Generator Output Voltage
|
06-21-2007, 10:13
Post: #2
|
|||
|
|||
Generator Output Voltage
--- In WanderlodgeForum@yahoogroups.com, "crissrace"
wrote: > > We were dry camping at the Formula I race at Indianopolis Speedway last > weekend when both the air conditioners quit. Quick investigation > revealed that the generator was running but no output. I checked the > breakers and the voltage to them was 84 volts on each leg. 120 would > have been better. There are 1400 hours on the unit. Does anyone have > an idea where to start to repair this fault? > Any and all help appreciated. > Bob Criss > 1990 SP36 > 143000 miles > Bob, I had a similar thing happen to my SP generator several years ago. It turned out to be a bad rectifier diode. One phase was bad which gave the low voltage. It was relatively inexpensive (less than $50) and not hard to replace (once you get the generator out of the bird). The info on how to troubleshoot is listed in the Onan manual and I was able to find them on the internet. Good luck. Jim Brookshire 1989 SP-36 |
|||
« Next Oldest | Next Newest »
|
Messages In This Thread |
Generator Output Voltage - crissrace - 06-21-2007, 09:50
Generator Output Voltage - agitator19 - 06-21-2007 10:13
Generator Output Voltage - agitator19 - 06-21-2007, 10:13
Generator Output Voltage - Alan - 06-21-2007, 10:48
|