Generator Problem
07-11-2010, 04:15
Post: #17
Generator Problem
Okay I will check these connectors. Thanks for your help. Robert

--- In WanderlodgeForum@yahoogroups.com, "Ralph L. Fullenwider"
wrote:
>
> Excellent! The relay is clicking, meaning it is being told to pull in and
> pass 12 vdc to the start solenoid but it is not getting there. Now then, I
> believe there are external plugs on the control box, 2 maybe 3 of them? Un
> plug the connectors, clean them and try a start.
>
> These same connectors send the 12 vdc to the slip rings on the rotor
> supplying the "flash" voltage to start the EMF building as the rotor turns
> inside of the stator (field) and that supplies voltage to the regulator and
> eventually builds to 110vac to pull in the 110vac relay in the control box,
> keeping the gen set running and giving you leg 1 and leg 2 AC voltage to
> the Coach.
>
> I believe that you have some corroded or dirty connectors.
>
> Ralph
>
> At 03:37 AM 7/11/2010 +0000, you wrote:
>
> >I checked that and there was nothing for voltage. at the small terminal
> >and ground. Just an occasional clicking sound that is coming from one of
> >those small plastic bosch boxes inside the control box. Robert
> >--- In WanderlodgeForum@yahoogroups.com, "Ralph L. Fullenwider"
> > wrote:
> > >
> > > Need to check between a ground point and the small terminal, then switch
> > > the start switch and see if you read 12 vdc. From ground to the small
> > > terminal there should be no voltage until you hit the start switch.
> > >
> > > The start switch supplies power to the small terminal (coil) of the
> > starter
> > > solenoid and pulls it in to pass full volts DC to the starter.
> > >
> > > Ralph
> > >
> > > At 02:48 AM 7/11/2010 +0000, you wrote:
> > > >So I checked and there is 12.9 volts between the small terminal and the
> > > >large terminal all the time weather the start switch is depressed or not.
> > > >if i go between the small terminal and the second large terminal there is
> > > >no voltage. There are three bosch little boxes in the controll box. some
> > > >of the time when the start switch is depressed, one of them makes a
> > > >clicking sound. I went to napa and bought another one of these, it makes
> > > >the same clicking when start is depressed. Robert
> > > >
> > > >--- In WanderlodgeForum@yahoogroups.com, "Ralph L. Fullenwider"
> > > > wrote:
> > > > >
> > > > > Nah, not over your head yet, your doing fine.
> > > > >
> > > > > Now then we know the battery is ok and the starter is running, now
> > we need
> > > > > to get 12 vdc to the small terminal on the starter solenoid sitting
> > on top
> > > > > of the starter. So place your mater red lead on the terminal and
> > the black
> > > > > on a ground and set the meter to dc volts. Check the voltage on the
> > small
> > > > > terminal when you flip the start switch on the control box, you
> > should see
> > > > > 12 vdc? If you do see 12 vdc then the starter solenoid is suspect,
> > and if
> > > > > you don't see the 12vdc then we trace back to the point of where we
> > lose
> > > > > it, and I will have to go get my schematic for the Yammar.
> > > > >
> > > > > Ralph
> > > > >
> > > > > At 12:36 AM 7/11/2010 +0000, you wrote:
> > > > >
> > > > > >Ralph, so I went back out to check a few things. The starter will
> > not run
> > > > > >at all from any of the switches. The battery is new and 12.9 volts. I
> > > > > >checked at the top of the starter and it is 12.9 there as well. When
I
> > > > > >jump across the two large posts on the starter the gen starts and
> > runs as
> > > > > >long as the actuator is held in. When I switch the coaches manual
> > power
> > > > > >switch from 50 amp to gen. there is no power in the coach. I
> > checked the
> > > > > >coolant level and oil level and checked for any disconected wires on
> > > > > >anything ion the engine. There is only a small 10 amp fuse on the
> > control
> > > > > >box and that is okay. The items you listed under further checks I
> > am not
> > > > > >at all familiar with. Am i over my head with this already, or is
there
> > > > > >anything I can check? Thanks for your help,
> > > > > >Robert
> > > > > >--- In WanderlodgeForum@yahoogroups.com, "Ralph L. Fullenwider"
> > > > > > wrote:
> > > > > > >
> > > > > > > Hi Robert:
> > > > > > >
> > > > > > > The fuel solenoid is what your holding slightly to run the
> > generator.
> > > > > > There
> > > > > > > are several things that will be the reason for it not to pull in.
> > > > So here
> > > > > > > go a few questions to you;
> > > > > > >
> > > > > > > 1. Is there voltage on the coil of the start relay located on top
> > > > of the
> > > > > > > starter?
> > > > > > > 2. Does the starter actually try to turn the engine over?
> > > > > > > 3. Check the fuse or circuit breaker on the control box?
> > > > > > > 4. Check the coolant fluid level?
> > > > > > > 5. Check the oil level?
> > > > > > > 6. checked to be sure wire did not come off the high water temp
> > > > switch?
> > > > > > and
> > > > > > > grounding some where. or hwt switch failed closed.
> > > > > > > 7. Wire off the oil pressure switch?
> > > > > > > Answering the questions are the first steps to be taken, I
> > write the
> > > > > > checks
> > > > > > > down as I go to keep track of where I have been
> > > > > > >
> > > > > > > Now then, with the engine running, you say there is no output from
> > > > the gen
> > > > > > > set? and does your Coach have a manual or automatic transfer
> > switch?
> > > > > > >
> > > > > > > Further checks;
> > > > > > > 1 As Ernie said, check the state of the gen battery
> > > > > > > 2 check the diode on the curb side down by the oil pressure
sender.
> > > > > > > 3 Check the bearing in the end bell, does it move up and down
> > > > greatly with
> > > > > > > a screw driver used as a pry bar?
> > > > > > > 4. Is a wire broken off one or both brushes on the slip rings?
> > > > > > > 5. is the diode and fuse on the quadrature windings ok?
> > > > > > >
> > > > > > > Answer those questions and we can go further
> > > > > > >
> > > > > > > Safe travels,
> > > > > > >
> > > > > > > Ralph and Charolette Fullenwider
> > > > > > > "84FC35 "Ruff Diamond"
> > > > > > > Duncan, Oklahoma
> > > > > > >
> > > > > > > At 09:43 PM 7/10/2010 +0000, you wrote:
> > > > > > > >I am having trouble with the genarator in my 88 pt 40. It is a
> > > > yanmar. I
> > > > > > > >started it and it ran for some time normally then shut off.
> > Now it
> > > > will
> > > > > > > >not start from any of the switches, I just get a clicking noise
> > > > from one
> > > > > > > >of the bosch relays in that little metal box by the gen in the
> > > > foreward
> > > > > > > >compartment. I replaced that and it does the same clicking. I can
> > > > start
> > > > > > > >the genarator by jumping across the starter while holding the
> > throttle
> > > > > > > >solonoid in a bit, but it stopps as soon as I let go. I checked
> > > > and there
> > > > > > > >is no voltage at the solonoid while it is running. Also there
> > is now
> > > > > > power
> > > > > > > >in the bus while the genarator is running. Any ideas?
> > > > > > > >
> > > > > > > >Robert Rahn
> > > > > > > >88 pt 40
> > > > > > > >Kalispell, Mt
> > > > > > > >
> > > > > > > >
> > > > > > > >
> > > > > > >
> > > > > >
> > > > > >
> > > > > >
> > > > > >
> > > > > >------------------------------------
> > > > > >
> > > > > >Yahoo! Groups Links
> > > > > >
> > > > > >
> > > > > >
> > > > > Safe travels,
> > > > >
> > > > > Ralph and Charolette Fullenwider
> > > > > "84FC35 "Ruff Diamond"
> > > > > Duncan, Oklahoma
> > > > >
> > > >
> > > >
> > > >
> > > >
> > > >------------------------------------
> > > >
> > > >Yahoo! Groups Links
> > > >
> > > >
> > > >
> > > Safe travels,
> > >
> > > Ralph and Charolette Fullenwider
> > > "84FC35 "Ruff Diamond"
> > > Duncan, Oklahoma
> > >
> >
> >
> >
> >
> >------------------------------------
> >
> >Yahoo! Groups Links
> >
> >
> >
> Safe travels,
>
> Ralph and Charolette Fullenwider
> "84FC35 "Ruff Diamond"
> Duncan, Oklahoma
>
Quote this message in a reply
Post Reply 


