Primus System
02-24-2006, 23:36
Primus System
Your panel in the rear is indicating just fine and you can operate with just
that side of the coach. You do not need to run the panel in the driver area. You can put the system on and go to the rear of the coach and here the boiler running. If it shuts down prematurely, there is a little reset button in the output line of the boiler. Your front unit could have a problem with the reset in that line, a bad thermister or it could have a bad board in the control unit. I would need more intormation before I could tell you more. So the end result is, you should be able to get ample heat with just the rear unit on. It will provide heat on the driver side of the coach from front to rear. R.E. (Ron) Marabito, Dallas, TX 92WB40 [Non-text portions of this message have been removed] |
02-25-2006, 04:05
Primus System
I am going to do some looking in the archives, but I wanted to get my
heat on today. When I turn on the boiler button in the bedroom, the light comes on green and stays green as if the system is working. I then go to the panel above the driver and press the boiler button and it turns red and then within a few seconds the fault light comes on. I tried it also without the bedroom control on and I still get a red light and fault light at the driver panel. After I press the boiler button on the driver's panel, I hear a humming sound outside somewhere (sounds like the front of the coach) and then a 'pop' kind of sound. I have the inverter on, I am plugged into 20 amp shore power to keep a charge on the batteries. The water system is winterized (no water in the coach) and the water heater breaker is turned off. I have the Summer/Winter switch turned to Winter. I am just trying to heat the coach, but I am not sure what is wrong. My guy who was working on the coach after I first bought it indicated that all heating systems worked fine. Brian Gatley 92 WLWB PT 40 Bend, OR [Non-text portions of this message have been removed] |
02-25-2006, 04:26
Primus System
Brian
The two controllers (switches) are seperate from each other as I recall. On controller (front) operates the left side exchangers and the other controller operates the right side exchangers. It has been awhile since our 91 coach but I believe they controll each individual boiler. And of course be certain you have plenty of propane! Fred & Jeanne Hulse Morristown Arizona 1997 Wanderlodge PT41 |
02-25-2006, 04:55
Primus System
Ron,
What other kind of information do you need to get the front panel working? This is the main panel and I do want to get it all working. We are cold here and I will need both sides working, plus the storage bays. Also, I want to get everything on the coach working. Any idea what the hum and then pop sounds might be? Is something else happening? Brian Gatley 93 WLWB PT 40 Bend, OR -----Original Message----- From: WanderlodgeForum@yahoogroups.com [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of erniecarpet@... Sent: Saturday, February 25, 2006 8:36 AM To: WanderlodgeForum@yahoogroups.com Subject: Re: [WanderlodgeForum] Primus System Your panel in the rear is indicating just fine and you can operate with just that side of the coach. You do not need to run the panel in the driver area. You can put the system on and go to the rear of the coach and here the boiler running. If it shuts down prematurely, there is a little reset button in the output line of the boiler. Your front unit could have a problem with the reset in that line, a bad thermister or it could have a bad board in the control unit. I would need more intormation before I could tell you more. So the end result is, you should be able to get ample heat with just the rear unit on. It will provide heat on the driver side of the coach from front to rear. R.E. (Ron) Marabito, Dallas, TX 92WB40 [Non-text portions of this message have been removed] SPONSORED LINKS Recreational <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z -8HJdysB3QLPj9U0JvqYQ> Automotive <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance Recreational <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles Automotive <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators _____ YAHOO! GROUPS LINKS * Visit your group "WanderlodgeForum <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. * To unsubscribe from this group, send an email to: WanderlodgeForum-unsubscribe@yahoogroups.com * Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . _____ [Non-text portions of this message have been removed] |
02-25-2006, 05:27
Primus System
Ok, here is what is happening with the front panel. I had someone press
