I have several problems with my Kuboto generator and before I start the
repairs I need some advice. First it does not use oil but smokes badly, to the point that it actually leaves some soot inside the coach. It has several diesel leaks. On a warm day it will overheat unless I slide it out and then it will run cool all day. It is noisy, loud as all get out. I covet those who have whisper quite generators. I'm thinking about a complete overhaul to replace all gaskets, etc. Injector pump rebuild, new injectors, new fuel lines to replace any leaking, radiator rod out, new muffler. Also the hydraulic generator slide out has quit, but I think repairing that may be over my head. It has gotten to the point that I dread starting up the ginny and it makes travel alot less enjoyable. All thoughts and advice would be welcomed before I do anything. Bill Garlen 84PT40 Jesup, GA |
|||
02-02-2008, 03:56
Post: #2
|
|||
|
|||
84 PT40 - Genset Problems
Just a few suggestions.
Overheating is a real concern, Check the cooling fans, then pull and service the radiator and cooling system including the thermostat. This probably will not stop the smoke , some smoke is normal. change the fuel filters and oil, adjust the valves, this may help. Bill 88 FC Michigan --- In WanderlodgeForum@yahoogroups.com, "jesupbill" > > I have several problems with my Kuboto generator and before I start the > repairs I need some advice. First it does not use oil but smokes badly, > to the point that it actually leaves some soot inside the coach. It has > several diesel leaks. On a warm day it will overheat unless I slide it > out and then it will run cool all day. It is noisy, loud as all get > out. I covet those who have whisper quite generators. > > I'm thinking about a complete overhaul to replace all gaskets, etc. > Injector pump rebuild, new injectors, new fuel lines to replace any > leaking, radiator rod out, new muffler. Also the hydraulic generator > slide out has quit, but I think repairing that may be over my head. > > It has gotten to the point that I dread starting up the ginny and it > makes travel alot less enjoyable. All thoughts and advice would be > welcomed before I do anything. > > Bill Garlen > 84PT40 > Jesup, GA > |
|||
02-02-2008, 04:06
Post: #3
|
|||
|
|||
84 PT40 - Genset Problems
On the smoking-do you use a vertical exhaust when parked? I
fabricated one last year, and after a few months, I was smoking horribly. Turned out that the un-vented vertical exhaust was creating too much back pressure and it was kicking out oil, in fact the muffler was full of oil. I fabricated a new vertical exhaust that is vented. On the noise-these are noisy units. All you can do it insulated the heck out of the compartment and try to isolate vibrations...for instance, I discovered that my cooling fan was vibrating and passing a resonant sound through the coach. A few strategically placed washers wedged between the mount & the frame solved that problem and reduced noise noticably. Chasing generator noise is one of my main hobbies. Scott Forman 86 PT38 Memphis --- In WanderlodgeForum@yahoogroups.com, "jesupbill" > > I have several problems with my Kuboto generator and before I start the > repairs I need some advice. First it does not use oil but smokes badly, > to the point that it actually leaves some soot inside the coach. It has > several diesel leaks. On a warm day it will overheat unless I slide it > out and then it will run cool all day. It is noisy, loud as all get > out. I covet those who have whisper quite generators. > > I'm thinking about a complete overhaul to replace all gaskets, etc. > Injector pump rebuild, new injectors, new fuel lines to replace any > leaking, radiator rod out, new muffler. Also the hydraulic generator > slide out has quit, but I think repairing that may be over my head. > > It has gotten to the point that I dread starting up the ginny and it > makes travel alot less enjoyable. All thoughts and advice would be > welcomed before I do anything. > > Bill Garlen > 84PT40 > Jesup, GA > |
|||
02-02-2008, 04:09
Post: #4
|
|||
|
|||
84 PT40 - Genset Problems
Always look at the simple stuff first. You will save a lot of money
over time taking this approach. While all of these older generators are louder and smoke more that the newer one they can be reliable and bearable. The first thing I would check is the air filter/inlet for any obstructions or a stopped up filter. In reading your post the comment about overheating is a big concern. While the generator should have a high temp shutoff on a coach this old it may or may not work. How Hot did it get, how many times, High temp is death to these engines. How many hours on the generator, How long have you had it, did it do this when you purchased it. Other things to check are any unusual noises, a knocking noise that sounds like a bad rod bearing can be a bad injector(lots of smoke). Check the oil, is it normal looking, overfull? All of these things can give you clues about the source of the problem. I don't remember if the 84 has the side or front mounted radiator. If it is the side mount check to see if when the gen set is in that you are not colapsing one of the coolant lines to the radiator. Hope some of this helps. Mike Mcmahan 96 Wanderlodge 42' --- In WanderlodgeForum@yahoogroups.com, "jesupbill" > > I have several problems with my Kuboto generator and before I start the > repairs I need some advice. First it does not use oil but smokes badly, > to the point that it actually leaves some soot inside the coach. It has > several diesel leaks. On a warm day it will overheat unless I slide it > out and then it will run cool all day. It is noisy, loud as all get > out. I covet those who have whisper quite generators. > > I'm thinking about a complete overhaul to replace all gaskets, etc. > Injector pump rebuild, new injectors, new fuel lines to replace any > leaking, radiator rod out, new muffler. Also the hydraulic generator > slide out has quit, but I think repairing that may be over my head. > > It has gotten to the point that I dread starting up the ginny and it > makes travel alot less enjoyable. All thoughts and advice would be > welcomed before I do anything. > > Bill Garlen > 84PT40 > Jesup, GA > |
|||
02-02-2008, 04:14
Post: #5
|
|||
|
|||
84 PT40 - Genset Problems
|
|||
02-02-2008, 06:20
Post: #6
|
|||
|
|||
84 PT40 - Genset Problems
Hey, Bob, haven't talked to you in a long time. Hope your doing good.
