Installing new Xantrex RS3000
|
11-26-2007, 13:34
Post: #1
|
|||
|
|||
Installing new Xantrex RS3000
Well here goes nothing. Ripped out the old Heart 2000 and twin Iota
45's today. Pulled the charger electrical box and the jbox for the inverted circuit off the firewall. The conduit is too small (1/2") for the new 50AMP circuits that need to be run to and from the new Xantrex RS3000. So will have to cut a larger hole in the floor behind the curb side draw in the bed room below the circuit breaker panel into the engine comparment next to the old circuits. Will then run teo new 3/4" liquid tight conduits from there to the inverter box above the batteries. Will need to pull the original 50 AMP circuit at the coach breaker panel and run it to a new 50 AMP breaker panel. Will mount the new breaker panel behind the current breaker panel but facing the other direction into the shirt closet, will cut an access panel in the shirt closet upper left storage area so the breaker cab be reset if it trips. Will then need to run out of this breaker panel to the inverter input. Then return from the inverter to the original 50 AMP breaker in the coach. The down side is that everything in the coach will be able to be on the inverter when shore power is lost. But I plan to add the Auto-generator start to the RS3000 so if I lose shore power it will start the generator when the batteries get down to a set voltage. Anyone else been down this road? If so would be interested in hearing what you did. I know some have replaced the original Heart with a Xantrex RS2000, the issue they may or may not know is that the RS2000/3000 doesn't have a built in circuit breaker. The old Heart inverters in our coaches have a 15 amp breaker on the inverted circuit. The way the older WB's are designed requires a circuit breaker in the inverter as there is no breaker on the inverted side of the coach AC circuits due to the way the WB engineers designed using relays vs a 2nd breaker panel. So if you have swapped your inverter out, please make sure that either your inverter is a built-in circuit breaker, or that you have added an external breaker to the inverted circuit. Michael Brundridge 92 WB40 Georgetown, TX |
|||
11-26-2007, 16:57
Post: #2
|
|||
|
|||
Installing new Xantrex RS3000
Unless The RS3 has a transfer requirement I cant see a need to
supply the RS3 with any more than 20 amps of wire size to run the chargers and 25 amps of wire size from the inverter to the inverter run appliances and recepticals. (300w/120volts=25amps) My 1994 with a Heart 2800 must have some 12v/120v relays that select the inverter power path because it is not like one leg of the panel is hot on inverted power???? I wonder if Xantrex has insight on the retrofit or a tech hotline. If someone here has info the only sure thing would be a horror story or what not to do. All other installs may not be totally necessary or proven. when I pas a hydrolic line through plys of steel, I make the hole round and larger. Round to keep from cracking, large to keep frm slicing the product. GregoryO'Connor 94ptRomolandca --- In WanderlodgeForum@yahoogroups.com, "mbrund" <mbrund@...> wrote: > > Well here goes nothing. Ripped out the old Heart 2000 and twin Iota > 45's today. Pulled the charger electrical box and the jbox for the > inverted circuit off the firewall. The conduit is too small (1/2") > for the new 50AMP circuits that need to be run to and from the new > Xantrex RS3000. So will have to cut a larger hole in the floor > behind the curb side draw in the bed room below the circuit breaker > panel into the engine comparment next to the old circuits. Will > then run teo new 3/4" liquid tight conduits from there to the > inverter box above the batteries. > > Will need to pull the original 50 AMP circuit at the coach breaker > panel and run it to a new 50 AMP breaker panel. Will mount the new > breaker panel behind the current breaker panel but facing the other > direction into the shirt closet, will cut an access panel in the > shirt closet upper left storage area so the breaker cab be reset if > it trips. Will then need to run out of this breaker panel to the > inverter input. Then return from the inverter to the original 50 > AMP breaker in the coach. The down side is that everything in the > coach will be able to be on the inverter when shore power is lost. > But I plan to add the Auto-generator