the button for me while I tried to see what was happening. When the front panel boiler button is pressed, the boiler sounds like it is on, but there is very light white smoke coming from the top of the boiler and kind of a hum noise (like it is fired, trying to fire or something). The boiler light on the panel is red and so there is some sort of problem and then a little while later the fault light comes on. This is the first time I have tried to run the heater since buying the coach. It did work in the past according to the previous owner and my mechanic. Any ideas? Brian Gatley 93 WLWB PT 40 -----Original Message----- From: WanderlodgeForum@yahoogroups.com [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of Brian Gatley Sent: Saturday, February 25, 2006 8:55 AM To: WanderlodgeForum@yahoogroups.com Subject: RE: [WanderlodgeForum] Primus System Ron, What other kind of information do you need to get the front panel working? This is the main panel and I do want to get it all working. We are cold here and I will need both sides working, plus the storage bays. Also, I want to get everything on the coach working. Any idea what the hum and then pop sounds might be? Is something else happening? Brian Gatley 93 WLWB PT 40 Bend, OR -----Original Message----- From: WanderlodgeForum@yahoogroups.com [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of erniecarpet@... Sent: Saturday, February 25, 2006 8:36 AM To: WanderlodgeForum@yahoogroups.com Subject: Re: [WanderlodgeForum] Primus System Your panel in the rear is indicating just fine and you can operate with just that side of the coach. You do not need to run the panel in the driver area. You can put the system on and go to the rear of the coach and here the boiler running. If it shuts down prematurely, there is a little reset button in the output line of the boiler. Your front unit could have a problem with the reset in that line, a bad thermister or it could have a bad board in the control unit. I would need more intormation before I could tell you more. So the end result is, you should be able to get ample heat with just the rear unit on. It will provide heat on the driver side of the coach from front to rear. R.E. (Ron) Marabito, Dallas, TX 92WB40 [Non-text portions of this message have been removed] SPONSORED LINKS Recreational <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > &k=Recreational+vehicles&w1=Recreation al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > &k=Wanderlodge&w1=Recreational+vehicle s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z -8HJdysB3QLPj9U0JvqYQ> Automotive <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > &k=Automotive+maintenance&w1=Recreatio nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance Recreational <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > &k=Recreational+vehicle+dealer&w1=Recr eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > &k=Used+recreational+vehicles&w1=Recre ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles Automotive <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > &k=Automotive+radiators&w1=Recreationa l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators _____ YAHOO! GROUPS LINKS * Visit your group "WanderlodgeForum <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. * To unsubscribe from this group, send an email to: WanderlodgeForum-unsubscribe@yahoogroups.com * Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . _____ [Non-text portions of this message have been removed] SPONSORED LINKS Recreational <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z -8HJdysB3QLPj9U0JvqYQ> Automotive <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance Recreational <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles Automotive <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators _____ YAHOO! GROUPS LINKS * Visit your group "WanderlodgeForum <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. * To unsubscribe from this group, send an email to: WanderlodgeForum-unsubscribe@yahoogroups.com * Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . _____ [Non-text portions of this message have been removed] |
02-25-2006, 05:35
Primus System
Don't care if it's cold or not, one unit can handle you. I've
operated with one unit down to zero degrees. The humming and pop is the pump running and the firing of the boiler probably. All normal. Simplest troubleshoot is to check the reset in the line of the output side of the boiler and then check to see if driver area control will fire system. If not, then you have to check the thermistor, which will be the one in the galley under the overhead cabinet on the driver side. It is a small black plastic finned unit about the size of a silver dollar and 3/4inch thick. Remove it and disconnect the two wires. Keep them separate and try firing the unit from the panel. If it fires, touch the two wires together and it should shut down the unit. If it doesn't fire, more then likely you have a bad board in the controller. It is possible that the board on the boiler is bad too, but you have to go through it methodically. The boards are pretty expensive. Remove the controll panel and check all the connections and inspect to see if anything is obvious. I can't help you much past that, other