Replace Roof AC units - 1992 WB40
06-10-2007, 17:10
Well I lost another roof AC unit (cracked copper tubing, again), so
that's it, I am going to replace them now. How do you get the lower unit cover off (these are the stock units that came from BlueBird, so they are the vinyl covered lower covers)? I can not seem to figure out how they are attached so I can get to the two rear most bolts through the AC unit. Still debating between the Dometics or Carrier units. Probably go with Penguins so I don't have to change a bunch of wires. But I will be stuck to what I can get this week as we go on our trip starting next weekend..... |
06-11-2007, 01:58
My inside covers are plastic -- and the screws holding them are
reachable inside after you remove the 'return' screen. While the Dometic Penguins are low profile (and probably exact replacements for what you currently have) you might consider the Dometic Brisk-air "High Efficiency" units. I replaced 2 of my 3 Penguins with these units. They only draw 10 amps (each) instead of the 15 amps of the Penguins. The Dometic brand will work (usually) work with the Dometic thermostats (if you have that arrangement) and simplify the wiring necessary. The downside is that the Brisk-Air units are several inches taller, costing you some clearance. On my coach, the King Dome is already taller -- so the Brisk-Air units didn't really affect my clearance anyway... The high efficiency units are slightly more expensive than the "normal" units -- but you may appreciate being able to run them when available current is limited -- it just gives you that much more margin when using a 30 amp connection, etc. Pete Masterson aeonix1@... '95 Blue Bird Wanderlodge WBDA 42' currently at Chief Hosa, Colorado On Jun 10, 2007, at 11:10 PM, mbrund wrote: > Well I lost another roof AC unit (cracked copper tubing, again), so > that's it, I am going to replace them now. > > How do you get the lower unit cover off (these are the stock units > that came from BlueBird, so they are the vinyl covered lower > covers)? > > I can not seem to figure out how they are attached so I can get to the > two rear most bolts through the AC unit. > > Still debating between the Dometics or Carrier units. Probably go > with Penguins so I don't have to change a bunch of wires. But I will > be stuck to what I can get this week as we go on our trip starting > next weekend..... |
06-11-2007, 06:43
Well because Dometic Tech Support is so bad, and the fact that I
could not get anyone to really tell me what I had to do with the Thermostats (could I convert the wiring etc., which I know I can, but the techs are clueless), I purchased 2 Carrier Heat Pumps which have the sensors in the lower units and hand operated remote controls. I will replace both forward AC's and put new lower units in as well. My current lower units are plywood wrapped with vinyl and I can not see how they are attached to the ceiling. I can find the two forward AC bolts in the return air side, but I thought there are two that would be located in ducted air side as well. But I can not get the lower unit off to see or get to them. Yes I can remove the metal grill that holds the air filter in, but that does not let the lower unit come down. Now that I had to purchase new lower units for the Carrier I can man handle them if I have to because if I destroy them it does not matter. But I would rather not do that. Guess I will call Jessie at BB and see if he can tell me how they are attached. Michael Brundridge 1992 WB40 Georgetown, TX --- In WanderlodgeForum@yahoogroups.com, Pete Masterson wrote: > > My inside covers are plastic -- and the screws holding them are > reachable inside after you remove the 'return' screen. > > While the Dometic Penguins are low profile (and probably exact > replacements for what you currently have) you might consider the > Dometic Brisk-air "High Efficiency" units. I replaced 2 of my 3 > Penguins with these units. They only draw 10 amps (each) instead of > the 15 amps of the Penguins. The Dometic brand will work (usually) > work with the Dometic thermostats (if you have that arrangement) and > simplify the wiring necessary. > > The downside is that the Brisk-Air units are several inches taller, > costing you some clearance. On my coach, the King Dome is already > taller -- so the Brisk-Air units didn't really affect my clearance > anyway... > > The high efficiency units are slightly more expensive than the > "normal" units -- but you may appreciate being able to run them when > available current is limited -- it just gives you that much more > margin when using a 30 amp connection, etc. > > Pete Masterson > aeonix1@... > '95 Blue Bird Wanderlodge WBDA 42' > currently at Chief Hosa, Colorado > > > > On Jun 10, 2007, at 11:10 PM, mbrund wrote: > > > Well I lost another roof AC unit (cracked copper tubing, again), so > > that's it, I am going to replace them now. > > > > How do you get the lower unit cover off (these are the stock units > > that came from BlueBird, so they are the vinyl covered lower > > covers)? > > > > I can not seem to figure out how they are attached so I can get to the > > two rear most bolts through the AC unit. > > > > Still debating between the Dometics or Carrier units. Probably go > > with Penguins so I don't have to change a bunch of wires. But I will > > be stuck to what I can get this week as we go on our trip starting > > next weekend..... > |
06-11-2007, 07:28
I have been trying to figure out how to get that lower cover off.