start to the RS3000 so if I > lose shore power it will start the generator when the batteries get > down to a set voltage. > > Anyone else been down this road? If so would be interested in > hearing what you did. > > I know some have replaced the original Heart with a Xantrex RS2000, > the issue they may or may not know is that the RS2000/3000 doesn't > have a built in circuit breaker. The old Heart inverters in our > coaches have a 15 amp breaker on the inverted circuit. The way the > older WB's are designed requires a circuit breaker in the inverter > as there is no breaker on the inverted side of the coach AC circuits > due to the way the WB engineers designed using relays vs a 2nd > breaker panel. So if you have swapped your inverter out, please > make sure that either your inverter is a built-in circuit breaker, > or that you have added an external breaker to the inverted circuit. > > Michael Brundridge > 92 WB40 > Georgetown, TX > |
|||
11-27-2007, 02:06
Post: #3
|
|||
|
|||
Installing new Xantrex RS3000
Hi Michael,
Two years ago, I installed at ProSine 2.0 in the Rediline/charger compartment. There was a 12/3 cable running up through grey plastic conduit to the closet behind the bedroom. It took some silicone grease, but I was able to pull the old rediline wire out and run 10/2 and the phone duplex cord for the ProSine's control panel up through the same conduit and behind the 48" flourescent wall sconce in the bedroom to the closet where the main breaker panel is located. I ended up pulling 4 circuits out of the main panel and relocating them to a smaller 30A sub panel in the closet behind the main breaker panel. The 110V supply for the charger side of the inverter was already routed to a duplex outlet in the charger compartment. I seem to recall that being 12/2 wire, and I've had no problems with the breaker tripping when there is a 100A charge dumping into the batteries. You can program the ProSine to know the size of the breaker. Shane Fedeli 85PT40 Hershey, PA --- In WanderlodgeForum@yahoogroups.com, "mbrund" <mbrund@...> wrote: > > Well here goes nothing. Ripped out the old Heart 2000 and twin Iota > 45's today. Pulled the charger electrical box and the jbox for the > inverted circuit off the firewall. The conduit is too small (1/2") > for the new 50AMP circuits that need to be run to and from the new > Xantrex RS3000. So will have to cut a larger hole in the floor > behind the curb side draw in the bed room below the circuit breaker > panel into the engine comparment next to the old circuits. Will > then run teo new 3/4" liquid tight conduits from there to the > inverter box above the batteries. > > Will need to pull the original 50 AMP circuit at the coach breaker > panel and run it to a new 50 AMP breaker panel. Will mount the new > breaker panel behind the current breaker panel but facing the other > direction into the shirt closet, will cut an access panel in the > shirt closet upper left storage area so the breaker cab be reset if > it trips. Will then need to run out of this breaker panel to the > inverter input. Then return from the inverter to the original 50 > AMP breaker in the coach. The down side is that everything in the > coach will be able to be on the inverter when shore power is lost. > But I plan to add the Auto-generator start to the RS3000 so if I > lose shore power it will start the generator when the batteries get > down to a set voltage. > > Anyone else been down this road? If so would be interested in > hearing what you did. > > I know some have replaced the original Heart with a Xantrex RS2000, > the issue they may or may not know is that the RS2000/3000 doesn't > have a built in circuit breaker. The old Heart inverters in our > coaches have a 15 amp breaker on the inverted circuit. The way the > older WB's are designed requires a circuit breaker in the inverter > as there is no breaker on the inverted side of the coach AC circuits > due to the way the WB engineers designed using relays vs a 2nd > breaker panel. So if you have swapped your inverter out, please > make sure that either your inverter is a built-in circuit breaker, > or that you have added an external breaker to the inverted circuit. > > Michael Brundridge > 92 WB40 > Georgetown, TX > |
|||
11-27-2007, 03:06
Post: #4
|
|||
|
|||
Installing new Xantrex RS3000
The RS series does have a transfer switch built in.