than to make sure you have adequate coolant in your reservoirs in the upper rear of your engine compartment. Those reset buttons in the output lines are high temperature cut-outs and when they go off, sometimes the reservoir will blow out coolant from the steam that develops in the line. If push comes to shove on tripping of the high-temp reset, then simply take the wires loose and connect them by-passing that safety. This is a redundant safety since there is another built-in to the boiler. Hope that helps some. R.E. (Ron) Marabito, Dallas, TX 92WB40 --- In WanderlodgeForum@yahoogroups.com, "Brian Gatley" > > Ron, > > What other kind of information do you need to get the front panel > working? This is the main panel and I do want to get it all working. > We are cold here and I will need both sides working, plus the storage > bays. Also, I want to get everything on the coach working. > > Any idea what the hum and then pop sounds might be? Is something else > happening? > > Brian Gatley > 93 WLWB PT 40 > Bend, OR > > -----Original Message----- > From: WanderlodgeForum@yahoogroups.com > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of > erniecarpet@... > Sent: Saturday, February 25, 2006 8:36 AM > To: WanderlodgeForum@yahoogroups.com > Subject: Re: [WanderlodgeForum] Primus System > > > Your panel in the rear is indicating just fine and you can operate with > just > that side of the coach. You do not need to run the panel in the driver > > area. You can put the system on and go to the rear of the coach and > here the > boiler running. If it shuts down prematurely, there is a little reset > button in > the output line of the boiler. > > Your front unit could have a problem with the reset in that line, a bad > > thermister or it could have a bad board in the control unit. > > I would need more intormation before I could tell you more. So the end > > result is, you should be able to get ample heat with just the rear unit > on. It > will provide heat on the driver side of the coach from front to rear. > > R.E. (Ron) Marabito, Dallas, TX 92WB40 > > > > [Non-text portions of this message have been removed] > > > > > SPONSORED LINKS > Recreational > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > -8HJdysB3QLPj9U0JvqYQ> Automotive > <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > Recreational > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > Automotive > <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > _____ > > YAHOO! GROUPS LINKS > > > > * Visit your group "WanderlodgeForum > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > * To unsubscribe from this group, send an email to: > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > Service <http://docs.yahoo.com/info/terms/> . > > > _____ > > > > > [Non-text portions of this message have been removed] > |
02-25-2006, 05:47
Primus System
The light white smoke indicates that the igniter is probably working
O.K., but you are not lighting the burner successfully. I've not dealt with that problem before, so not sure if it is a propane supply problem or the board on the boiler not turning on the propane. Since I'm not there, no way to know. Make sure you follow the troubleshooting guide that is provided in your manual that comes with the system. It is referred to as a Fault Tracing Schedule. It should give you some additional help. If you don't have it, let me know. Unfortunately, I am at a rally till tomorrow and do not have my scanner with me or I could send that portion to you. R.E. (Ron) Marabito, Dallas, TX 92WB40 --- In WanderlodgeForum@yahoogroups.com, "Brian Gatley" > > Ok, here is what is happening with the front panel. I had someone press > the button for me while I tried to see what was happening. > > When the front panel boiler button is pressed, the boiler sounds like it > is on, but there is very light white smoke coming from the top of the > boiler and kind of a hum noise (like it is fired, trying to fire or > something). The boiler light on the panel is red and so there is some > sort of problem and then a little while later the fault light comes on. > > This is the first time I have tried to run the heater since buying the > coach. It did work in the past according to the previous owner and my > mechanic. > > Any ideas? > > Brian Gatley > 93 WLWB PT 40 > > -----Original Message----- > From: WanderlodgeForum@yahoogroups.com > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of Brian Gatley > Sent: Saturday, February 25, 2006 8:55 AM > To: WanderlodgeForum@yahoogroups.com > Subject: RE: [WanderlodgeForum] Primus System > > > Ron, > > What other kind of information do you need to get the front panel > working? This is the main panel and I do want to get it all working. > We are cold here and I will need both sides working, plus the storage > bays. Also, I want to get everything on the coach working. > > Any idea what the hum and then pop sounds might be? Is something else > happening? > > Brian