some regulators use stab on connections that work loose. remove them all and crimp them, reinsert them several times to clean them and do not use chemicals unless necessary

--- On Fri, 5/27/11, Ralph wrote:
From: Ralph
Subject: Re: [WanderlodgeForum] Gen help needed!
To: "Wanderlodge Forum"
Date: Friday, May 27, 2011, 2:36 PM





Voltage regulator has gone out is what it sounds like or check the brushes


Safe travels, Ralph Charolette Fullenwider
'84 FC35 "Ruff Diamond"
Duncan, Oklahoma
Sent via BlackBerry by AT&T


From: Markus Meyer
Date: Fri, 27 May 2011 14:30:09 -0400
To:
Subject: [WanderlodgeForum] Gen help needed!
About to leave for the weekend in an hour. 4 hour ride ahead in 90 or so temps. Ran generator for about 4 hours yesterday no problem. Started it today before noon, left to walk the dog at 1, still running. Got back at 2, not running. Gas tank is full, oil in the gen is at proper level, coolant tank half full. The solenoid pulls out or releases when it shuts off, if you hold it, it keeps running. But even when you hold it to keep it running, no power whatsoever inside.



Ideas?

Markus

86 PT40
Quote this message in a reply
Post Reply 


Messages In This Thread
Gen help needed! - Markus Meyer - 05-27-2011, 06:30
Gen help needed! - Ralph - 05-27-2011, 06:36
Gen help needed! - Ralph L. Fullenwider - 05-27-2011, 06:48