THe charger is a 150 AMP charger and requires 25 AMPS AC I believe to operate at that rate. So wire is going to have to be run no matter what as the current wiring was slightly under-rated for the circuit to being with as it appears to be 14/2 (which is derated to 15 AMPs by code). Yes, the BB engineers used a set of relays that engaged side is coming from the breaker panel and they jumper shore power to the relay coil as well. The other side of the relay is attached to the inverter. When shore power is lost the relays go back to the inverter contacts as the relay coil is not being driven by shore power and now you are on inverter power on those circuits. But like I said in the prior message, that circuit has to be protected by a circuit breaker between the inverter and the coils, just happens that the Heart units in the coaches have one built in the inverter (it is a round push button type on the face of the inverter). But some of the new inverters don't install such an breaker and require that an external breaker be used, which is just the case in the Xantrex RS series. Michael Brundridge 92 WB40 Georgetown, TX --- In WanderlodgeForum@yahoogroups.com, "Gregory OConnor" > > Unless The RS3 has a transfer requirement I cant see a need to > supply the RS3 with any more than 20 amps of wire size to run the > chargers and 25 amps of wire size from the inverter to the inverter > run appliances and recepticals. (300w/120volts=25amps) > > My 1994 with a Heart 2800 must have some 12v/120v relays that select > the inverter power path because it is not like one leg of the panel > is hot on inverted power???? > > I wonder if Xantrex has insight on the retrofit or a tech hotline. > If someone here has info the only sure thing would be a horror story > or what not to do. All other installs may not be totally necessary > or proven. > > when I pas a hydrolic line through plys of steel, I make the hole > round and larger. Round to keep from cracking, large to keep frm > slicing the product. > > GregoryO'Connor > 94ptRomolandca > --- In WanderlodgeForum@yahoogroups.com, "mbrund" <mbrund@> > wrote: > > > > Well here goes nothing. Ripped out the old Heart 2000 and twin > Iota > > 45's today. Pulled the charger electrical box and the jbox for > the > > inverted circuit off the firewall. The conduit is too small > (1/2") > > for the new 50AMP circuits that need to be run to and from the new > > Xantrex RS3000. So will have to cut a larger hole in the floor > > behind the curb side draw in the bed room below the circuit > breaker > > panel into the engine comparment next to the old circuits. Will > > then run teo new 3/4" liquid tight conduits from there to the > > inverter box above the batteries. > > > > Will need to pull the original 50 AMP circuit at the coach breaker > > panel and run it to a new 50 AMP breaker panel. Will mount the > new > > breaker panel behind the current breaker panel but facing the > other > > direction into the shirt closet, will cut an access panel in the > > shirt closet upper left storage area so the breaker cab be reset > if > > it trips. Will then need to run out of this breaker panel to the > > inverter input. Then return from the inverter to the original 50 > > AMP breaker in the coach. The down side is that everything in the > > coach will be able to be on the inverter when shore power is > lost. > > But I plan to add the Auto-generator start to the RS3000 so if I > > lose shore power it will start the generator when the batteries > get > > down to a set voltage. > > > > Anyone else been down this road? If so would be interested in > > hearing what you did. > > > > I know some have replaced the original Heart with a Xantrex > RS2000, > > the issue they may or may not know is that the RS2000/3000 doesn't > > have a built in circuit breaker. The old Heart inverters in our > > coaches have a 15 amp breaker on the inverted circuit. The way the > > older WB's are designed requires a circuit breaker in the inverter > > as there is no breaker on the inverted side of the coach AC > circuits > > due to the way the WB engineers designed using relays vs a 2nd > > breaker panel. So if you have swapped your inverter out, please > > make sure that either your inverter is a built-in circuit breaker, > > or that you have added an external breaker to the inverted circuit. > > > > Michael Brundridge > > 92 WB40 > > Georgetown, TX > > > |
|||
11-27-2007, 03:12
Post: #5
|
|||
|
|||
Installing new Xantrex RS3000
THe RS3000 is the same, you can tell it what the input breaker size