Gatley > 93 WLWB PT 40 > Bend, OR > > -----Original Message----- > From: WanderlodgeForum@yahoogroups.com > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of > erniecarpet@... > Sent: Saturday, February 25, 2006 8:36 AM > To: WanderlodgeForum@yahoogroups.com > Subject: Re: [WanderlodgeForum] Primus System > > > Your panel in the rear is indicating just fine and you can operate with > just > that side of the coach. You do not need to run the panel in the driver > > area. You can put the system on and go to the rear of the coach and > here the > boiler running. If it shuts down prematurely, there is a little reset > button in > the output line of the boiler. > > Your front unit could have a problem with the reset in that line, a bad > > thermister or it could have a bad board in the control unit. > > I would need more intormation before I could tell you more. So the end > > result is, you should be able to get ample heat with just the rear unit > on. It > will provide heat on the driver side of the coach from front to rear. > > R.E. (Ron) Marabito, Dallas, TX 92WB40 > > > > [Non-text portions of this message have been removed] > > > > > SPONSORED LINKS > Recreational > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > > &k=Recreational+vehicles&w1=Recreation > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > > &k=Wanderlodge&w1=Recreational+vehicle > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > -8HJdysB3QLPj9U0JvqYQ> Automotive > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > > &k=Automotive+maintenance&w1=Recreatio > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > Recreational > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > > &k=Recreational+vehicle+dealer&w1=Recr > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > > &k=Used+recreational+vehicles&w1=Recre > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > Automotive > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > > &k=Automotive+radiators&w1=Recreationa > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > _____ > > YAHOO! GROUPS LINKS > > > > * Visit your group "WanderlodgeForum > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > * To unsubscribe from this group, send an email to: > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > Service <http://docs.yahoo.com/info/terms/> . > > > _____ > > > > > [Non-text portions of this message have been removed] > > > > > SPONSORED LINKS > Recreational > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > -8HJdysB3QLPj9U0JvqYQ> Automotive > <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > Recreational > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > Automotive > <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > _____ > > YAHOO! GROUPS LINKS > > > > * Visit your group "WanderlodgeForum > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > * To unsubscribe from this group, send an email to: > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > Service <http://docs.yahoo.com/info/terms/> . > > > _____ > > > > > [Non-text portions of this message have been removed] > |
02-25-2006, 06:16
Primus System
Brian I'm hoping Stephen Birtles chimes in here. He seems to know a thing
or three about these Primus systems. Original Message: ----------------- From: Brian Gatley brian@... Date: Sat, 25 Feb 2006 08:05:36 -0800 To: wanderlodge@yahoogroups.com, WanderlodgeForum@yahoogroups.com Subject: [WanderlodgeForum] Primus System I am going to do some looking in the archives, but I wanted to get my heat on today. When I turn on the boiler button in the bedroom, the light comes on green and stays green as if the system is working. I then go to the panel above the driver and press the boiler button and it turns red and then within a few seconds the fault light comes on. I tried it also without the bedroom control on and I still get a red light and fault light at the driver panel. After I press the boiler button on the driver's panel, I hear a humming sound outside somewhere (sounds like the front of the coach) and then a 'pop' kind of sound. I have the inverter on, I am plugged into 20 amp shore power to keep a charge on the batteries. The water system is winterized (no water in the coach) and the water heater breaker is turned off. I have the Summer/Winter switch turned to Winter. I am just trying to heat the coach, but I am not sure what is wrong. My guy who was working on the coach after I first bought it indicated that all heating systems worked fine. Brian Gatley 92 WLWB PT 40 Bend, OR [Non-text portions of this message have been removed] <!-- |**|begin egp html banner|**| --> SPONSORED LINKS
<!-- |**|end egp html banner|**| --> <!-- |**|begin egp html banner|**| --> YAHOO! GROUPS LINKS
<!-- |**|end egp html banner|**| --> -------------------------------------------------------------------- mail2web - Check your email from the web at http://mail2web.com/ . |
02-25-2006, 07:06
Primus System
Thank you Ron.
