house electrical question
07-18-2006, 09:15
Post: #3
house electrical question
Sounds haunted.

We need to isolate the source of the problem.

First plug in the cord to the supply, without the plug on the coach.
No trip?

Next turn the two 30a breakers (separate box below the main breaker
panel in an '82) off, and turn the transfer switch to OFF, plug the
cord into the lower 30a (yellow) coach connection.
No trip?

Turn the transfer switch to "30A"
No trip?

Turn off the two main breakers in the main breaker panel (50a
breakers), and turn on the two 30a breakers in the lower panel one
at a time.
No trip?

Turn off all breakers in the main panel, turn on the main breakers
one at a time.
No trip?

Turn on load breakers one at a time, preferrably with AC and other
loads off until you find the one that trips.
No trip?

Turn loads on individually until the offending load is found.

Once you find the part of this sequence that trips the breaker it
will become apparent where the short is. Most likely it is in the
cordset, or between the 30a connection and the main breaker panel
(which includes the transfer switch). BTW, and I apologize if you
already know this, but the 30a position on the transfer switch is
for the two (yellow) separate 30a cords. When using the single (red-
tape) 30a cord you use the 50a setting on the transfer switch.

- Jeff Miller
in Holland, MI


--- In WanderlodgeForum@yahoogroups.com, "davidkerryedwards"
wrote:
>
> 82 FC. When I hook up the 50amp cable to the 50 amp connector,
> everything is fine. When I hook the top 30amp cable front ac and
half
> coach work fine (as it should). When I hook up the bottom 30 amp
> connector it immediately trips breaker on the supply. Same thing
> happens when I use the 30 amp cable designed for the 50 amp hook
up.
> Why would it work ok with 50 amp cable but trip breaker with 30
amp on
> either the 50amp supply side or the bottom 30 amp supply? It's
done
> this as long as I've had it. The frustration associated with it
is
> that I can only run the front AC when hooked up to 30amps and it
> doesn't cool the bedroom.
>
>
> Kerry
> 82 FC 3
> Denver
> currently on the road in Upstate NY. Saw Tom Warner a couple of
days
> ago by happenstance.
>
Quote this message in a reply
Post Reply 


Messages In This Thread
house electrical question - davidkerryedwards - 07-18-2006, 08:31
house electrical question - Rob Robinson - 07-18-2006, 08:59
house electrical question - Jeff Miller - 07-18-2006 09:15
house electrical question - davidkerryedwards - 07-18-2006, 12:46
house electrical question - davidkerryedwards - 07-18-2006, 12:48
house electrical question - davidkerryedwards - 07-19-2006, 10:38
house electrical question - Jeff Miller - 07-20-2006, 05:43



User(s) browsing this thread: 1 Guest(s)