is so that when it is in power share mode (i.e. charger is charging batteries) it will reduce the charger input power to insure the input breaker does not trip. The RS3000 battery charger only pulls power from circuit 1. So I will need to make sure that the circuit with the two AC's on them is on the opposite circuit to insure I get max charge potential. Michael Brundridge 92 WB40 Georgetown, TX --- In WanderlodgeForum@yahoogroups.com, "sfedeli3" <sfedeli3@...> wrote: > > Hi Michael, > > Two years ago, I installed at ProSine 2.0 in the Rediline/charger > compartment. There was a 12/3 cable running up through grey plastic > conduit to the closet behind the bedroom. It took some silicone > grease, but I was able to pull the old rediline wire out and run 10/2 > and the phone duplex cord for the ProSine's control panel up through > the same conduit and behind the 48" flourescent wall sconce in the > bedroom to the closet where the main breaker panel is located. I ended > up pulling 4 circuits out of the main panel and relocating them to a > smaller 30A sub panel in the closet behind the main breaker panel. The > 110V supply for the charger side of the inverter was already routed to > a duplex outlet in the charger compartment. I seem to recall that > being 12/2 wire, and I've had no problems with the breaker tripping > when there is a 100A charge dumping into the batteries. You can > program the ProSine to know the size of the breaker. > > Shane Fedeli > 85PT40 > Hershey, PA > > --- In WanderlodgeForum@yahoogroups.com, "mbrund" <mbrund@> wrote: > > > > Well here goes nothing. Ripped out the old Heart 2000 and twin Iota > > 45's today. Pulled the charger electrical box and the jbox for the > > inverted circuit off the firewall. The conduit is too small (1/2") > > for the new 50AMP circuits that need to be run to and from the new > > Xantrex RS3000. So will have to cut a larger hole in the floor > > behind the curb side draw in the bed room below the circuit breaker > > panel into the engine comparment next to the old circuits. Will > > then run teo new 3/4" liquid tight conduits from there to the > > inverter box above the batteries. > > > > Will need to pull the original 50 AMP circuit at the coach breaker > > panel and run it to a new 50 AMP breaker panel. Will mount the new > > breaker panel behind the current breaker panel but facing the other > > direction into the shirt closet, will cut an access panel in the > > shirt closet upper left storage area so the breaker cab be reset if > > it trips. Will then need to run out of this breaker panel to the > > inverter input. Then return from the inverter to the original 50 > > AMP breaker in the coach. The down side is that everything in the > > coach will be able to be on the inverter when shore power is lost. > > But I plan to add the Auto-generator start to the RS3000 so if I > > lose shore power it will start the generator when the batteries get > > down to a set voltage. > > > > Anyone else been down this road? If so would be interested in > > hearing what you did. > > > > I know some have replaced the original Heart with a Xantrex RS2000, > > the issue they may or may not know is that the RS2000/3000 doesn't > > have a built in circuit breaker. The old Heart inverters in our > > coaches have a 15 amp breaker on the inverted circuit. The way the > > older WB's are designed requires a circuit breaker in the inverter > > as there is no breaker on the inverted side of the coach AC circuits > > due to the way the WB engineers designed using relays vs a 2nd > > breaker panel. So if you have swapped your inverter out, please > > make sure that either your inverter is a built-in circuit breaker, > > or that you have added an external breaker to the inverted circuit. > > > > Michael Brundridge > > 92 WB40 > > Georgetown, TX > > > |
|||
11-27-2007, 03:14
Post: #6
|
|||
|
|||
Installing new Xantrex RS3000
If possible, I also install a rubber grommet (available from many
hardware stores) in the hole to further protect the wires/tubing, etc. When I pulled some wires from the basement into the interior, I also sealed the hole with a generous blob of silicone caulk -- in addition to blocking unwanted air flow, it tends to hold the wire (or tubing) so that it won't rub on the edges of the hole and wear. Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 aeonix1@... On the road at Lockhart Texas On Nov 26, 2007, at 10:57 PM, Gregory OConnor wrote: > <snip> > when I pas a hydrolic line through plys of steel, I make the hole > round and larger. Round to keep from cracking, large to keep frm > slicing the product. > > GregoryO'Connor > 94ptRomolandca > |
|||
11-27-2007, 03:22
Post: #7
|
|||
|
|||
Installing new Xantrex RS3000
100 amp charge at 12 v is about 8.5 amps at 120 vac (plus conversion
losses). It's no wonder the breaker doesn't trip as this is a modest draw on the 120 vac side. Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 aeonix1@... On the road at Lockhart Texas On Nov 27, 2007, at 8:06 AM, sfedeli3 wrote: > Hi Michael, > > <snip> I've had no problems with the breaker tripping > when there is a 100A charge dumping into the batteries. You can > program the ProSine to know the size of the breaker. |
|||