Of course you remember when I bought this coach, you were a great help and I'll never forget your kindness. How hard is the swap-out and is the newer generator quieter. Mine is a front mounted radiator and actually starts and runs good everytime, except for all these problems. It uses no oil and when slid out will run forever. But that puts smoky exhaust under the coach and makes it louder. Bill Garlen 84PT40 Jesup, GA --- In WanderlodgeForum@yahoogroups.com, "bloomas" wrote: > > > ----- Original Message ----- > From: jesupbill > To: WanderlodgeForum@yahoogroups.com > Sent: Saturday, February 02, 2008 9:41 AM > Subject: [WanderlodgeForum] 84 PT40 - Genset Problems Hi Bill Back about seven years ago I was having oil leaks fuel leaks and black soot.I got a price for > repairs and then a price for a new 12 KW power teck.There was not that much difference in price so I opted > for the new generator.Was able to sell the old one that help to get the cost down. > Bob Loomas 1985 PT 36 > Harahan La. > > > I have several problems with my Kuboto generator and before I start the > repairs I need some advice. First it does not use oil but smokes badly, > to the point that it actually leaves some soot inside the coach. It has > several diesel leaks. On a warm day it will overheat unless I slide it > out and then it will run cool all day. It is noisy, loud as all get > out. I covet those who have whisper quite generators. > > I'm thinking about a complete overhaul to replace all gaskets, etc. > Injector pump rebuild, new injectors, new fuel lines to replace any > leaking, radiator rod out, new muffler. Also the hydraulic generator > slide out has quit, but I think repairing that may be over my head. > > It has gotten to the point that I dread starting up the ginny and it > makes travel alot less enjoyable. All thoughts and advice would be > welcomed before I do anything. > > Bill Garlen > 84PT40 > Jesup, GA > |
|||
02-02-2008, 06:28
Post: #7
|
|||
|
|||
84 PT40 - Genset Problems
Soot is a sign of incomplete diesel combustion. Check the air cleaner and ensure that the exhaust pipe isn't blocked. I had severe sooting from my Kubota engined PowerTech. I found the crankcase breather terminated about a foot from the air cleaner air intake. While the output from the breather wasn't much, it was "killing" the air filter after only a short time. I replaced the crankcase breather tube with a longer one and found I could route it outside the generator enclosure by slipping it past some foam sound insulation where the door and enclosure box meet, so I didn't have to drill a hole through the enclosure.
Also check the exhaust pipe for blockage/constriction. Once the sooting started, I discovered that the soot built up in the alternate exhaust stack (that goes through the roof in my coach). [I don't know if your unit has this feature.] Once I opened the bottom exhaust opening, a considerable amount of soot was ejected (making a _huge_ mess). However, after replacing the air cleaner filter and getting the soot accumulation out of the exhaust pipe, the generator runs much cleaner and with little black smoke once it gets going. Your generator engine may need the complete going over you suggest and it sure sounds like you have some cooling problems. (Be sure the cooling fan is operating 100% of the time that engine is running. If it is "cycling" on and off, that's a sign that the motor is wearing out. There is no thermostat (that I know of) in the system that cycles the fan. It should come on shortly after start up (when the generator starts outputting electricity) and run until the system is shut down. If the engine has enough hours, then the fuel lines, gaskets, injector pump, etc. may be necessary -- that's a judgment you'll have to make. Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 El Sobrante CA "aeonix1@mac.com" On Feb 2, 2008, at 7:41 AM, jesupbill wrote:
|
|||
02-02-2008, 06:36
Post: #8
|
|||
|
|||
84 PT40 - Genset Problems
I wish my generator had the squirrel cage instead of the front radiator. Mine, also, quite loud.
Ernie Ekberg 83PT40 Weatherford, Tx Who's never won? Biggest Grammy Award surprises of all time on AOL Music. |
|||
02-02-2008, 08:06
Post: #9
|
|||
|
|||
84 PT40 - Genset Problems
I got lucky on my 83. My radiator is in the left side.
Paul Downey
Versailles Ky
83PT35
Our Rollin Home Who's never won? Biggest Grammy Award surprises of all time on AOL Music. |
|||
02-02-2008, 11:12
Post: #10
|
|||
|
|||
84 PT40 - Genset Problems
I think Scott gives good advice on the exhaust system checkup. a
plugged system will make the unit run hot, smoke and shake. the vibration is almost as bad as the noise. Pete may be on to something when he refers to oil getting sucked up into the intake because as you state that your kubota leaks oil all over. I wonder if opening the genset compartment is not cooling the engine but giving starved air to the intake???? if the closed compartment is too sealed off it is choking the turbo for air and this will also make it run hot and smoke???? GregoryO'Connor 94ptRomolandCa --- In WanderlodgeForum@yahoogroups.com, "jesupbill" wrote: > > I have several problems with my Kuboto generator and before I start the > repairs I need some advice. First it does not use oil but smokes badly, > to the point that it actually leaves some soot inside the coach. It has > several diesel leaks. On a warm day it will overheat unless I slide it > out and then it will run cool all day. It is noisy, loud as all get > out. I covet those who have whisper quite generators. > > I'm thinking about a complete overhaul to replace all gaskets, etc. > Injector pump rebuild, new injectors, new fuel lines to replace any > leaking, radiator rod out, new muffler. Also the hydraulic generator > slide out has quit, but I think repairing that may be over my head. > > It has gotten to the point that I dread starting up the ginny and it > makes travel alot less enjoyable. All thoughts and advice would be > welcomed before I do anything. > > Bill Garlen > 84PT40 > Jesup, GA > |
|||