I finally got a hold of my mechanic on the phone. Here is what we did and I will see if the coach gets heat: 1. Make sure I was getting propane. Make sure LPG valve is on and master switch on. Light stove. Works fine. 2. Turn on bedroom Primus boiler button. Light is green, but no indication of boiler firing up (no sound, no noise, nothing). 3. With bedroom boiler button on, I turned on the drivers boiler button. Boiler(s) begin to fire. Looks like steam and condensation coming out, but eventually it calms down and sounds like normal boilers running. 4. Boiler button light at drivers panel is still red and the button at bedroom is green. Manual says nothing about a red light. After a while heat is being produced on both sides of the coach. Both rheostat fan controls in the bathroom and kitchen work and push warm air. The front control panel still has a red light at the boiler button and I can't find reference to it in the manuals, except vaguely when testing control panel and adjusting temperature gauge. I can't tell if there is an implication from the manual that the panel is not getting adequate voltage or not when the red light is lit. Everything seems to heat up fine so far. Bedroom is a little cold, but hopefully it will warm up also. Can't find any coils except for under the bed. Brian Gatley 93 WLWB PT40 Bend, OR -----Original Message----- From: WanderlodgeForum@yahoogroups.com [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of ronmarabito2002 Sent: Saturday, February 25, 2006 9:47 AM To: WanderlodgeForum@yahoogroups.com Subject: [WanderlodgeForum] Re: Primus System The light white smoke indicates that the igniter is probably working O.K., but you are not lighting the burner successfully. I've not dealt with that problem before, so not sure if it is a propane supply problem or the board on the boiler not turning on the propane. Since I'm not there, no way to know. Make sure you follow the troubleshooting guide that is provided in your manual that comes with the system. It is referred to as a Fault Tracing Schedule. It should give you some additional help. If you don't have it, let me know. Unfortunately, I am at a rally till tomorrow and do not have my scanner with me or I could send that portion to you. R.E. (Ron) Marabito, Dallas, TX 92WB40 --- In WanderlodgeForum@yahoogroups.com, "Brian Gatley" wrote: > > Ok, here is what is happening with the front panel. I had someone press > the button for me while I tried to see what was happening. > > When the front panel boiler button is pressed, the boiler sounds like it > is on, but there is very light white smoke coming from the top of the > boiler and kind of a hum noise (like it is fired, trying to fire or > something). The boiler light on the panel is red and so there is some > sort of problem and then a little while later the fault light comes on. > > This is the first time I have tried to run the heater since buying the > coach. It did work in the past according to the previous owner and my > mechanic. > > Any ideas? > > Brian Gatley > 93 WLWB PT 40 > > -----Original Message----- > From: WanderlodgeForum@yahoogroups.com > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of Brian Gatley > Sent: Saturday, February 25, 2006 8:55 AM > To: WanderlodgeForum@yahoogroups.com > Subject: RE: [WanderlodgeForum] Primus System > > > Ron, > > What other kind of information do you need to get the front panel > working? This is the main panel and I do want to get it all working. > We are cold here and I will need both sides working, plus the storage > bays. Also, I want to get everything on the coach working. > > Any idea what the hum and then pop sounds might be? Is something else > happening? > > Brian Gatley > 93 WLWB PT 40 > Bend, OR > > -----Original Message----- > From: WanderlodgeForum@yahoogroups.com > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of > erniecarpet@... > Sent: Saturday, February 25, 2006 8:36 AM > To: WanderlodgeForum@yahoogroups.com > Subject: Re: [WanderlodgeForum] Primus System > > > Your panel in the rear is indicating just fine and you can operate with > just > that side of the coach. You do not need to run the panel in the driver > > area. You can put the system on and go to the rear of the coach and > here the > boiler running. If it shuts down prematurely, there is a little reset > button in > the output line of the boiler. > > Your front unit could have a problem with the reset in that line, a bad > > thermister or it could have a bad board in the control unit. > > I would need more intormation before I could tell you more. So the end > > result is, you should be able to get ample heat with just the rear unit > on. It > will provide heat on the driver side of the coach from front to rear. > > R.E. (Ron) Marabito, Dallas, TX 92WB40 > > > > [Non-text portions of this message have been removed] > > > > > SPONSORED LINKS > Recreational > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > &k=Recreational+vehicles&w1=Recreation > > &k=Recreational+vehicles&w1=Recreation > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > &k=Wanderlodge&w1=Recreational+vehicle > > &k=Wanderlodge&w1=Recreational+vehicle > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > -8HJdysB3QLPj9U0JvqYQ> Automotive > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > &k=Automotive+maintenance&w1=Recreatio > > &k=Automotive+maintenance&w1=Recreatio > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > Recreational > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > &k=Recreational+vehicle+dealer&w1=Recr > > &k=Recreational+vehicle+dealer&w1=Recr > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > &k=Used+recreational+vehicles&w1=Recre > > &k=Used+recreational+vehicles&w1=Recre > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > Automotive > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > &k=Automotive+radiators&w1=Recreationa > > &k=Automotive+radiators&w1=Recreationa > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > _____ > > YAHOO! GROUPS LINKS > > > > * Visit your group "WanderlodgeForum > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > * To unsubscribe from this group, send an email to: > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > Service <http://docs.yahoo.com/info/terms/> . > > > _____ > > > > > [Non-text portions of this message have been removed] > > > > > SPONSORED LINKS > Recreational > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > &k=Recreational+vehicles&w1=Recreation > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > &k=Wanderlodge&w1=Recreational+vehicle > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > -8HJdysB3QLPj9U0JvqYQ> Automotive > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > &k=Automotive+maintenance&w1=Recreatio > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > Recreational > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > &k=Recreational+vehicle+dealer&w1=Recr > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > &k=Used+recreational+vehicles&w1=Recre > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > Automotive > <http://groups.yahoo.com/gads?t=ms <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > &k=Automotive+radiators&w1=Recreationa > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > _____ > > YAHOO! GROUPS LINKS > > > > * Visit your group "WanderlodgeForum > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > * To unsubscribe from this group, send an email to: > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > Service <http://docs.yahoo.com/info/terms/> . > > > _____ > > > > > [Non-text portions of this message have been removed] > SPONSORED LINKS Recreational <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z -8HJdysB3QLPj9U0JvqYQ> Automotive <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance Recreational <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles Automotive <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators _____ YAHOO! GROUPS LINKS * Visit your group "WanderlodgeForum <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. * To unsubscribe from this group, send an email to: WanderlodgeForum-unsubscribe@yahoogroups.com * Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . _____ [Non-text portions of this message have been removed] |
02-25-2006, 09:27
Primus System
What bedroom layout do you have? I have a cross Queen. There is a
coil along the rear side bed isle which is on the drivers side circuit. There is also a coil in the baseboard of the passenger side of the vehicle at the foot of the bed and it is on the passendger side circuit. R.E. (Ron) Marabito, Dallas, TX 92WB40 --- In WanderlodgeForum@yahoogroups.com, "Brian Gatley" > > Thank you Ron. > > I finally got a hold of my mechanic on the phone. Here is what we did > and I will see if the coach gets heat: > > 1. Make sure I was getting propane. Make sure LPG valve is on and > master switch on. Light stove. Works fine. > > 2. Turn on bedroom Primus boiler button. Light is green, but no > indication of boiler firing up (no sound, no noise, nothing). > > 3. With bedroom boiler button on, I turned on the drivers boiler button. > Boiler(s) begin to fire. Looks like steam and condensation coming out, > but eventually it calms down and sounds like normal boilers running. > > 4. Boiler button light at drivers panel is still red and the button at > bedroom is green. Manual says nothing about a red light. > > After a while heat is being produced on both sides of the coach. Both > rheostat fan controls in the bathroom and kitchen work and push warm > air. > > The front control panel still has a red light at the boiler button and I > can't find reference to it in the manuals, except vaguely when testing > control panel and adjusting temperature gauge. I can't tell if there is > an implication from the manual that the panel is not getting adequate > voltage or not when the red light is lit. > > Everything seems to heat up fine so far. Bedroom is a little cold, but > hopefully it will warm up also. Can't