Installing new Xantrex RS3000
Well here goes nothing. Ripped out the old Heart 2000 and twin Iota
45's today. Pulled the charger electrical box and the jbox for the
inverted circuit off the firewall. The conduit is too small (1/2")
for the new 50AMP circuits that need to be run to and from the new
Xantrex RS3000. So will have to cut a larger hole in the floor
behind the curb side draw in the bed room below the circuit breaker
panel into the engine comparment next to the old circuits. Will
then run teo new 3/4" liquid tight conduits from there to the
inverter box above the batteries.

Will need to pull the original 50 AMP circuit at the coach breaker
panel and run it to a new 50 AMP breaker panel. Will mount the new
breaker panel behind the current breaker panel but facing the other
direction into the shirt closet, will cut an access panel in the
shirt closet upper left storage area so the breaker cab be reset if
it trips. Will then need to run out of this breaker panel to the
inverter input. Then return from the inverter to the original 50
AMP breaker in the coach. The down side is that everything in the
coach will be able to be on the inverter when shore power is lost.
But I plan to add the Auto-generator start to the RS3000 so if I
lose shore power it will start the generator when the batteries get
down to a set voltage.

Anyone else been down this road? If so would be interested in
hearing what you did.

I know some have replaced the original Heart with a Xantrex RS2000,
the issue they may or may not know is that the RS2000/3000 doesn't
have a built in circuit breaker. The old Heart inverters in our
coaches have a 15 amp breaker on the inverted circuit. The way the
older WB's are designed requires a circuit breaker in the inverter
as there is no breaker on the inverted side of the coach AC circuits
due to the way the WB engineers designed using relays vs a 2nd
breaker panel. So if you have swapped your inverter out, please
make sure that either your inverter is a built-in circuit breaker,
or that you have added an external breaker to the inverted circuit.

Michael Brundridge
92 WB40
Georgetown, TX
Quote this message in a reply
Post Reply 


Messages In This Thread
Installing new Xantrex RS3000 - mbrund - 11-26-2007 13:34
Installing new Xantrex RS3000 - Gregory OConnor - 11-26-2007, 16:57
Installing new Xantrex RS3000 - sfedeli3 - 11-27-2007, 02:06
Installing new Xantrex RS3000 - mbrund - 11-27-2007, 03:06
Installing new Xantrex RS3000 - mbrund - 11-27-2007, 03:12
Installing new Xantrex RS3000 - Pete Masterson - 11-27-2007, 03:14
Installing new Xantrex RS3000 - Pete Masterson - 11-27-2007, 03:22



User(s) browsing this thread: 1 Guest(s)