What's that annoying buzing???
12-02-2006, 02:36
Post: #1
What's that annoying buzing???
Hi Gang, Decided to run the central vac, so I plugged into the lower
30 amp service. Everything works fine, but unless there is a load on
the service, there is a pronounced buzzing coming from behind the
incoming AC supply switch. It does not do this when I am hooked up to
the upper service...but then again, the battery chargers are running,
so there is a load...any thoughts? Thanks from balmy Gunnison, 5
degrees F above here this AM. Doug Engel, Gunnison, CO 1981
FC35SB "Pokey"
Quote this message in a reply
12-02-2006, 03:57
Post: #2
What's that annoying buzing???
Sounds like you are describing the buzzing caused by the coil in a
transfer relay. This usually happens when delamination occurs. Three
fixes: 1. Slap the outter surface of the box containing the relay
(temporary). 2. Disconnect all power and remove the cover, clean any
debris and tighten the mounting screws. 3. Replace rhe relay.

Rich D. '99LXi43' CT


--- In WanderlodgeForum@yahoogroups.com, "doug_ngl"
wrote:
>
> Hi Gang, Decided to run the central vac, so I plugged into the lower
> 30 amp service. Everything works fine, but unless there is a load on
> the service, there is a pronounced buzzing coming from behind the
> incoming AC supply switch. It does not do this when I am hooked up to
> the upper service...but then again, the battery chargers are running,
> so there is a load...any thoughts? Thanks from balmy Gunnison, 5
> degrees F above here this AM. Doug Engel, Gunnison, CO 1981
> FC35SB "Pokey"
>
Quote this message in a reply
12-02-2006, 07:18
Post: #3
What's that annoying buzing???
Thanks, I'll check that out. Doug

g_man1146 wrote: Sounds like you are
describing the buzzing caused by the coil in a
transfer relay. This usually happens when delamination occurs. Three
fixes: 1. Slap the outter surface of the box containing the relay
(temporary). 2. Disconnect all power and remove the cover, clean any
debris and tighten the mounting screws. 3. Replace rhe relay.

Rich D. '99LXi43' CT

--- In WanderlodgeForum@yahoogroups.com, "doug_ngl"
wrote:
>
> Hi Gang, Decided to run the central vac, so I plugged into the lower
> 30 amp service. Everything works fine, but unless there is a load on
> the service, there is a pronounced buzzing coming from behind the
> incoming AC supply switch. It does not do this when I am hooked up to
> the upper service...but then again, the battery chargers are running,
> so there is a load...any thoughts? Thanks from balmy Gunnison, 5
> degrees F above here this AM. Doug Engel, Gunnison, CO 1981
> FC35SB "Pokey"
>






Doug Engel, Gunnison, CO. 1981 FC35SB "Pokey"

---------------------------------
Cheap Talk? Check out Yahoo! Messenger's low PC-to-Phone call rates.

[Non-text portions of this message have been removed]
Quote this message in a reply
Post Reply 




User(s) browsing this thread: 2 Guest(s)