Messages In This Thread
Generator Problem - Chris - 05-20-2006, 14:09
Generator Problem - Ralph L. Fullenwider - 05-20-2006, 14:11
Generator Problem - Chris Reed - 05-22-2006, 14:11
Generator Problem - Chris Reed - 06-10-2006, 18:33
Generator Problem - chaunceyboyblu - 07-10-2010, 09:43
Generator Problem - Ernie Ekberg - 07-10-2010, 10:52
Generator Problem - Ralph L. Fullenwider - 07-10-2010, 11:38
Generator Problem - chaunceyboyblu - 07-10-2010, 12:36
Generator Problem - dmb993@earthlink.net - 07-10-2010, 12:45
Generator Problem - Ralph L. Fullenwider - 07-10-2010, 13:30
Generator Problem - Ralph L. Fullenwider - 07-10-2010, 13:55
Generator Problem - chaunceyboyblu - 07-10-2010, 14:48
Generator Problem - Ralph L. Fullenwider - 07-10-2010, 15:32
Generator Problem - Ralph L. Fullenwider - 07-10-2010, 15:36
Generator Problem - chaunceyboyblu - 07-10-2010, 15:37
Generator Problem - Ralph L. Fullenwider - 07-10-2010, 15:44
Generator Problem - chaunceyboyblu - 07-11-2010 04:15
Generator Problem - chaunceyboyblu - 07-11-2010, 09:02
Generator Problem - Ralph L. Fullenwider - 07-11-2010, 09:13



User(s) browsing this thread: 1 Guest(s)