Please post your results Thanks, Thomas 93 wlwb |
06-11-2007, 12:00
Well I got them off. I purchased two Carrier AirV 15K BTU Heat Pumps,
I have had some internmittent issue with the Primus, so the heat pumps give me heat without the need for Propane as long as the outside temp does not get too low. They also solve the issues of having to replace the dometic thermostats and get the special adapters to convert the ribbon cable to RJ11 as they come with remote thermostats and a built in head in the new lower unit. If your lower units are like mine, where they match the ceiling material, they are attached with four plastic push in retainers. I will send you a picture from the side of the panel. The push pins are located about 3 1/2" in from each corner. To remove the grill: 1) Remove the 6 screws attaching the return air grill to the vinyl covered lower unit 2) Grasp the lower unit with your fingers located on the inside edge of the covers forward edge, and your thumbs on the outside edge about 4" from each corner and pull down. This takes a little force as there are four plastic pins that go from the lower panel up into the coaches roof. These plastic pins have many small retaining fingers that cause the panel to stay and place and you must over come their resistance. 3) Once the front comes lose you will be able to grab the back edge and pull the rear of the unit down in the same fashion. NOTE: I take no responsibility for these instructions, your mileage may vary ![]() Michael Brundridge 1992 WB40 Georgetown, TX --- In WanderlodgeForum@yahoogroups.com, "Thomas Rembert" > > I have been trying to figure out how to get that lower cover off. > Please post your results Thanks, Thomas 93 wlwb > |
06-11-2007, 12:06
I replaced a dometic with a carrier heat pump in my 1981 FC but i didn't like
it. the carrier moves a lot more air and seemed a lot noisier even on the lowest setting. i would be interested in your opinion on them after you get them installed. Thanks Dan 81FC33 Jackson, MS ----- Original Message ----- From: mbrund To: WanderlodgeForum@yahoogroups.com Sent: Monday, June 11, 2007 7:00 PM Subject: [WanderlodgeForum] Re: Replace Roof AC units - 1992 WB40 Well I got them off. I purchased two Carrier AirV 15K BTU Heat Pumps, I have had some internmittent issue with the Primus, so the heat pumps give me heat without the need for Propane as long as the outside temp does not get too low. They also solve the issues of having to replace the dometic thermostats and get the special adapters to convert the ribbon cable to RJ11 as they come with remote thermostats and a built in head in the new lower unit. If your lower units are like mine, where they match the ceiling material, they are attached with four plastic push in retainers. I will send you a picture from the side of the panel. The push pins are located about 3 1/2" in from each corner. To remove the grill: 1) Remove the 6 screws attaching the return air grill to the vinyl covered lower unit 2) Grasp the lower unit with your fingers located on the inside edge of the covers forward edge, and your thumbs on the outside edge about 4" from each corner and pull down. This takes a little force as there are four plastic pins that go from the lower panel up into the coaches roof. These plastic pins have many small retaining fingers that cause the panel to stay and place and you must over come their resistance. 3) Once the front comes lose you will be able to grab the back edge and pull the rear of the unit down in the same fashion. NOTE: I take no responsibility for these instructions, your mileage may vary ![]() Michael Brundridge 1992 WB40 Georgetown, TX --- In WanderlodgeForum@yahoogroups.com, "Thomas Rembert" > > I have been trying to figure out how to get that lower cover off. > Please post your results Thanks, Thomas 93 wlwb > ------------------------------------------------------------------------------ No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.472 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM [Non-text portions of this message have been removed] |
