Generator Switch Box
|
03-02-2013, 09:52
Post: #4
|
|||
|
|||
RE: Generator Switch Box
(02-28-2013 17:20)pgchin Wrote: Darrell, More info on generator transfer switch. Thanks to you both for the insight and direction. Once again I ran all 3 AC's under load (had to set the thermostats at 40F) and observed the amp gages. During normal cycling of the AC's no current spiking was observed. The replacement 10 ga wire didn't get warm, no smell or smoke and my clamp-on amp meter agreed with the coaches. About 12amps per unit under load. If I manually start an individual unit while there is a demand in that zone I will see a prolonged spike on the meter of which ever leg that unit is wired to. I haven't had the guts to leave it on for more than 3 to 5 seconds and the 20amp breaker doesn't trip. This happens to all 3 units including the center unit which was replaced last spring. Yes indeed the transfer switch comes from the factory with 10ga wires between both sets of T1 and T3 terminals and one 6ga wire between the T2s (white neutral). The balance of the terminals were wired by BB with 6ga. Should there be some logic in the AC units or the thermostat that delays engaging the compressor until the motor has started? Why don't the breakers trip? I'm pretty sure this condition is what fried the earlier 10 ga wire. Nice to have the Aqua Hot last night, warm floors too! D |
|||