find any coils except for under > the bed. > > Brian Gatley > 93 WLWB PT40 > Bend, OR > > -----Original Message----- > From: WanderlodgeForum@yahoogroups.com > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of ronmarabito2002 > Sent: Saturday, February 25, 2006 9:47 AM > To: WanderlodgeForum@yahoogroups.com > Subject: [WanderlodgeForum] Re: Primus System > > > The light white smoke indicates that the igniter is probably working > O.K., but you are not lighting the burner successfully. I've not > dealt with that problem before, so not sure if it is a propane supply > problem or the board on the boiler not turning on the propane. Since > I'm not there, no way to know. Make sure you follow the > troubleshooting guide that is provided in your manual that comes with > the system. It is referred to as a Fault Tracing Schedule. It should > give you some additional help. If you don't have it, let me know. > Unfortunately, I am at a rally till tomorrow and do not have my > scanner with me or I could send that portion to you. > > R.E. (Ron) Marabito, Dallas, TX 92WB40 > > --- In WanderlodgeForum@yahoogroups.com, "Brian Gatley" > wrote: > > > > Ok, here is what is happening with the front panel. I had someone > press > > the button for me while I tried to see what was happening. > > > > When the front panel boiler button is pressed, the boiler sounds like > it > > is on, but there is very light white smoke coming from the top of the > > boiler and kind of a hum noise (like it is fired, trying to fire or > > something). The boiler light on the panel is red and so there is some > > sort of problem and then a little while later the fault light comes > on. > > > > This is the first time I have tried to run the heater since buying the > > coach. It did work in the past according to the previous owner and my > > mechanic. > > > > Any ideas? > > > > Brian Gatley > > 93 WLWB PT 40 > > > > -----Original Message----- > > From: WanderlodgeForum@yahoogroups.com > > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of Brian Gatley > > Sent: Saturday, February 25, 2006 8:55 AM > > To: WanderlodgeForum@yahoogroups.com > > Subject: RE: [WanderlodgeForum] Primus System > > > > > > Ron, > > > > What other kind of information do you need to get the front panel > > working? This is the main panel and I do want to get it all working. > > We are cold here and I will need both sides working, plus the storage > > bays. Also, I want to get everything on the coach working. > > > > Any idea what the hum and then pop sounds might be? Is something else > > happening? > > > > Brian Gatley > > 93 WLWB PT 40 > > Bend, OR > > > > -----Original Message----- > > From: WanderlodgeForum@yahoogroups.com > > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of > > erniecarpet@ > > Sent: Saturday, February 25, 2006 8:36 AM > > To: WanderlodgeForum@yahoogroups.com > > Subject: Re: [WanderlodgeForum] Primus System > > > > > > Your panel in the rear is indicating just fine and you can operate > with > > just > > that side of the coach. You do not need to run the panel in the > driver > > > > area. You can put the system on and go to the rear of the coach and > > here the > > boiler running. If it shuts down prematurely, there is a little > reset > > button in > > the output line of the boiler. > > > > Your front unit could have a problem with the reset in that line, a > bad > > > > thermister or it could have a bad board in the control unit. > > > > I would need more intormation before I could tell you more. So the > end > > > > result is, you should be able to get ample heat with just the rear > unit > > on. It > > will provide heat on the driver side of the coach from front to rear. > > > > R.E. (Ron) Marabito, Dallas, TX 92WB40 > > > > > > > > [Non-text portions of this message have been removed] > > > > > > > > > > SPONSORED LINKS > > Recreational > > <http://groups.yahoo.com/gads?t=ms > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > > &k=Recreational+vehicles&w1=Recreation > > > &k=Recreational+vehicles&w1=Recreation > > > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > > > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > > <http://groups.yahoo.com/gads?t=ms > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > > &k=Wanderlodge&w1=Recreational+vehicle > > > &k=Wanderlodge&w1=Recreational+vehicle > > > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > > > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > > -8HJdysB3QLPj9U0JvqYQ> Automotive > > <http://groups.yahoo.com/gads?t=ms > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > > &k=Automotive+maintenance&w1=Recreatio > > > &k=Automotive+maintenance&w1=Recreatio > > > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > > > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > > Recreational > > <http://groups.yahoo.com/gads?t=ms > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > > &k=Recreational+vehicle+dealer&w1=Recr > > > &k=Recreational+vehicle+dealer&w1=Recr > > > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > > > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > > <http://groups.yahoo.com/gads?t=ms > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > > &k=Used+recreational+vehicles&w1=Recre > > > &k=Used+recreational+vehicles&w1=Recre > > > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > > > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > > Automotive > > <http://groups.yahoo.com/gads?t=ms > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > > &k=Automotive+radiators&w1=Recreationa > > > &k=Automotive+radiators&w1=Recreationa > > > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > > > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > > > _____ > > > > YAHOO! GROUPS LINKS > > > > > > > > * Visit your group "WanderlodgeForum > > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > > > > * To unsubscribe from this group, send an email to: > > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > > > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > > Service <http://docs.yahoo.com/info/terms/> . > > > > > > _____ > > > > > > > > > > [Non-text portions of this message have been removed] > > > > > > > > > > SPONSORED LINKS > > Recreational > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > > &k=Recreational+vehicles&w1=Recreation > > > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > > > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > > &k=Wanderlodge&w1=Recreational+vehicle > > > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > > > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > > -8HJdysB3QLPj9U0JvqYQ> Automotive > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > > &k=Automotive+maintenance&w1=Recreatio > > > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > > > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > > Recreational > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > > &k=Recreational+vehicle+dealer&w1=Recr > > > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > > > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > > &k=Used+recreational+vehicles&w1=Recre > > > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > > > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > > Automotive > > <http://groups.yahoo.com/gads?t=ms > <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > > &k=Automotive+radiators&w1=Recreationa > > > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > > > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > > > _____ > > > > YAHOO! GROUPS LINKS > > > > > > > > * Visit your group "WanderlodgeForum > > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > > > > * To unsubscribe from this group, send an email to: > > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > > > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > > Service <http://docs.yahoo.com/info/terms/> . > > > > > > _____ > > > > > > > > > > [Non-text portions of this message have been removed] > > > > > > > > > > > SPONSORED LINKS > Recreational > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicles&w1=Recreation > al+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+veh > icle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s= > 163&.sig=DAUkCKkU7Dzhn_ObWmSYTw> vehicles Wanderlodge > <http://groups.yahoo.com/gads?t=ms&k=Wanderlodge&w1=Recreational+vehicle > s&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehicle+deale > r&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=163&.sig=Z > -8HJdysB3QLPj9U0JvqYQ> Automotive > <http://groups.yahoo.com/gads?t=ms&k=Automotive+maintenance&w1=Recreatio > nal+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+ve > hicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s > =163&.sig=IF4u_5wI8Pmy34cC1O9CxA> maintenance > Recreational > <http://groups.yahoo.com/gads?t=ms&k=Recreational+vehicle+dealer&w1=Recr > eational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreation > al+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators& > c=6&s=163&.sig=z6_XahaeYHfELr6o72IW1A> vehicle dealer Used > <http://groups.yahoo.com/gads?t=ms&k=Used+recreational+vehicles&w1=Recre > ational+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreationa > l+vehicle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c > =6&s=163&.sig=UGEY5km4L-kXbDI4ZSadEw> recreational vehicles > Automotive > <http://groups.yahoo.com/gads?t=ms&k=Automotive+radiators&w1=Recreationa > l+vehicles&w2=Wanderlodge&w3=Automotive+maintenance&w4=Recreational+vehi > cle+dealer&w5=Used+recreational+vehicles&w6=Automotive+radiators&c=6&s=1 > 63&.sig=ePNVMmISsCWgTnMq_4GlXA> radiators > > _____ > > YAHOO! GROUPS LINKS > > > > * Visit your group "WanderlodgeForum > <http://groups.yahoo.com/group/WanderlodgeForum> " on the web. > > > * To unsubscribe from this group, send an email to: > WanderlodgeForum-unsubscribe@yahoogroups.com > > > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of > Service <http://docs.yahoo.com/info/terms/> . > > > _____ > > > > > [Non-text portions of this message have been removed] > |