drive it,something > > about the air blowing into the units drain so that it blows out the > > unit into your coach..what i did to fix this problem was to cut a > > piece of 1'' pvc pipe adout an inch long and force it under the > > unit,between the unit and the bus roof,then i glued it in with some > > silicone sealer..i got on the roof,measured the gap,had my helper cut > > the pvc and i put it in.on my coach there are 2 drains per unit,so 6 > > pieces of pipe was required..randydupree93wb |
|||
05-30-2005, 03:09
Post: #7
|
|||
|
|||
Front Air Conditioner Drain problem
Hi Jeff,
The two Intertherm Polaris A/C's on our 88FC, do not have roof drain tubes. The condensation just runs off of the roof, sometimes onto the awnings. What is the correct way of routing the water?? Bill 88 FC --- In WanderlodgeForum@yahoogroups.com, "Jeff Miller" > I don't believe that the '87 had drain tubes, not sure though. > > The A/C units on the '87 have a foam drain tray, not easily > replacable, but from my attempts no longer available. > > I have used Silicone sealer to re-build damaged walls on this foam > tray so that the condensation is routed correctly with good success. > > - Jeff Miller > > > --- In WanderlodgeForum@yahoogroups.com, Curt Sprenger > > > Randy, > > Does the 1987 PT38 have the drains you describe? > > > > Curt Sprenger `87PT38, Anaheim, Calif. > > > > randydupree wrote: > > > > > liz,the problem is this. the unit was designed so that the water > would > > > drain onto the roof.but BB put a fitting in the roof just below > the > > > drain in the ac unit,there is a 1'' or so gap between the unit > and the > > > roof that had a spongie foam donut filling the gap.this foam > donut > > > shrinks with age and allows water to leak onto your roof,it will > also > > > make the water run onto your floor or bed when you drive > it,something > > > about the air blowing into the units drain so that it blows out > the > > > unit into your coach..what i did to fix this problem was to cut a > > > piece of 1'' pvc pipe adout an inch long and force it under the > > > unit,between the unit and the bus roof,then i glued it in with > some > > > silicone sealer..i got on the roof,measured the gap,had my helper > cut > > > the pvc and i put it in.on my coach there are 2 drains per > unit,so 6 > > > pieces of pipe was required..randydupree93wb |
|||
05-30-2005, 03:48
Post: #8
|
|||
|
|||
Front Air Conditioner Drain problem
BB routed the condensation water from roof A/Cs on PT coaches
through tubes leading down from the roof, I believe starting with the WLWB. The Intertherm is a unique piece, really nice units except for the drop-open door over the controls ;~) Intertherm parts are no longer available, take good care of your unit and shrouds. If one of yours dies, and has a good shroud, save the shroud for your other unit or another BB owner. - Jeff Miller --- In WanderlodgeForum@yahoogroups.com, "pattypape" wrote: > > > Hi Jeff, > > The two Intertherm Polaris A/C's on our 88FC, do not have > roof drain tubes. The condensation just runs off of the roof, > sometimes onto the awnings. > What is the correct way of routing the water?? > > Bill 88 FC > > --- In WanderlodgeForum@yahoogroups.com, "Jeff Miller" > > > I don't believe that the '87 had drain tubes, not sure though. > > > > The A/C units on the '87 have a foam drain tray, not easily > > replacable, but from my attempts no longer available. > > > > I have used Silicone sealer to re-build damaged walls on this foam > > tray so that the condensation is routed correctly with good > success. > > > > - Jeff Miller > > > > > > --- In WanderlodgeForum@yahoogroups.com, Curt Sprenger > > > > > Randy, > > > Does the 1987 PT38 have the drains you describe? > > > > > > Curt Sprenger `87PT38, Anaheim, Calif. > > > > > > randydupree wrote: > > > > > > > liz,the problem is this. the unit was designed so that the > water > > would > > > > drain onto the roof.but BB put a fitting in the roof just > below > > the > > > > drain in the ac unit,there is a 1'' or so gap between the unit > > and the > > > > roof that had a spongie foam donut filling the gap.this foam > > donut > > > > shrinks with age and allows water to leak onto your roof,it > will > > also > > > > make the water run onto your floor or bed when you drive > > it,something > > > > about the air blowing into the units drain so that it blows > out > > the > > > > unit into your coach..what i did to fix this problem was to > cut a > > > > piece of 1'' pvc pipe adout an inch long and force it under > the > > > > unit,between the unit and the bus roof,then i glued it in with > > some > > > > silicone sealer..i got on the roof,measured the gap,had my > helper > > cut > > > > the pvc and i put it in.on my coach there are 2 drains per > > unit,so 6 > > > > pieces of pipe was required..randydupree93wb |
|||
05-30-2005, 09:02
Post: #9
|
|||
|
|||
Front Air Conditioner Drain problem
Howdy, Randy.
Thanks for writing. +++ In WanderlodgeForum@yahoogroups.com, randydupree > liz,the problem is this. the unit was designed so that the water would drain onto the roof.but BB put a fitting in the roof just below the drain in the ac unit,there is a 1'' or so gap between the unit and the roof that had a spongie foam donut filling the gap.this foam donut shrinks with age and allows water to leak onto your roof++++++ Jack took care of that donut some time ago. We just had a plugged up drain tube. Now the water flows down the drain tube like a cow on a flat rock. Now that I have your attention, will you pretty please post the model of Sharp microwave/convection oven you have in your 1993 coach? Thanks, Liz Regards, Jack and Liz Pearce 1993 Wanderlodge WB40 Homesick Texans in Lantana, FL |
|||
05-30-2005, 12:43
Post: #10
|
|||
|
|||
Front Air Conditioner Drain problem
liz,the microwaves model # is R1850A. randydupree93wb
----- Original Message ----- From: Jack and Liz Pearce To: WanderlodgeForum@yahoogroups.com Sent: Monday, May 30, 2005 5:02 PM Subject: [WanderlodgeForum] Re: Front Air Conditioner Drain problem Howdy, Randy. Thanks for writing. +++ In WanderlodgeForum@yahoogroups.com, randydupree > liz,the problem is this. the unit was designed so that the water would drain onto the roof.but BB put a fitting in the roof just below the drain in the ac unit,there is a 1'' or so gap between the unit and the roof that had a spongie foam donut filling the gap.this foam donut shrinks with age and allows water to leak onto your roof++++++ Jack took care of that donut some time ago. We just had a plugged up drain tube. Now the water flows down the drain tube like a cow on a flat rock. Now that I have your attention, will you pretty please post the model of Sharp microwave/convection oven you have in your 1993 coach? Thanks, Liz Regards, Jack and Liz Pearce 1993 Wanderlodge WB40 Homesick Texans in Lantana, FL ------------------------------------------------------------------------------ Yahoo! Groups Links a.. To visit your group on the web, go to: http://groups.yahoo.com/group/WanderlodgeForum/ b.. To unsubscribe from this group, send an email to: WanderlodgeForum-unsubscribe@yahoogroups.com c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. [Non-text portions of this message have been removed] |
|||