Maybe this will be a good approach?
I did a little homework and read about the "hot skin test". One post there
mentioned simply checking continuity between neutral and ground on the coach side of the shore power plug (with the power off of course). I've got only 2 Ohms of resistance, should be infinite. Leads me to think that I can do the same test at the panel, checking continuity between the neutral bus bar and ground. Pull one white at a time, and when I finally get an open circuit, there is the problem. I may leave them all disconnected as I proceed to allow for more than 1 bad circuit, checking again after reconnecting each. Does this procedure make sense? John Churchill --- In WanderlodgeForum@yahoogroups.com, "Chuck Wheeler" > > John, > > There are some active circuits even when all breakers are off. They are > involved in the circuit that warns you if you turn the ignition on with > shore power applied. Turning off the breakers only breaks the "hot" side. > If there is a cross between Neutral and ground it will still be there even > with the breakers off. That is why I had to disconnect the neutrals in > order to isolate my problem. There may be a different or better way,but > this was the only way I could think of. > > - Chuck Wheeler- > 1982 FC 31SB Fort Worth TX > > > _____ > > From: WanderlodgeForum@yahoogroups.com > [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of Robin > Sent: Tuesday, March 24, 2009 9:19 PM > To: WanderlodgeForum@yahoogroups.com > Subject: [WanderlodgeForum] gfci still tripping > way > > > Well, I've completely removed both my PowerWatch reverse polarity indicators > to re-do them. Decided to check the coach with them removed and the GFCI > still trips when I plug the 30 amp cord in. It trips when I plug it into > either of the two 30 amp receptacles on the coach. (I do not own a 50 amp > cord.) Trips even though all the breakers are off including individual > circuits, main breaker and the separate 30 amp disconnect breakers. If I > switch the master shore power switch to off, gen or 50 amp it does not trip. > It does trip if this switch is set at 30 amps. If I start with everything at > off, then gradually flip switches it seems to barely hold, but if the > switches are on and I plug in the cord, the GFCI trips, suggesting I am > right at the trip point. > > One possible problem area is the genset which has been replaced in the past, > but does not ever seem to have been run prior to my getting the coach. > > I am looking for advice on the proper troubleshooting technique for this > problem. > > John Churchill > 1980 FC33 > LARGE MARGE > Sanibel, FL > |
|||
03-25-2009, 01:29
Post: #2
|
|||
|
|||
Maybe this will be a good approach?
|
|||
03-25-2009, 02:41
Post: #3
|
|||
|
|||
Maybe this will be a good approach?
That should work, and was what I was trying to say...guess I do not write too clearly. The reason I disconnected more than one at a time was that I had several small "leaks" adding up. The worst was the front heater, but that is when I discovered that the various monitors all cause a little resistance. I had a red marker with me and when I discovered a circuit that caused the resistance to increase when disconnected I put a red mark on it. When finished I had three circuits open, the heater and the two that fed the power monitor and shore power. The heater and shore power monitor I could clear with repairs, the power monitor by design will draw a small ground current for it's proper operation but this is less than .5ma which is well below the GFI trip point. Since you have your power monitor out, I would think you should be able to clear it all.
- Chuck Wheeler-
1982 FC 31SB Fort Worth TX
From: WanderlodgeForum@yahoogroups.com [mailto:WanderlodgeForum@yahoogroups.com] On Behalf Of Robin Sent: Wednesday, March 25, 2009 5:06 AM To: WanderlodgeForum@yahoogroups.com Subject: [WanderlodgeForum] Maybe this will be a good approach? I did a little homework and read about the "hot skin test". One post there mentioned simply checking continuity between neutral and ground on the coach side of the shore power plug (with the power off of course). I've got only 2 Ohms of resistance, should be infinite. Leads me to think that I can do the same test at the panel, checking continuity between the neutral bus bar and ground. Pull one white at a time, and when I finally get an open circuit, there is the problem. I may leave them all disconnected as I proceed to allow for more than 1 bad circuit, checking again after reconnecting each. Does this procedure make sense? John Churchill --- In "WanderlodgeForum%40yahoogroups.com", "Chuck Wheeler" > > John, > > There are some active circuits even when all breakers are off. They are > involved in the circuit that warns you if you turn the ignition on with > shore power applied. Turning off the breakers only breaks the "hot" side. > If there is a cross between Neutral and ground it will still be there even > with the breakers off. That is why I had to disconnect the neutrals in > order to isolate my problem. There may be a different or better way,but > this was the only way I could think of. > > - Chuck Wheeler- > 1982 FC 31SB Fort Worth TX > > > _____ > > From: "WanderlodgeForum%40yahoogroups.com" > [mailto:"WanderlodgeForum%40yahoogroups.com"] On Behalf Of Robin > Sent: Tuesday, March 24, 2009 9:19 PM > To: "WanderlodgeForum%40yahoogroups.com" > Subject: [WanderlodgeForum] gfci still tripping > way > > > Well, I've completely removed both my PowerWatch reverse polarity indicators > to re-do them. Decided to check the coach with them removed and the GFCI > still trips when I plug the 30 amp cord in. It trips when I plug it into > either of the two 30 amp receptacles on the coach. (I do not own a 50 amp > cord.) Trips even though all the breakers are off including individual > circuits, main breaker and the separate 30 amp disconnect breakers. If I > switch the master shore power switch to off, gen or 50 amp it does not trip. > It does trip if this switch is set at 30 amps. If I start with everything at > off, then gradually flip switches it seems to barely hold, but if the > switches are on and I plug in the cord, the GFCI trips, suggesting I am > right at the trip point. > > One possible problem area is the genset which has been replaced in the past, > but does not ever seem to have been run prior to my getting the coach. > > I am looking for advice on the proper troubleshooting technique for this > problem. > > John Churchill > 1980 FC33 > LARGE MARGE > Sanibel, FL > |
|||
03-29-2009, 11:43
Post: #4
|
|||
|
|||
Maybe this will be a good approach?