06-11-2007, 12:21
I would say the same thing about the Colemans. We installed the
Coleman Mach 3PS (10AMP units) on our last coach and damn near never got any sleep as the unit's where so noisy. That is one reason I am not replacing the one in the bedroom at this time as the Dometic is nice and quite, especially with the 1/2" thick padded plywood cover that came with it from BB. Michael Brundridge 1992 WB40 Georgetown, TX --- In WanderlodgeForum@yahoogroups.com, "Dan" > > I replaced a dometic with a carrier heat pump in my 1981 FC but i didn't like it. the carrier moves a lot more air and seemed a lot noisier even on the lowest setting. i would be interested in your opinion on them after you get them installed. > Thanks > > Dan > 81FC33 > Jackson, MS > > ----- Original Message ----- > From: mbrund > To: WanderlodgeForum@yahoogroups.com > Sent: Monday, June 11, 2007 7:00 PM > Subject: [WanderlodgeForum] Re: Replace Roof AC units - 1992 WB40 > > > Well I got them off. I purchased two Carrier AirV 15K BTU Heat Pumps, > I have had some internmittent issue with the Primus, so the heat pumps > give me heat without the need for Propane as long as the outside temp > does not get too low. They also solve the issues of having to replace > the dometic thermostats and get the special adapters to convert the > ribbon cable to RJ11 as they come with remote thermostats and a built > in head in the new lower unit. > > If your lower units are like mine, where they match the ceiling > material, they are attached with four plastic push in retainers. I > will send you a picture from the side of the panel. The push pins are > located about 3 1/2" in from each corner. > > To remove the grill: > > 1) Remove the 6 screws attaching the return air grill to the vinyl > covered lower unit > > 2) Grasp the lower unit with your fingers located on the inside edge of > the covers forward edge, and your thumbs on the outside edge about 4" > from each corner and pull down. This takes a little force as there are > four plastic pins that go from the lower panel up into the coaches > roof. These plastic pins have many small retaining fingers that cause > the panel to stay and place and you must over come their resistance. > > 3) Once the front comes lose you will be able to grab the back edge and > pull the rear of the unit down in the same fashion. > > NOTE: I take no responsibility for these instructions, your mileage may > vary ![]() > > Michael Brundridge > 1992 WB40 > Georgetown, TX > > --- In WanderlodgeForum@yahoogroups.com, "Thomas Rembert" > > > > > I have been trying to figure out how to get that lower cover off. > > Please post your results Thanks, Thomas 93 wlwb > > > > > > > > > -------------------------------------------------------------------- ---------- > > > No virus found in this incoming message. > Checked by AVG Free Edition. > Version: 7.5.472 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM > > > [Non-text portions of this message have been removed] > |
06-11-2007, 12:38
Picture of unit posted here:
http://autos.ph.groups.yahoo.com/group/W...os/view/d7 f3?b=1 --- In WanderlodgeForum@yahoogroups.com, "mbrund" <mbrund@...> wrote: > > Well I got them off. I purchased two Carrier AirV 15K BTU Heat Pumps, > I have had some internmittent issue with the Primus, so the heat pumps > give me heat without the need for Propane as long as the outside temp > does not get too low. They also solve the issues of having to replace > the dometic thermostats and get the special adapters to convert the > ribbon cable to RJ11 as they come with remote thermostats and a built > in head in the new lower unit. > > If your lower units are like mine, where they match the ceiling > material, they are attached with four plastic push in retainers. I > will send you a picture from the side of the panel. The push pins are > located about 3 1/2" in from each corner. > > To remove the grill: > > 1) Remove the 6 screws attaching the return air grill to the vinyl > covered lower unit > > 2) Grasp the lower unit with your fingers located on the inside edge of > the covers forward edge, and your thumbs on the outside edge about 4" > from each corner and pull down. This takes a little force as there are > four plastic pins that go from the lower panel up into the coaches > roof. These plastic pins have many small retaining fingers that cause > the panel to stay and place and you must over come their resistance. > > 3) Once the front comes lose you will be able to grab the back edge and > pull the rear of the unit down in the same fashion. > > NOTE: I take no responsibility for these instructions, your mileage may > vary ![]() > > Michael Brundridge > 1992 WB40 > Georgetown, TX > |
06-11-2007, 12:50
One thing we found with the Brisk air is to regularly exercise the fan
or it will seize on the bearing and there is no way to free them up without replacing the fan motor We replaced 2 that were only 2 years old they were covered under warranty but it is a pain in the butt Stephen 77fc35 dometic service parts and appliances available --- In WanderlodgeForum@yahoogroups.com, "mbrund" <mbrund@...> wrote: > > Picture of unit posted here: > > http://autos.ph.groups.yahoo.com/group/W...os/view/d7 > f3?b=1 > > > --- In WanderlodgeForum@yahoogroups.com, "mbrund" <mbrund@> wrote: > > > > Well I got them off. I purchased two Carrier AirV 15K BTU Heat > Pumps, > > I have had some internmittent issue with the Primus, so the heat > pumps > > give me heat without the need for Propane as long as the outside > temp > > does not get too low. They also solve the issues of having to > replace > > the dometic thermostats and get the special adapters to convert the > > ribbon cable to RJ11 as they come with remote thermostats and a > built > > in head in the new lower unit. > > > > If your lower units are like mine, where they match the ceiling > > material, they are attached with four plastic push in retainers. I > > will send you a picture from the side of the panel. The push pins > are > > located about 3 1/2" in from each corner. > > > > To remove the grill: > > > > 1) Remove the 6 screws attaching the return air grill to the vinyl > > covered lower unit > > > > 2) Grasp the lower unit with your fingers located on the inside > edge of > > the covers forward edge, and your thumbs on the outside edge about > 4" > > from each corner and pull down. This takes a little force as there > are > > four plastic pins that go from the lower panel up into the coaches > > roof. These plastic pins have many small retaining fingers that > cause > > the panel to stay and place and you must over come their resistance. > > > > 3) Once the front comes lose you will be able to grab the back edge > and > > pull the rear of the unit down in the same fashion. > > > > NOTE: I take no responsibility for these instructions, your mileage > may > > vary ![]() > > > > Michael Brundridge > > 1992 WB40 > > Georgetown, TX > > > |
06-11-2007, 13:26
Isn't your system ducted? I run the front or center unit at night and
it keeps the bedroom reasonably cool (having cooled the bedroom down with the rear unit first) with little noise. Pete Masterson aeonix1@... '95 Blue Bird Wanderlodge WBDA 42' El Sobrante, CA On Jun 11, 2007, at 6:21 PM, mbrund wrote: > I would say the same thing about the Colemans. We installed the > Coleman Mach 3PS (10AMP units) on our last coach and damn near never > got any sleep as the unit's where so noisy. That is one reason I am > not replacing the one in the bedroom at this time as the Dometic is > nice and quite, especially with the 1/2" thick padded plywood cover > that came with it from BB. > > Michael Brundridge > 1992 WB40 > Georgetown, TX > > --- In WanderlodgeForum@yahoogroups.com, "Dan" >> >> I replaced a dometic with a carrier heat pump in my 1981 FC but i > didn't like it. the carrier moves a lot more air and seemed a lot > noisier even on the lowest setting. i would be interested in your > opinion on them after you get them installed. >> Thanks <snip> |