Generator Switch Box
|
03-04-2013, 22:52
Post: #13
|
|||
|
|||
RE: Generator Switch Box
(03-02-2013 11:27)davidmbrady Wrote: Darrell,Dave Had a look at AC voltage today with shore power and genny. SP has 125v no load, and 116~v when 1 compressor kicks in. Genny shows 120v and 119v when 1 compressor kicks in. I have an extension cord 100' long with #8 wire so I think this is part of the problem with voltage drop. It hasn't concerned me since I won't be using this arrangement once my permanent AC connection is in place in a couple of weeks (before air conditioning season). But the problem with high starting current still occurs with genny power. If I turn on the forward AC switch and create a demand at the thermostat all will work well. The fan will come on and a short time later the compressor will pull in with a quick spike. But if I should turn off the forward AC switch while there is a demand and turn it on again there is a prolonged spike of about 10 secs + that is kinda scary. This happens on all units. I plan on contacting Dometic to see what gives with delays as it seems they have one for one condition but not one for an equally important condition. D |
|||