|
|||
03-29-2009, 12:58
Post: #5
|
|||
|
|||
Maybe this will be a good approach?
Gary-
Thanks for the info, but I am not sure I understand the function. Isn't the NEC just applicable to houses, etc? In a boat (which I know a bit), the neutral is kept separate aboard and brought ashore for connection to the ground. In the main panel of LARGE MARGE, all the whites are together on the buss bar. Are you saying that the neutral ought to be connected to the ground on the coach? That does not make sense to me. John Churchill 1980 FC33 --- In WanderlodgeForum@yahoogroups.com, GARY MINKER > > The National Electrical Code calls for a neutral bonding screw in the first disconnect or panel. Look in the disconnect or panels for this screw that is driven through the neutral bar in to the case. It is normal. Coaches are not meant to be plugged in to GFI recepticals because of this. You take a low risk removing the bolt/screw. This is why many newer units only have a 3 conductor cord. > Gary > > --- On Wed, 3/25/09, Chuck Wheeler > > From: Chuck Wheeler > Subject: RE: [WanderlodgeForum] Maybe this will be a good approach? > To: WanderlodgeForum@yahoogroups.com > Date: Wednesday, March 25, 2009, 9:41 AM > > > > > > > > > > > > > > > > That should work, and was what I was trying to say...guess > I do not write too clearly. The reason I disconnected more than one at a > time was that I had several small "leaks" adding up. The worst was the > front heater, but that is when I discovered that the various monitors all cause > a little resistance. Â I had a red marker with me and when I > discovered a circuit that caused the resistance to increase when disconnected I > put a red mark on it. When finished I had three circuits open, the heater > and the two that fed the power monitor and shore power. The heater and > shore power monitor I could clear with repairs, the power monitor by design will > draw a small ground current for it's proper operation but this is less than .5ma > which is well below the GFI trip point. Since you have your power monitor > out, I would think you should be able to clear it all. > > - Chuck > Wheeler- > 1982 FC 31SB Fort Worth TX > > > > > From: WanderlodgeForum@ yahoogroups. com > [mailto:Wanderlodge Forum@yahoogroup s.com] On Behalf Of > Robin > Sent: Wednesday, March 25, 2009 5:06 AM > To: > WanderlodgeForum@ yahoogroups. com > Subject: [WanderlodgeForum] Maybe > this will be a good approach? > > > > > I did a little homework and read about the "hot skin test". One post there > mentioned simply checking continuity between neutral and ground on the coach > side of the shore power plug (with the power off of course). I've got only 2 > Ohms of resistance, should be infinite. Leads me to think that I can do the same > test at the panel, checking continuity between the neutral bus bar and ground. > Pull one white at a time, and when I finally get an open circuit, there is the > problem. I may leave them all disconnected as I proceed to allow for more than 1 > bad circuit, checking again after reconnecting each. Does this procedure make > sense? > > John Churchill > > --- In WanderlodgeForum@ yahoogroups. com, > "Chuck Wheeler" > > > > John, > > > > > There are some active circuits even when all breakers are off. They > are > > involved in the circuit that warns you if you turn the ignition on > with > > shore power applied. Turning off the breakers only breaks the "hot" > side. > > If there is a cross between Neutral and ground it will still be > there even > > with the breakers off. That is why I had to disconnect the > neutrals in > > order to isolate my problem. There may be a different or > better way,but > > this was the only way I could think of. > > > > > - Chuck Wheeler- > > 1982 FC 31SB Fort Worth TX > > > > > > > _____ > > > > From: WanderlodgeForum@ yahoogroups. com > > > [mailto:WanderlodgeForum@ yahoogroups. com] > On Behalf Of Robin > > Sent: Tuesday, March 24, 2009 9:19 PM > > To: WanderlodgeForum@ yahoogroups. com > > > Subject: [WanderlodgeForum] gfci still tripping > > way > > > > > > > Well, I've completely removed both my PowerWatch reverse polarity > indicators > > to re-do them. Decided to check the coach with them removed > and the GFCI > > still trips when I plug the 30 amp cord in. It trips when I > plug it into > > either of the two 30 amp receptacles