In order to recommend the slab thickness, type concrete and
reinforcing, it is necessary to know the soil characteristics in the area. I definitely would not use 2000 psi concrete. That's just about good enough for a sidewalk, but not for a Bird. There should be detailed soil information available from your county agent. R.E. (Ron) Marabito, Dallas, TX 92WB40 Architect, retired. --- In WanderlodgeForum@yahoogroups.com, "Howard O. Truitt" > > I'm getting ready to build a storage building for my 86 8V92 PT40. The > previous owner had kept it in a barn on his farm. I would appreciate > some advise on the concrete pad. I plan on building a 16'x56' building > with 14'x14' roll up doors on each end. I had one builder say to > compact the dirt well and pour 4" of 2000# concrete with fiber the > other says I need to pour 6" of 3000# concrete with wire. > I also plan on putting in a 42" wide by 42" deep by 12' long service > pit. > I would appreciate your imput. > Howard Truitt > Camilla, Ga. > 86 8V92 PT40 > |
|||
« Next Oldest | Next Newest »
|
Messages In This Thread |
New Building - Howard O. Truitt - 11-18-2005, 11:05
New Building - ronmarabito2002 - 11-18-2005 11:36
New Building - Wallace Craig - 11-18-2005, 11:51
New Building - Blair - 11-18-2005, 12:22
New Building - Robert Johannesen - 11-18-2005, 13:37
New Building - Gregory OConnor - 11-18-2005, 17:08
New Building - dspithaler@... - 11-18-2005, 21:31
New Building - John Suter - 11-18-2005, 23:44
New Building - Blair - 11-19-2005, 02:08
New Building - Richard Hayden - 11-19-2005, 14:43
New Building - Dan Darst - 11-19-2005, 15:52
New Building - Howard O. Truitt - 11-20-2005, 08:06
New Building - Richard Hayden - 11-22-2005, 15:22
|
User(s) browsing this thread: 8 Guest(s)