No Inverter charge with shore but OK with genset
|
01-22-2015, 16:04
Post: #3
|
|||
|
|||
RE: No Inverter charge with shore but OK with genset
Thanks for the schematics.. Power seems OK to inverters..and OK through the bypass.
Possibly need 115 V input?? Could that cause inverters to not charge?? Meters above door read 110 V not 115 as I posted earlier. Ross Latest : Bypass inverter 2 puts shore power directly EMS panel 3 which then does not shed and works normally. So allowing power to go through inverter causes the EMS issue. But still no charge with inverter one. (Last night both inverters charged for a while) Very unlikely that both inverters toasted at the same time. John .. I think the power input from post is suspect. I'll find/borrow an accurate meter. My new one is crap. Borrowed a good meter -- 110, 111 on post .. each line and 224 across. Inverter outputs on inverter recept. reads 105 V ! No line V drop when coach attached ( meter with plug part way out). (01-22-2015 15:36)davidbrady Wrote: Ross, Ross MacKillop Wiarton Ontario 2006 450 Lxi |
|||