on the coach. (I do > not own a 50 amp > > cord.) Trips even though all the breakers are off > including individual > > circuits, main breaker and the separate 30 amp > disconnect breakers. If I > > switch the master shore power switch to off, > gen or 50 amp it does not trip. > > It does trip if this switch is set at 30 > amps. If I start with everything at > > off, then gradually flip switches it > seems to barely hold, but if the > > switches are on and I plug in the cord, > the GFCI trips, suggesting I am > > right at the trip point. > > > > > One possible problem area is the genset which has been replaced in the > past, > > but does not ever seem to have been run prior to my getting the > coach. > > > > I am looking for advice on the proper troubleshooting > technique for this > > problem. > > > > John Churchill > > 1980 > FC33 > > LARGE MARGE > > Sanibel, FL > > > |
|||
03-29-2009, 13:30
Post: #6
|
|||
|
|||
Maybe this will be a good approach?
The RVIA establishes the standards for RV construction. While most of the NEC applies, the ground and neutral are to be kept separate in an RV. There is a danger than the RV frame (and in the case of a WL) and body can become energized, leading to a chance of electrocution if someone is grounded outside, is touching the body of the coach, and there is an electrical fault. That is one reason to check polarity when hooking up to a power source, reversed polarity can lead to the same dangerous situation.
Pete Masterson '95 Blue Bird Wanderlodge WBDA 42 El Sobrante CA "aeonix1@mac.com" On Mar 29, 2009, at 5:58 PM, Robin wrote:
|
|||
04-07-2009, 06:54
Post: #7
|
|||
|
|||
Maybe this will be a good approach?
|
|||
04-07-2009, 06:58
Post: #8
|
|||
|
|||
Maybe this will be a good approach?
|
|||
04-07-2009, 11:23
Post: #9
|
|||
|
|||
Maybe this will be a good approach?
many inverter and gensets have internal grounding to neutral paths. so if the
transfer switch does only the two hot legs an additional relay is needed to unbond the genset or inverter ground to neutral ( if it is bonded during use). I think Magnum has this worked out with internal relays. or that is their sales pitch. I was concerned about the inverter charger bonding when I added a new unit and couldnt get a good answer so I sent the updated bus into a good boat shop for a look over. you are not going to get a good answer here because ther are many variables and changed configurations in these old units. and the idea of 'to bond' or 'not to bond' while on genset/invert has no standard. Gregory of Tim&Greg --- In WanderlodgeForum@yahoogroups.com, GARY MINKER > > Hi, > I almost missed the post. I don't get to read em all. Give me a call and I can go over it all with you. > Gary > 561 969-9245 > > --- On Sun, 3/29/09, Robin > > From: Robin > Subject: [WanderlodgeForum] Re: Maybe this will be a good approach? > To: WanderlodgeForum@yahoogroups.com > Date: Sunday, March 29, 2009, 8:58 PM > > > > > > > > > > > > > Gary- > > Thanks for the info, but I am not sure I understand the function. Isn't the NEC just applicable to houses, etc? In a boat (which I know a bit), the neutral is kept separate aboard and brought ashore for connection to the ground. In the main panel of LARGE MARGE, all the whites are together on the buss bar. Are you saying that the neutral ought to be connected to the ground on the coach? That does not make sense to me. > > John Churchill > > 1980 FC33 > > > > --- In WanderlodgeForum@ yahoogroups. com, GARY MINKER wrote: > > > > > > The National Electrical Code calls for a neutral bonding screw in the first disconnect or panel. Look in the disconnect or panels for this screw that is driven through the neutral bar in to the case. It is normal. Coaches are not meant to be plugged in to GFI recepticals because of this. You take a low risk removing the bolt/screw. This is why many newer units only have a 3 conductor cord. > > > Gary > > > > > > --- On Wed, 3/25/09, Chuck Wheeler > > > > > > From: Chuck Wheeler > > > Subject: RE: [WanderlodgeForum] Maybe this will be a good approach? > > > To: WanderlodgeForum@ yahoogroups. com > > > Date: Wednesday, March 25, 2009, 9:41 AM > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > That should work, and was what I was trying to say...guess > > > I do not write too clearly. The reason I disconnected more than one at a > > > time was that I had several small "leaks" adding up. The worst was the > > > front heater, but that is when I discovered that the various monitors all cause > > > a little resistance.  