Kohler 12.5 Yanmar Engine Generator Not Running ?
|
10-08-2008, 08:39
Post: #3
|
|||
|
|||
Kohler 12.5 Yanmar Engine Generator Not Running ?
I agree with Scott. I've had that happen three times (no AC to run
the blower). Once was the voltage regulator and twice it was a broken brush wire. (Until I realized I needed to replace the commutator slip rings). Tom Sorrentino 1987 PT38 12.5 Yanmar/Kohler --- In WanderlodgeForum@yahoogroups.com, "Scott Forman" <scottforman75@...> wrote: > > It is not making electricity. If AC (current, not air conditioning) > isn't present, the engine will shut down in a few seconds. You have > an internal problem in the generator head unit. > > Scott Forman > 86 PT38 > Memphis > > --- In WanderlodgeForum@yahoogroups.com, "fmc360" > wrote: > > > > Engine will start but will not keep running. start solenoid will > not > > open injection pump. Items not working or not powered: > > l. start solenoid 2. Oil Pressure gauge 3. Water temperature > > gauge 4. Radiator > Blower > > Looks to me like the engine is in auto shutdown mode. I need to > > know where the circuit breakers or fuses are for the Oil Pressure > > gauge, fuel solenoid and > blower. > > The Coach is a 89 PT 40 I have already replaced the > > battery with no > difference. > > C. E. Wooten Madisonville, Texas 936 348 6855 PLEASE > > REPLY TO EMAIL ADDRESS fmc360@ Thanks for any > > help. > > > |
|||
« Next Oldest | Next Newest »
|
Messages In This Thread |
Kohler 12.5 Yanmar Engine Generator Not Running ? - fmc360 - 10-08-2008, 02:48
Kohler 12.5 Yanmar Engine Generator Not Running ? - Scott Forman - 10-08-2008, 05:51
Kohler 12.5 Yanmar Engine Generator Not Running ? - thomas_sorrentino - 10-08-2008 08:39
|
User(s) browsing this thread: 1 Guest(s)