I had a red marker with me and when I > > > discovered a circuit that caused the resistance to increase when disconnected I > > > put a red mark on it. When finished I had three circuits open, the heater > > > and the two that fed the power monitor and shore power. The heater and > > > shore power monitor I could clear with repairs, the power monitor by design will > > > draw a small ground current for it's proper operation but this is less than .5ma > > > which is well below the GFI trip point. Since you have your power monitor > > > out, I would think you should be able to clear it all. > > >  > > > - Chuck > > > Wheeler- > > > 1982 FC 31SB Fort Worth TX > > >  > > > > > > > > > > > > From: WanderlodgeForum@ yahoogroups. com > > > [mailto:Wanderlodge Forum@yahoogroup s.com] On Behalf Of > > > Robin > > > Sent: Wednesday, March 25, 2009 5:06 AM > > > To: > > > WanderlodgeForum@ yahoogroups. com > > > Subject: [WanderlodgeForum] Maybe > > > this will be a good approach? > > > > > > > > > > > > > > > I did a little homework and read about the "hot skin test". One post there > > > mentioned simply checking continuity between neutral and ground on the coach > > > side of the shore power plug (with the power off of course). I've got only 2 > > > Ohms of resistance, should be infinite. Leads me to think that I can do the same > > > test at the panel, checking continuity between the neutral bus bar and ground. > > > Pull one white at a time, and when I finally get an open circuit, there is the > > > problem. I may leave them all disconnected as I proceed to allow for more than 1 > > > bad circuit, checking again after reconnecting each. Does this procedure make > > > sense? > > > > > > John Churchill > > > > > > --- In WanderlodgeForum@ yahoogroups. com, > > > "Chuck Wheeler" > > > > > > > > John, > > > > > > > > > > > There are some active circuits even when all breakers are off. They > > > are > > > > involved in the circuit that warns you if you turn the ignition on > > > with > > > > shore power applied. Turning off the breakers only breaks the "hot" > > > side. > > > > If there is a cross between Neutral and ground it will still be > > > there even > > > > with the breakers off. That is why I had to disconnect the > > > neutrals in > > > > order to isolate my problem. There may be a different or > > > better way,but > > > > this was the only way I could think of. > > > > > > > > > > > - Chuck Wheeler- > > > > 1982 FC 31SB Fort Worth TX > > > > > > > > > > > > > > > _____ > > > > > > > > From: WanderlodgeForum@ yahoogroups. com > > > > > > > [mailto:Wanderlodge Forum@ yahoogroups. com] > > > On Behalf Of Robin > > > > Sent: Tuesday, March 24, 2009 9:19 PM > > > > To: WanderlodgeForum@ yahoogroups. com > > > > > > > Subject: [WanderlodgeForum] gfci still tripping > > > > way > > > > > > > > > > > > > > > Well, I've completely removed both my PowerWatch reverse polarity > > > indicators > > > > to re-do them. Decided to check the coach with them removed > > > and the GFCI > > > > still trips when I plug the 30 amp cord in. It trips when I > > > plug it into > > > > either of the two 30 amp receptacles on the coach. (I do > > > not own a 50 amp > > > > cord.) Trips even though all the breakers are off > > > including individual > > > > circuits, main breaker and the separate 30 amp > > > disconnect breakers. If I > > > > switch the master shore power switch to off, > > > gen or 50 amp it does not trip. > > > > It does trip if this switch is set at 30 > > > amps. If I start with everything at > > > > off, then gradually flip switches it > > > seems to barely hold, but if the > > > > switches are on and I plug in the cord, > > > the GFCI trips, suggesting I am > > > > right at the trip point. > > > > > > > > > > > One possible problem area is the genset which has been replaced in the > > > past, > > > > but does not ever seem to have been run prior to my getting the > > > coach. > > > > > > > > I am looking for advice on the proper troubleshooting > > > technique for this > > > > problem. > > > > > > > > John Churchill > > > > 1980 > > > FC33 > > > > LARGE MARGE > > > > Sanibel, FL > > > > > > > > |
|||